Junior Member
 
Join Date: Oct 2018
Posts: 3
I think your problem was due to loose connections in your breaker box. Loose connections will cause excessive heating. You stated that your wife said the breaker box was too hot to place her hand on. Once you get your breaker box replaced, I would open and check every outlet. Making sure all screws are tight. I have a Predator 3500 and use all the time. My Solitude has a 50A service and the Inverter will handle 30A load 24/7 with refueling the only time for shutdowns.
neonwizard is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-25-2019, 07:42 PM   #72
Member
 
Join Date: Sep 2014
Location: Hendersonville, nc
Posts: 69
Quote:
Originally Posted by travelnoob View Post
It is the habor freight predator 3500 watt inverter generator. Maybe you can see the adapter for it when you look it up if not here is a link to a video

https://youtu.be/7mBYq9ZgbKk

On his tip 2 he talks about the adapter
I had a 3500 watt Generator from Harbor freight that was not an inverter generator. and it worked fine. BUT NOT with a twist plug. I had to use two adapters from each of the 15 amp (one plug in each duplex only) duplex to thirty amp output. I remember a wye connection to thirty amp. Then a thirty to fifty amp adapter from that. Worked great several times. I have since sold it since it made too much noise no matter what i did. Built a box to house it on the back bumper,, added an above the roof exhaust, (Made no difference in noise that I could tell) added insulation to the box. (helped some) but nothing made enough of a difference. I know that the thirty amp plug was not properly matched to what the camper needed,. That's as much as I remember,, except that every thing ran as though I was on shore power. You need to check the connection from the Generator, with a proper meter, before you plug in the RV. You should have two separate circuits of 110 to 120 going into the RV. NOT 220V. I Assume the inverter also uses a thirty amp twist plug that is actually 220V ?
shippwreck is offline   Reply With Quote
Old 08-25-2019, 08:42 PM   #73
Member
 
Join Date: Aug 2008
Location: SE Michigan
Posts: 57
Smile 30 amp

Quote:
Originally Posted by shippwreck View Post
I had a 3500 watt Generator from Harbor freight that was not an inverter generator. and it worked fine. BUT NOT with a twist plug. I had to use two adapters from each of the 15 amp (one plug in each duplex only) duplex to thirty amp output. I remember a wye connection to thirty amp. Then a thirty to fifty amp adapter from that. Worked great several times. I have since sold it since it made too much noise no matter what i did. Built a box to house it on the back bumper,, added an above the roof exhaust, (Made no difference in noise that I could tell) added insulation to the box. (helped some) but nothing made enough of a difference. I know that the thirty amp plug was not properly matched to what the camper needed,. That's as much as I remember,, except that every thing ran as though I was on shore power. You need to check the connection from the Generator, with a proper meter, before you plug in the RV. You should have two separate circuits of 110 to 120 going into the RV. NOT 220V. I Assume the inverter also uses a thirty amp twist plug that is actually 220V ?
A 30 amp is 110/120 volt only. A 50 amp is 2 110/120 volt circuits with 220/240 available. I’ve wired all of them, they all checked out and worked fine.
RadioRadio is offline   Reply With Quote
Old 08-25-2019, 10:37 PM   #74
Senior Member
 
Join Date: May 2019
Posts: 297
Sounds familiar. Check if the neutral and ground wires are reversed in the generator. Whether they are or not, I'd guess your generator tried to dump all its current through the neutral wire direcdt to ground. This melted the neutral wire which then caused your generator to be unable to power your system (no neutral). Take a multi-meter and measure the generator output, If the wires are reversed, Harbor Fright should (!) be responsible for your damage.If you have to take your rig to a dealer for repair, I'd suggest havent them tesst the generator. If you repair it yourself, you may find you have other componens damaged - refer, TV, microwave, etc.
Good luck, let us know how it turns out.
Bob
'14 Winnebgo 37F Jeep toad
bobfrommaine is offline   Reply With Quote
Old 08-26-2019, 12:09 AM   #75
Senior Member
 
mike5511's Avatar
 
Join Date: Jul 2017
Location: NW Arkansas
Posts: 269
Why would you use your surge protector with an inverter generator?
mike5511 is offline   Reply With Quote
Old 08-26-2019, 07:02 AM   #76
Member
 
Join Date: Dec 2016
Posts: 77
Quote:
Originally Posted by Persistent View Post
We are back to which breakers tripped at which incident.
If the main breaker in the TT tripped, that means more than 30 amps through the breaker.
If branch breakers in the TT tripped, that means more than 15 amps through the branch circuity.
If pedestal breaker tripped during lightning, more than 30 amps at that time.
If Generator breaker tripped, that means more that 30 amps at that time.

