Reverse Polarity Blew my panel?
Hey guys
So I went to try some boondocking in a Walmart. I bought a Haber Freight Predator Inverter Generator just to for this purpose. I plugged in my 30 amp plug into it and all the power went on just fine for 30 seconds. Then my breakers tripped. I figured I had to many things on so I turned some light off flipped them back on and the power when back on. Then they went off again in about 30 sec.
It never came one again. The next day I opened up the panel and the Neutral bar and wires and panel and adjacent cabinets where melts/burned. I plugged my surge protector into the generator and it told me it has reverse polarity.
How could this change anything. Inst AC bouncing back and forth.
Thanks
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
08-18-2019, 08:50 AM
|
#2
|
Senior Member
Newmar Owners Club
Join Date: Oct 2009
Posts: 10,310
|
Was the plug in on the generator 30 amp/240 volt?
__________________
2012 Essex 4544 2011 Jeep JK, M&G Braking, 2014 MTI 27' Hog Hauler, Wireless brake control, 2006 Ultra & 1989 Springer, 2003 Harley-Davidson
FLHR Road King Anniversary
|
|
|
08-18-2019, 08:58 AM
|
#3
|
Senior Member
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
|
Did you use an adapter on the twist lock or did you plug into one of the duplex outlets?
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
|
|
|
08-18-2019, 09:17 AM
|
#4
|
Member
Join Date: Jul 2019
Posts: 71
|
No when I used my multimeter I got 61 volts each side.
|
|
|
08-18-2019, 09:18 AM
|
#5
|
Senior Member
Join Date: Nov 2017
Location: Oakhurst, CA
Posts: 926
|
Some add on inverters are not made to be chassis grounded, the third non insulated copper wire. You have to check the manual. The also fail a polarity checker. You can not get 220 from a 120 inverter. Another thing, bringing in shore power bypasses protections you have to only power low current items. Now your are applying power to the water heater and air conditioners etc. Your inverter may not be big enough to power those items. When I installed a inverter in my class C, I had its own socket to run things like computers etc.
__________________
2007 Country Coach Tribute 260 Sequoia
40' DP w/Cat400, F494513, Lithium Battery & Solar
Live next to Yosemite
|
|
|
08-18-2019, 09:18 AM
|
#6
|
Member
Join Date: Jul 2019
Posts: 71
|
I used the adaptor that came with it. It looks like a twist lock to a 30 amp
|
|
|
08-18-2019, 09:25 AM
|
#7
|
Member
Join Date: Jul 2019
Posts: 71
|
Im in a group on Facebook for the intech sol that’s what I have. They recommend me this generator they said it works fine for them. I did chain the generator to the aluminum frame of the sol, So it didn’t take a walk on me at night. Maybe that acted like a ground. Don’t see how that can change much. Dealer first said looks like I plugged into a 240 or something I never did.. then they said maybe lighting strick. During a thunder storm my main blew one night but I was using a surge protector and that was weeks ago. I have had power for a week or so until I tried the generator.
|
|
|
08-18-2019, 10:35 AM
|
#8
|
Senior Member
Join Date: Nov 2017
Location: Oakhurst, CA
Posts: 926
|
I would start back at square one, fix the wiring damage and verify everything works when plugged it. I would also reduce the plug connection to a standard 20 amp connector.
The turn off all your breakers so you do not have anything connected and connect inverter.
Then check power before breakers to see if correct, then turn on outlets with nothing plugged in and check voltages, plug in small light, check again.
Make sure large current device at off like water heater.
__________________
2007 Country Coach Tribute 260 Sequoia
40' DP w/Cat400, F494513, Lithium Battery & Solar
Live next to Yosemite
|
|
|
08-18-2019, 10:55 AM
|
#9
|
Senior Member
Join Date: Jul 2014
Posts: 35,442
|
How many watt Predator ?
Less the 3600 watts, probable only a 120 volt unit. A 3 blade twist lock is 120 volts. A 4 blade twist lock is 240 volts.
The inverter generators have floating grounds so 61 volts per side is normal. That will give you reverse polarity warning. AC is alternating current. The polarity changes 60 times a second. Tying one side to ground is a safety thing for humans. Doe dnt burn up bus bars.
Get or build a Edison plug to fix that. Google it.
Surge protectors are NOT lightning protectors. Damage was probably already there.
|
|
|
08-18-2019, 11:00 AM
|
#10
|
Senior Member
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
|
Reverse polarity shouldn't do that in a 120 volt panel. Generator probably has rubber feet which isolates it from ground. Chain shouldn't have made any difference since there really is not actual ground in the generator circuit anyway.
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
|
|
|
08-18-2019, 11:25 AM
|
#11
|
Senior Member
Join Date: Jul 2018
Posts: 4,925
|
Quote:
Originally Posted by gpounder
Some add on inverters are not made to be chassis grounded, the third non insulated copper wire. You have to check the manual. The also fail a polarity checker. You can not get 220 from a 120 inverter. Another thing, bringing in shore power bypasses protections you have to only power low current items. Now your are applying power to the water heater and air conditioners etc. Your inverter may not be big enough to power those items. When I installed a inverter in my class C, I had its own socket to run things like computers etc.
|
^^^ THIS ^^^
Most inverter generators have "balanced power" where half the voltage is on the hot and the other half of the neutral, much like ocean going vessels that supply domestic power.
You can "force" a neutral/ground bond by modifying a 15 amp Edison plug, shorting the neutral (silver) pin to the ground pin (brass) with a short piece of wire and plugging it into the generator.. but this isn't necessary for most loads.
I'm more curious about the "adapter" supplied with the generator and EXACTLY which generator the OP purchased.
__________________
2005 Four Winds Majestic 23A
“To the world you may be one person; but to one person you may be the world.” - Dr Suess
|
|
|
08-18-2019, 11:32 AM
|
#12
|
Member
Join Date: Jul 2019
Posts: 71
|
It is the habor freight predator 3500 watt inverter generator. Maybe you can see the adapter for it when you look it up if not here is a link to a video
https://youtu.be/7mBYq9ZgbKk
On his tip 2 he talks about the adapter
|
|
|
08-18-2019, 11:32 AM
|
#13
|
Senior Member
Join Date: Nov 2015
Posts: 26,843
|
Quote:
Originally Posted by twinboat
Surge protectors are NOT lightning protectors. Damage was probably already there.
|
THIS^^^^^^^^^
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
|
|
|
08-18-2019, 11:45 AM
|
#14
|
Member
Join Date: Jul 2019
Posts: 71
|
Quote:
Originally Posted by Old-Biscuit
THIS^^^^^^^^^
|
Wouldn’t the surge protector have fried too though
|
|
|
|
|