Fusing individual 100AH BattleBorn batteries in a 4 battery bank

I read various opinions about fusing each individual battery in a four battery bank of Battle Born 100AH batteries.


What are some opinions and reasoning why?
__________________
Fred & Denise (RVM157) New Mexico
2007 Excel Classic 30RSO & 2025 ORV 19MKS
2007 RAM 3500 Diesel 6Spd Auto, SWD, 4x4, CC&LB
rarebear.nm is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-12-2025, 05:18 PM   #2
Senior Member
 
Join Date: Mar 2022
Posts: 538
I have three DIY batteries feeding a bus. Each battery has a MRBF on it. My reasoning is that without individual fusing, that wire between the bus and battery post is unprotected. If an idiot (not me) were to drop a wrench across the battery terminals there is nothing to stop the current from the other batteries from feeding a heap of current into the short.

I will also add that the BMS in the other batteries would shut down due to overcurrent, but if I fully trust that, then there is no need for fuses.
__________________
2019 Palomino Solaire 147X
2013 Ford F150
TacomaJoe is offline   Reply With Quote
Old 03-12-2025, 09:16 PM   #3
Senior Member
 
rarebear.nm's Avatar
 
Excel Owners Club
Ford Super Duty Owner
Join Date: Aug 2014
Location: Santa Fe, NM
Posts: 7,257
OP here:


I agree with your reasoning for individual fuses.


What I did not mention in the OP, is that all four batteries connect to a 500amp buss bar with 2/0 wire that is then connected via 4/0 wire to a 400a Class T fuse before it goes anywhere else.


I could use 100 amp MRBF fuses connected to the battery posts then feed the first buss bar. Those batteries have a 100 amp BMS.


A Multiplus 120v 3000watt inverter is connected via 4/0 wire off a main buss bar.
__________________
Fred & Denise (RVM157) New Mexico
2007 Excel Classic 30RSO & 2025 ORV 19MKS
2007 RAM 3500 Diesel 6Spd Auto, SWD, 4x4, CC&LB
rarebear.nm is offline   Reply With Quote
Old 03-26-2025, 11:19 PM   #4
Senior Member
 
Join Date: Jul 2013
Location: North East
Posts: 145
An even more important reason to fuse each individual battery, is in case one battery develops a dead short, and the BMS fails to disconnect that battery, the fuses will prevent the energy stored in the other three batteries from entering the shorted battery. All of my batteries are fused using MRBF fuses.
__________________
'95 Safari Serengeti 38', 300hp 6CTA8.3L Cummins, 6spd. Allison, Pac brake, Magnum chassis, Valvet Ride (torsilastic susp.), VW Jetta TDI toad, Big tripple bay window (from floor to ceiling cabinets)!!!
beach house is offline   Reply With Quote
Old 03-27-2025, 10:05 AM   #5
Senior Member
 
Join Date: Apr 2024
Posts: 429
Quote:
Originally Posted by rarebear.nm View Post
OP here:


I agree with your reasoning for individual fuses.


What I did not mention in the OP, is that all four batteries connect to a 500amp buss bar with 2/0 wire that is then connected via 4/0 wire to a 400a Class T fuse before it goes anywhere else.


I could use 100 amp MRBF fuses connected to the battery posts then feed the first buss bar. Those batteries have a 100 amp BMS.
you need larger than a 100 amp MRBF, 100 amps is your working output, then you have a over current for a period of time so 200 amp for 30 seconds and 500 amps for 1/2 a second. I would fuse them for say 250amps, but here is the recommendation from battle born.

