SOLVED! Troubleshoot furnace wiring from a/c
Thanks for the reply Bflinn181, wasp's nests removed. The problem was the wiring at the a/c was disconnected, I assume because of the furnace attempting to operate, making some noise and the owner worried about damage. They simply chose to use electric heat instead of repairing the furnace.
There are two white wires coming from the control box in the ac unit. They BOTH connect into thermostat wire bundles. However, a close examination of the wiring diagram finds that two blue/white wires(14 guage) from the a/c control box connect to a white wire(18 gauge) and a red wire(18 gauge), from a two-wire thermostat bundle. these two wires(red and white) go to the furnace.
The single white wire(14 gauge) from the a/c control box connects to a white wire((18 gauge) in a thermostat bundle, I think it was a 5 or 6 wire bundle. That wire goes to the thermostat.
Connect the wire and the furnace works, who knew!?!! Normal furnace operation, fan, heat and it shuts off just like new.
Interestingly:
1)When the a/c control box wire is disconnected from the thermostat. the thermostat lug for furnace will flash a 7vdc approximately when changing from "furnace" to "off" to "cool", that makes diagnosing difficult. 2) When selecting "furnace" at the thermostat, the a/c fan will come on until the wiring is connected, then the a/c operates normally. 3) I tried to connect the furnace directly to 12vdc(at the blower connector on the furnace), while I could get the blower at the furnace to turn on, the furnace did not operate. When I tried to connect the furnace wires at the a/c control box to direct 12vdc power, the furnace would not operate.
Hths,
Sam
|