109 VAC at PT50X - Ok or NO?

I have my Mountain Aire parked in the back yard about 200 ft from the house. There is a power pole (25A outdoor circuit) 50 ft out from the house and a 150 ft extension cord that is 10/3. I set the magnum shore power to 20 amps and also set the EMS on the Newmar to 20 amps. I have a Progressive Ind EMS-PT50X in line on the extension cords to the house.

I am showing about 109V (about 5% based on 115V) on the PT50X and I seem to be able to float charge or run the 1 front A/C at a pull of about 15 amps on the Newmar EMS. I am not running the charger and the front A/C at the same time.

I am assuming that the PT50X will ensure that I do no hurt the coach in any way. Is that correct? Am I missing something?

I just want a double check to make sure that the voltage is Ok prior to running the A/C or charger at length. Thanks in advance.
ColoradoBnd is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-03-2017, 02:02 PM   #2
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
The voltage spec is generally 120 +- 10%. That would make 108 the lower end it should pass without faulting.

If the power pole circuit has more than one outlet I would be inclined to check the voltage there just to see if a bigger cord would do any good.
nothermark is offline   Reply With Quote
Old 08-03-2017, 02:08 PM   #3
Senior Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Apr 2017
Location: Eden, UT
Posts: 418
The PT50X faults the voltage at 104 volts. If I assume 115V at the pole, the voltage calculators predict right at 108 volts. Thank you very much for your response.
ColoradoBnd is offline   Reply With Quote
Old 08-03-2017, 02:10 PM   #4
Senior Member
 
APhotoWizard's Avatar
 
Join Date: Jan 2014
Posts: 390
The nominal design voltage in the US is now 120 volts even though all the tables state 110. I would not use your configuration for my air conditioner. The voltage is too low and it will struggle when the weather is hot.

You can see from the table below that you need a larger wire, and I'll bet the wiring for the outside plug is also under sized for your needs.

I would devise a better plan.

Have a great day - Jerry

http://www.cerrowire.com/files/file/voltagedrop.pdf
__________________
My wife and I would travel full time, but we have to sleep occasionally.
2001 Tiffin Allegro Bus 40 ft DP named the Wild Eagle
Followed by the Eaglet - A 2014 Jeep Grand Cherokee.
APhotoWizard is offline   Reply With Quote
Old 08-03-2017, 02:28 PM   #5
Senior Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Apr 2017
Location: Eden, UT
Posts: 418
Just measured 119V at the pole.
ColoradoBnd is offline   Reply With Quote
Old 08-03-2017, 02:48 PM   #6
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
I'd be inclined to either get a bigger cord or set up a double extension cord setup. Even putting a 50 ft 30 or 50 Amp cord in the mix and a shorter extension cord would make a significant difference.
nothermark is offline   Reply With Quote
Old 08-03-2017, 02:55 PM   #7
Senior Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Apr 2017
Location: Eden, UT
Posts: 418
I can do that from the pole to the coach. The house to the pole would still be a choke point. I guess it would still help on the 150' run where I loose a lot of voltage, right? I know I have close to 119V static at the pole. Called dometic and they didn't help much. They mostly quoted the amps required which is not much of an issue. I will run 2 10awg from the pole tomorrow and see what my voltage does.
ColoradoBnd is offline   Reply With Quote
Old 08-04-2017, 12:20 PM   #8
Senior Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Apr 2017
Location: Eden, UT
Posts: 418
I called Newmar today and they had the exact answer. They are impressive. Anything above 105 V is acceptable. So as long as you are using a product like the EMS-PT50X there are no worries on voltage.
ColoradoBnd is offline   Reply With Quote
Old 08-07-2017, 10:44 AM   #9
Senior Member
 
computerguy's Avatar
 
Join Date: Jul 2010
Location: FT on the Road
Posts: 3,839
Quote:
Originally Posted by ColoradoBnd View Post
I called Newmar today and they had the exact answer. They are impressive. Anything above 105 V is acceptable. So as long as you are using a product like the EMS-PT50X there are no worries on voltage.
Hmmm. "no worries". Famous last words.
If it were me and I were going to have this situation on a regular basis I would be planning on premature failure of any device being run.
Lower voltage means higher amperage. That equates to higher heat and heat is any electronics enemy.
Call the AC manufacturer and ask them directly.
Best of luck to you and your decision to use this setup.
__________________
I don't subscribe to threads I reply to so will not see your reply to my comment. Drop me a direct message if you want a reply from me.
Cheers!
computerguy is offline   Reply With Quote
Old 08-07-2017, 10:57 AM   #10
Senior Member
 