"For a Battle Born 100Ah 12V LiFePO4 battery, a Class T fuse rated for 200 amps or higher is recommended for the main power conductor on the positive side, within 7 inches of the battery"
Stircrazy1 is offline   Reply With Quote
Old 04-05-2025, 02:04 PM   #6
Senior Member
 
Join Date: Jul 2013
Location: North East
Posts: 145
The protection needs are different compared to lead acid batteries, and the key point of using MRBF fuses is to prevent thermal runaway of the Lithium battery bank in case the bms fails, especially during and internal battery short situation. Under those situations, every second counts. Attached is trip curve of the MRBF fuses per Blue Sea website. It shows that it takes about 10 minutes to blow an MRBF fuse at 140% load, and about 1.5 minutes to blow a fuse at 200% load. It logically makes sense that the bigger the battery bank is, the lower (with in reason) the MRBF fuse should be. For 4 batteries, the numbers show that a 150 amp fuse would be more that adequate. 140% of 150 amps is 210, so it would take about 10 minutes to blow a 150 MRBF fuse at 210 amps, if the bms fails to shut down. Now multiply that by four. That would be 840 amps combined draw on the system, and if you are drawing that much, something is really wrong. The point being that unless you have a short in the inverter, or an internal short in one of the batteries, the odds of blowing one of these MRBF fuses is extremely low. Even using 100 amp fuses with four batteries would take 560 amps to trip, and that would take 10 minutes to trip. So with a four battery bank, even if you have a spike of 560 amps, it would have to be sustained for 10 minutes to blow 100A fuses. For a four battery setup, a 150 amp fuse is more than adequate, allowing you more than plenty of overhead for surge spikes, but providing more protection, at a quicker rate, in case of an internal battery short, or any short for that matter. On the other hand, if one uses 200A fuses, like suggested, it would take about 10 minutes of a combined draw of 1120 amp to blow those fuses. At 200% load, that would be a combined 1600 amps to blow the fuses, and it would still take about 1.5 minutes to cut off. That is way to much unneeded overhead and does not provide enough protection on the larger battery banks. If it was a single battery, that is a different story, in that case, a 200A fuse would be appropriate. Everyone has their own safety threshold, look over the chart, do the math, and make you own decision.
Attached Thumbnails
Click image for larger version

Name:	terminal_fuse_delay_4.jpg
Views:	4
Size:	47.3 KB
ID:	437889  
__________________
'95 Safari Serengeti 38', 300hp 6CTA8.3L Cummins, 6spd. Allison, Pac brake, Magnum chassis, Valvet Ride (torsilastic susp.), VW Jetta TDI toad, Big tripple bay window (from floor to ceiling cabinets)!!!
beach house is offline   Reply With Quote
Old 04-07-2025, 09:47 AM   #7
Senior Member
 
Join Date: Apr 2024
Posts: 429
Quote:
Originally Posted by beach house View Post
The protection needs are different compared to lead acid batteries, and the key point of using MRBF fuses is to prevent thermal runaway of the Lithium battery bank in case the bms fails, especially during and internal battery short situation. Under those situations, every second counts. Attached is trip curve of the MRBF fuses per Blue Sea website. It shows that it takes about 10 minutes to blow an MRBF fuse at 140% load, and about 1.5 minutes to blow a fuse at 200% load. It logically makes sense that the bigger the battery bank is, the lower (with in reason) the MRBF fuse should be. For 4 batteries, the numbers show that a 150 amp fuse would be more that adequate. 140% of 150 amps is 210, so it would take about 10 minutes to blow a 150 MRBF fuse at 210 amps, if the bms fails to shut down. Now multiply that by four. That would be 840 amps combined draw on the system, and if you are drawing that much, something is really wrong. The point being that unless you have a short in the inverter, or an internal short in one of the batteries, the odds of blowing one of these MRBF fuses is extremely low. Even using 100 amp fuses with four batteries would take 560 amps to trip, and that would take 10 minutes to trip. So with a four battery bank, even if you have a spike of 560 amps, it would have to be sustained for 10 minutes to blow 100A fuses. For a four battery setup, a 150 amp fuse is more than adequate, allowing you more than plenty of overhead for surge spikes, but providing more protection, at a quicker rate, in case of an internal battery short, or any short for that matter. On the other hand, if one uses 200A fuses, like suggested, it would take about 10 minutes of a combined draw of 1120 amp to blow those fuses. At 200% load, that would be a combined 1600 amps to blow the fuses, and it would still take about 1.5 minutes to cut off. That is way to much unneeded overhead and does not provide enough protection on the larger battery banks. If it was a single battery, that is a different story, in that case, a 200A fuse would be appropriate. Everyone has their own safety threshold, look over the chart, do the math, and make you own decision.
so given that, you are using the wrong type of fuse to protect a LiFePO4 battery. what should be on each battery is a proper sized "T" classed fuse which is a fast acting fuse not a slow one, which is the perfect match for LiFePO4 batteries. it should be sized at 1.2 to 2X the maximum current through the battery.

