110V Short in Coach
We have a 2008 Fleetwood Revolution LE, when I plugged to shore power on this trip the Surge Guard Protector (permanent mounted) kept tripping about 10 sec. after engaging. It showed green light for both lines, showing good.
Flipped over to Generator power and everything runs fine.
Checked EMS panel no smell, no melted or charred wires. Checked the transfer switch, everything looks good, can see contact engage when Generator kicks in and return when turned off.
Figured issue was surge protector was bad, bypassed the surge protector.
ALL works well, until you touch the unit and get a shock like an electric fence. Of course I pulled power immediately.
I am thinking I must have short between shore power and transfer switch, but looking for thoughts from anyone.
Please share
__________________
Thomas Lefler
2008 Fleetwood Revolution LE 42K
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
07-01-2018, 08:10 AM
|
#2
|
Senior Member
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 31,442
|
Welcome to iRV2.
Sorry you're here with problems .
If your wiring was shorted , the power post circuit breaker should have tripped. If not before you by passed the surge guard ; then after.
The shock you get when touching the RV when on shore power ; commonly called " hot skin" is most commonly caused by miss wired power and neutral in the supply .
Was this problem only apparent on one power post ?
Did you contact the park and have the post wiring checked , or switch to another post or site?
When you by-passed the hard wired surge guard , did you get all the wires correct?
Can you see the wiring between the surge guard and the ATS , or are they in separate compartments?
EDIT: Could you add the brand name of the surge protector to you post .
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
|
|
|
07-01-2018, 09:24 AM
|
#3
|
Member
Fleetwood Owners Club
Join Date: Jun 2012
Location: Hope, IN
Posts: 68
|
Quote:
Originally Posted by Skip426
Welcome to iRV2.
Sorry you're here with problems .
If your wiring was shorted , the power post circuit breaker should have tripped. If not before you by passed the surge guard ; then after.
The shock you get when touching the RV when on shore power ; commonly called " hot skin" is most commonly caused by miss wired power and neutral in the supply .
Was this problem only apparent on one power post ?
Did you contact the park and have the post wiring checked , or switch to another post or site?
When you by-passed the hard wired surge guard , did you get all the wires correct?
Can you see the wiring between the surge guard and the ATS , or are they in separate compartments?
EDIT: Could you add the brand name of the surge protector to you post .
|
Thanks Skip426
We had the grounds electrician come over. Post are good, started to shutting down breakers and found the water heater has a short in it.
Thanks for the questions.
Surge protector is a Surge Guard model 35550
__________________
Thomas Lefler
2008 Fleetwood Revolution LE 42K
|
|
|
07-01-2018, 09:41 AM
|
#4
|
Senior Member
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 31,442
|
A full short of the water heater element should have tripped the circuit breaker in the coach . ; particularly after you by-passed the surge guard.
I'd be interested to see a photo of the old element , when you've changed it.
What brand and model of WH ?
Odd electrical issues , fascinate me.
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
|
|
|
07-01-2018, 10:40 AM
|
#5
|
Senior Member
Join Date: Jul 2014
Posts: 35,417
|
Water heater coils have a resistance wire insulated inside the outer copper covering.
When they run without water, the wire burns thru the insulation and shorts to the outer cover. That causes a short to ground and depending ever it burnt thru, how many amps it can draw. 1/2 way thru, it won't trip the breaker.
If you got a hot skin, there is still a ground issue. The straycurrent should have gone back to the power post ground.
Sent from my VS835 using iRV2 - RV Forum mobile app
|
|
|
07-01-2018, 12:40 PM
|
#6
|
Senior Member
Join Date: Jan 2016
Location: Northridge, CA
Posts: 1,218
|
The easy way to start any 120v electrical troubleshooting is to turn all breakers off then energize one by one and turning off each as you go. If no trouble then turn all off and turn on leaving each off until trouble is encountered.
This will narrow searches quickly.
Sent from my SM-G935P using iRV2 - RV Forum mobile app
__________________
Harry Grace
KM6ZRG
|
|
|
07-01-2018, 01:10 PM
|
#7
|
Senior Member
Join Date: Jul 2000
Location: Yankton, SD
Posts: 324
|
Quote:
Originally Posted by IndyHntr
We have a 2008 Fleetwood Revolution LE, when I plugged to shore power on this trip the Surge Guard Protector (permanent mounted) kept tripping about 10 sec. after engaging. It showed green light for both lines, showing good.
Flipped over to Generator power and everything runs fine.
Checked EMS panel no smell, no melted or charred wires. Checked the transfer switch, everything looks good, can see contact engage when Generator kicks in and return when turned off.
Figured issue was surge protector was bad, bypassed the surge protector.
ALL works well, until you touch the unit and get a shock like an electric fence. Of course I pulled power immediately.