xrated's Avatar
 
Join Date: Jan 2017
Location: "Murvul", TN
Posts: 1,665
Quote:
Originally Posted by ColoradoBnd View Post
I can do that from the pole to the coach. The house to the pole would still be a choke point. I guess it would still help on the 150' run where I loose a lot of voltage, right? I know I have close to 119V static at the pole. Called dometic and they didn't help much. They mostly quoted the amps required which is not much of an issue. I will run 2 10awg from the pole tomorrow and see what my voltage does.
The key word here is "static" or no load voltage. If the A/C unit is being used, and the distance of cord that you are talking about is being used, you will get a fairly large voltage drop when the load is applied. It may or may not operate, but running any AC motor on low voltage (if the EMS doesn't take it off line) is not good for the motor AND will result in the motor windings getting hot. Of course, the more load the motor sees, the higher the current will climb and it will eventually damage the motor windings......if the EMS doesn't drop it first.
__________________
2016 F350 Crew Cab Dually Diesel King Ranch 4x4
2018 Grand Design Momentum 394M Toy Hauler
Excessive Payload Capacity is a Wonderful Thing!
xrated is offline   Reply With Quote
Old 08-08-2017, 01:01 AM   #11
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
Quote:
Originally Posted by ColoradoBnd View Post
I can do that from the pole to the coach. The house to the pole would still be a choke point. I guess it would still help on the 150' run where I loose a lot of voltage, right? I know I have close to 119V static at the pole. Called dometic and they didn't help much. They mostly quoted the amps required which is not much of an issue. I will run 2 10awg from the pole tomorrow and see what my voltage does.
I wonder how it worked out. Should have cut your voltage drop from the pole to the RV in half or around 114 VAC. That should be manageable. If that is a long term setup think about burying some #6.
nothermark is offline   Reply With Quote
Old 08-08-2017, 11:44 AM   #12
Senior Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Apr 2017
Location: Eden, UT
Posts: 418
I doubled up on the #10 extension cord to improve the voltage drop. Now I have to find a male-male-female #10 adapter. Haven't found one yet. I guess I will have to make one myself.
ColoradoBnd is offline   Reply With Quote
Old 08-08-2017, 10:08 PM   #13
Senior Member
 
Duner's Avatar
 
Winnebago Owners Club
Workhorse Chassis Owner
Join Date: Jul 2002
Location: Camarillo, CA ---Back in the house after 7 yrs fulltiming
Posts: 1,652
It's not clear to me which end of the cord you have the Progressive EMS. Near the source or right at the coach end? If you have it measuring voltage at the pedestal and then running the long cord to the coach, it's not seeing the voltage that the coach is actually getting.

I have a Hughes Autoformer to boost low voltage and the built in Progressive EMS wired in after the Hughes and both inside my power compartment. So EMS sees the voltage after the power cord and before it gets distributed inside the coach.

If you are measuring 108 volts with the ac running, then it's very probable that when the ac compressor is starting the voltage is dropping a whole lot more during startup. With 11 volt drop in the cord and connectors (119-108 = 11 v) in the steady state, then my guess is an additional drop of 5-10 volts during motor startup. Anything below 100 volts at startup will shorted the life of the a/c unit. Ditto with the microwave.

A few years back I was at my cousin's farm for 3 months. I used two 50 ft extension cords thinking the Hughes will boost the voltage back up so I could use my basement a/c in heat pump mode on the colder nights. After being parked for 2.5 months I was braking camp and the connection point where the two cords were plugged together would not come apart. The plastic plug/socket was melted together at the surface. It took box cutter to separate them. Running anything near 20-30 amps on extension cords is asking for problems.
__________________
Bill & dear wife Helen
Last of the Chieftains, 2004 39T, W22, UP tune, Banks, Koni's, Safe-T-Plus, SMI brake
2017 Lincoln MKZ Hybrid towed 4-down or my 2008 Jeep Wrangler JK
https://www.irv2.com/attachments/signaturepics/sigpic23522_1.gif]
Duner is offline   Reply With Quote
Old 08-10-2017, 06:47 AM   #14
Senior Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Apr 2017
Location: Eden, UT
Posts: 418
Thanks for the reply. The 50x is at the coach with the extension cords running from the pole to the 50x.
ColoradoBnd is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
ISC 330 with 109,000 miles, good or bad? Prospect Cummins Engines 10 10-28-2016 11:26 PM
Question:Kumho 205R14 109/107QD tires bubbajean Travel Trailer Discussion 5 06-14-2013 09:55 PM
109 degrees unfinished91 Excel Owner's Forum 9 08-08-2011 04:43 PM
Reynolds Handi-Vac Vacuum Sealer Lorna RV Gourmet 1 11-19-2007 04:52 PM
Vel Vac mirrors rmmpe Alpine Coach Owner's Forum 12 10-12-2007 02:22 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 01:28 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.