Tripping the breakers protects the circuits. Burned wires means the circuit was not protected. Wires in the distribution box burned and so the current must not have flowed through breakers. If the generator flow burned the wires, the breaker in the generator would have tripped.

Did the generator breaker trip?

Very interesting!

I am starting to entertain the idea that there was more than two incidents.
You did not smell smoke at any time. Yet smoke must have been generated. A substantial amount of copper and insulation was vaporized or burned.

There may have been a second lightning strike when TT was not occupied. It is possible the second strike caused the damage. Once wires burned off they may have shorted. Vibration from towing the TT may have dislodged a damaged wire causing a short circuit. The first connection to the generator finished them off. The generator will run high starting current for about 30 seconds before tripping its circuit breaker.

None of this makes really good sense. The extensive damage should not have been caused by the generator. It has a circuit breaker that certainly would have protected the shore power cord.

A lightning strike could easily cause the damage and trip circuit breakers at the same time. Arching across terminals and through insulation is a hallmark of a lightning strike. However, I can't see how smoke was not produced when the lightning struck.

A second strike on the distribution panel area would leave signs on the TT walls unless the shore power cord was attached. Also, smoke would have been generated and some trace would probably remain when you reopened the TT.

In any case you have a lot of electrical parts to replace. The generator is probably OK and probably did not cause the damage.

I wish you good luck with the repairs.
These are all very interesting points Persistent made, also see the picture below seeing the green flakes and the corrosion on the bus bar makes me think you might have had or still have water infiltration.
Attached Thumbnails
Click image for larger version

Name:	buss bar.jpg
Views:	45
Size:	226.0 KB
ID:	258014  
sledbiker1 is offline   Reply With Quote
Old 08-26-2019, 07:05 AM   #77
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
Quote:
Originally Posted by bobfrommaine View Post
Sounds familiar. Check if the neutral and ground wires are reversed in the generator. Whether they are or not, I'd guess your generator tried to dump all its current through the neutral wire direcdt to ground. This melted the neutral wire which then caused your generator to be unable to power your system (no neutral). Take a multi-meter and measure the generator output, If the wires are reversed, Harbor Fright should (!) be responsible for your damage.If you have to take your rig to a dealer for repair, I'd suggest havent them tesst the generator. If you repair it yourself, you may find you have other componens damaged - refer, TV, microwave, etc.
Good luck, let us know how it turns out.
Bob
'14 Winnebgo 37F Jeep toad
OP already did. The neutral is floating and he measured 60 volts from hot to ground and 61 volts from neutral to ground. Can't dump to ground since ground and neutral are isolated in his box (clearly evident) and generator is floating.
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 08-26-2019, 08:50 AM   #78
Member
 
Join Date: Jul 2019
Location: Southern Illinois
Posts: 53
Beginning to sound like this was a long term issue and that the generator is an innocent bystander.

Long term there may have been loose connections generating heat (panel warm/hot to touch) but insufficient to do anything more than slowly degrade connections further. Degraded connections combined with over the road vibrations eventually caused connections to open up BUT with an insufficient air gap to preclude current flow. Add generator and fire up circuits, current arcs gap causing high current flow. Breaker trips, further damage done. Close breakers, fire up generator, further arcing, more high current flow, breakers trip, this time with sufficient damage done as to open circuits with enough air gap to prevent arcing (I.e. it already burnt things apart). Nothing works now....

May have all started with that lightning strike..... OP doesn’t really say if panel/box was always warm/hot or if it developed after strike. If after strike may have damaged a connection and started the whole process.

As I said, generator is an innocent bystander - wrong place wrong time.
Tip10 is offline   Reply With Quote
Old 08-26-2019, 10:48 AM   #79
Junior Member
 
Join Date: Aug 2009
Location: Youngsville, NC
Posts: 13
As I followed this blog, it might be good for all of us to have a qualified tech check the neutral connections in our power panels. I had a similar situation where the neutral feed came loose at the busbar and burned up my shorepower outlet in the garage because the RV’s generator neutral was hard wired to ground after the transfer switch. Caught it just before it set the house on fire.