I am thinking I must have short between shore power and transfer switch, but looking for thoughts from anyone.
Please share
|
Bypassing a safety device doesnt mean it is bad. The data still indicates you dont have a short but an open. Hook everything back up the way you started and begin again. Look closer at the surge protector lights.
https://rvpower.southwire.com/wp-con...0117-B-DSG.pdf
The word of the "grounds electrician" can not be taken as the truth.
__________________
George
2011 Ford F350 DRW
2015 Mobile Suites 41RSSB4
|
|
|
07-02-2018, 04:23 AM
|
#8
|
Member
Fleetwood Owners Club
Join Date: Jun 2012
Location: Hope, IN
Posts: 68
|
Thanks for all the feedback. So I also am not 100% positive what the exact issue is, as we have not pulled the water heater yet. There are two switches at the kitchen sink, one for propane and one for the water heater to run on 110 electrical. When you turn on the 110 switch, we get the “hot skin”, my meter reads 48v. Turn the switch off and the “hot skin” goes away. I al taking a simple meter, not digital and push the wires probe into the dirt and touching the probe to one of the bay doors. We have had unit for 3weeks and the dealer had to replace the heating element as it did not work in our walk through. And the water is really hot, so I think the thermostat is bad also.
Surge protector lights, line1 & 2 always green, caution light flashes for the 2 min, 15 sec. delay, then power light goes green. For about 15 sec. the protector cuts power and caution light flashes again, until power reset.
Again, thanks for all the input. Keep sending ideas
__________________
Thomas Lefler
2008 Fleetwood Revolution LE 42K
|
|
|
07-02-2018, 07:36 AM
|
#9
|
Senior Member
Join Date: Jul 2000
Location: Yankton, SD
Posts: 324
|
Quote:
Originally Posted by IndyHntr
Thanks for all the feedback. So I also am not 100% positive what the exact issue is, as we have not pulled the water heater yet. There are two switches at the kitchen sink, one for propane and one for the water heater to run on 110 electrical. When you turn on the 110 switch, we get the “hot skin”, my meter reads 48v. Turn the switch off and the “hot skin” goes away. I al taking a simple meter, not digital and push the wires probe into the dirt and touching the probe to one of the bay doors. We have had unit for 3weeks and the dealer had to replace the heating element as it did not work in our walk through. And the water is really hot, so I think the thermostat is bad also.
Surge protector lights, line1 & 2 always green, caution light flashes for the 2 min, 15 sec. delay, then power light goes green. For about 15 sec. the protector cuts power and caution light flashes again, until power reset.
Again, thanks for all the input. Keep sending ideas
|
Well there you go. If you look at the link I sent, you can see that there is a problem with the incoming power.
__________________
George
2011 Ford F350 DRW
2015 Mobile Suites 41RSSB4
|
|
|
07-02-2018, 10:12 AM
|
#10
|
Senior Member/RVM #90
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,768
|
Hi ! Welcome to IRV2! We're sure glad you joined the gang!
I would move to a different part of the CG and see what happens.
Good luck, happy trails, and God bless!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
|
|
|
07-02-2018, 02:15 PM
|
#11
|
Member
Fleetwood Owners Club
Join Date: Jun 2012
Location: Hope, IN
Posts: 68
|
Quote:
Originally Posted by Fulltimer
Well there you go. If you look at the link I sent, you can see that there is a problem with the incoming power.
|
I will hook everything back up tonight and see what happens. Will give feedback later.
__________________
Thomas Lefler
2008 Fleetwood Revolution LE 42K
|
|
|
07-02-2018, 02:59 PM
|
#12
|
Registered User
Join Date: Jul 2018
Posts: 24
|
I would venture another 'guess'... a neutral wire has rubbed/scraped/pinched and is touching metal, probably at or within the water heater...especially since this was 'just worked on' by an RV shop.
Your surge protector is sensing this 'open neutral' and is protecting you from the 'hot skin' situation.
GA RV Insurance
|
|
|
07-02-2018, 09:12 PM
|
#13
|
Member
Fleetwood Owners Club
Join Date: Jun 2012
Location: Hope, IN
Posts: 68
|
Quote:
Originally Posted by IndyHntr
I will hook everything back up tonight and see what happens. Will give feedback later.
|
Ok, hooked everything back up the way it was from beginning. NO ISUES!!
I will call the RV park grounds manager tomorrow to tell them to take another look at their pole. Must be on their side.
__________________
Thomas Lefler
2008 Fleetwood Revolution LE 42K
|
|
|
07-03-2018, 02:40 AM
|
#14
|
Member
Fleetwood Owners Club
Join Date: Jun 2012
Location: Hope, IN
Posts: 68
|
I will still have the wiring to the water heater looked at. Better safe than sorry.
__________________
Thomas Lefler