sorry I missed that you were using a MRBF in the original post or I would have mentioned it then. LiFePO4 are not subject to thermal runaway like "other" lithium batteries a MBR isn't going to protect it in the way it needs to be protected, or in the way you think it will.
Stircrazy1 is offline   Reply With Quote
Old 04-09-2025, 02:27 PM   #8
Senior Member
 
Join Date: Jul 2013
Location: North East
Posts: 145
Quote:
Originally Posted by Stircrazy1 View Post
so given that, you are using the wrong type of fuse to protect a LiFePO4 battery. what should be on each battery is a proper sized "T" classed fuse which is a fast acting fuse not a slow one, which is the perfect match for LiFePO4 batteries. it should be sized at 1.2 to 2X the maximum current through the battery.

sorry I missed that you were using a MRBF in the original post or I would have mentioned it then. LiFePO4 are not subject to thermal runaway like "other" lithium batteries a MBR isn't going to protect it in the way it needs to be protected, or in the way you think it will.

Attached below is a link to Class T fuse trip curve (scroll to page 3), it shows a similar deal, but not as extreme. So, yes, they are faster acting, but still have a curve built in to prevent the fuse from blowing during reasonable spikes. The issue comes in when one has a large battery bank, of 4 or more batteries. Although LFP batteries are fairly stable and safe, they still can achieve thermal runaway, even though it is not as violent as some of the other Lithium chemistries. With either type of fuse, if one has a large battery bank, it is prudent to do the math and calculate what total spike you would expect in your system, and build in a bit of overhead, and then under-size the fuses for each individual battery, essentially building in an additional safety measure, in case something goes wrong. Many times, in RV applications, there are room constraints, where one does not have the room to place 6 individual class T fuses, but does have room for MRBF fuses. In those situation, especially if one moderatley under-sizes the fuses, it will provide protection, specifically in the case of a single battery shorting out, causing an inrush of power from the rest of the battery bank. In the case of a short, the inrush will be enough to easily and quickly trigger an MRBF fuse, but it can't hurt to look at the charts to fine tune things a bit more for a quicker trip. Basically my point is, one can build in additional safety, even when the choices are limited, all they have to do is some homework and math, and it is much better (provides much more safety) than having just one master fuse and no individual fuses for each battery. Put another way, is it perfect? No, nothing is ever 100% when it comes to safety, but it sure is better than nothing. It never hurts to get creative and to improvise, when working with certain constraints and still wanting to provide an additional safety cushion.


Link to Class T fuse graph: https://www.eaton.com/content/dam/ea...s-1025-jjn.pdf
__________________
'95 Safari Serengeti 38', 300hp 6CTA8.3L Cummins, 6spd. Allison, Pac brake, Magnum chassis, Valvet Ride (torsilastic susp.), VW Jetta TDI toad, Big tripple bay window (from floor to ceiling cabinets)!!!
beach house is offline   Reply With Quote
Reply

Tags
batteries, battery



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Battleborn four BB10012 battery bank failure guzmane76 RV Systems & Appliances 11 07-10-2024 02:13 PM
Cooling of Battleborn batteries rarebear.nm Class C Motorhome Discussions 3 04-22-2022 11:31 AM
Battleborn bb10012h batteries rarebear.nm Class C Motorhome Discussions 1 10-08-2021 10:18 AM
Experience with Renogy 12v 100AH Lithium Batteries? Jrhea Going Green 8 10-28-2018 04:39 PM
Battery bank cabling/fusing HHIDan Newmar Owner's Forum 12 02-10-2015 09:16 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:34 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, vBulletin Solutions, Inc.