Based on the photos and the comment from the OP that his wife said the box was uncomfortably hot to touch that one of the neutral connections was heating over some period of time. Probably the one by the melted hole in the case. As mentioned earlier, this type of failure becomes cumulative with time. The fact that the conductors are Copper and the busbar is Aluminum can cause problems like this due to oxidation so the connection becomes resistive and heats up. The insulation in the wire bundle is also compromised.

Why the main breaker tripped when there was a lightning strike nearby is a mystery unless there may have a current surge or voltage dip that got thru any upstream protection and tripped the breaker as the trailer load responded to whatever the fault was.
Just my humble opinion. Was a low voltage power engineer for many years and used to do forensic failure analysis on these type of failures in telecom systems.
__________________
Glenn and wife Shirley- retired
ChiChi rescued ChiPom 12 yrs. old
2013 Cougar Xlite 32SAB 2016 Ram 2500HD Cummins 6.7
dcpowerglenn is offline   Reply With Quote
Old 08-26-2019, 09:55 PM   #80
Senior Member
 
Join Date: Dec 2017
Posts: 207
Quote:
Originally Posted by rg4bs View Post
I think my head to going to explode!
^^^^^
Me too. I'm totally confused about buss bars, L1 Highs, and I guess I better go to Google and start learning about generators and inverter generators. Who knew it could get so complicated. Lesson 1--Difference between a regular generator and an inverter generator. Lesson 2--after my brain absorbs that.
Linda Bohr is offline   Reply With Quote
Old 08-27-2019, 06:12 AM   #81
Member
 
Join Date: Jul 2019
Location: Southern Illinois
Posts: 53
Quote:
Originally Posted by Linda Bohr View Post
^^^^^

Me too. I'm totally confused about buss bars, L1 Highs, and I guess I better go to Google and start learning about generators and inverter generators. Who knew it could get so complicated. Lesson 1--Difference between a regular generator and an inverter generator. Lesson 2--after my brain absorbs that.


Lesson 0 — an awful lot of what you read posted and postulated on blogs is from folks who simply don’t really know what they are talking about.....
Tip10 is offline   Reply With Quote
Old 08-27-2019, 06:16 AM   #82
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
Quote:
Originally Posted by Tip10 View Post
Lesson 0 — an awful lot of what you read posted and postulated on blogs is from folks who simply don’t really know what they are talking about.....
I agree. However, the title of this thread should definitely be changed because Reverse Polarity definitely did NOT blow the OP's Panel
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 08-27-2019, 06:25 AM   #83
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 3,165
Quote:
Originally Posted by bobfrommaine View Post
Sounds familiar. Check if the neutral and ground wires are reversed in the generator. Whether they are or not, I'd guess your generator tried to dump all its current through the neutral wire direcdt to ground. This melted the neutral wire which then caused your generator to be unable to power your system (no neutral). Take a multi-meter and measure the generator output, If the wires are reversed, Harbor Fright should (!) be responsible for your damage.If you have to take your rig to a dealer for repair, I'd suggest havent them tesst the generator. If you repair it yourself, you may find you have other componens damaged - refer, TV, microwave, etc.
Good luck, let us know how it turns out.
Bob
'14 Winnebgo 37F Jeep toad
HF is responsible for nothing. They did not build or design the Gen. The GEN did not cause the problem. Loose wire connections caused the problem. The same thing happens in house panels and building panels. Who you gonna blame there???
__________________
2011 Keystone Sprinter 323 BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
cavie is offline   Reply With Quote
Old 08-27-2019, 06:29 AM   #84
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 3,165
Quote:
Originally Posted by Sbrownstein View Post
I agree. However, the title of this thread should definitely be changed because Reverse Polarity definitely did NOT blow the OP's Panel
Click image for larger version

Name:	What he said in that comment up there (1).jpg
Views:	39
Size:	17.1 KB
ID:	258169
__________________
2011 Keystone Sprinter 323 BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
cavie is offline   Reply With Quote
Reply

Tags
panel



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Passenger side front panel blew off! Doula Winnebago Industries Owner's Forum 15 02-20-2013 10:36 AM
Solar panel reverse polarity question? RCtime Going Green 8 11-07-2011 07:46 PM
Polarity Tester dickiebob RV Systems & Appliances 18 06-10-2008 09:16 AM