My sister lives in an Open Range 50 amp 5th wheel as her permanent residence, plugged into a power receptacle she had put in. She has always HATED the propane appliances. She does not use the furnace; both roof air conditioners are out of service, she has window air conditioners. Her gas wall oven recently also went bad, so she has purchased a 20" electric range, 220V. My question is: how should this new stove be wired into the circuit breaker box? I know there are 50 amps on each side. The stove requires 2 20amp breakers. Any help would be appreciated.
|
|
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
06-28-2022, 08:41 AM
|
#2
|
Senior Member
Join Date: Oct 2014
Posts: 7,284
|
You will need to get a 50 amp duplex breaker.
So, new wires from each of those breakers (one will be L1, the other L2) plus a neutral and ground from their respective buss bars.
Wire size appropriate for 50 amps from there to the stove.
Make sure she is aware that she will need to "energy manage" if stove and oven draw approaches the 50 amps.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
|
|
|
06-28-2022, 09:04 AM
|
#3
|
Junior Member
Join Date: Aug 2011
Posts: 15
|
another question
Thanks for your quick reply. I have another question: In the breaker box, there is a two pole breaker, each pole 20. One pole is marked a/c, which she doesn't use, and the other pole, marked Conv, has been switched off since she bought the rv. So could that breaker be used for the stove?
|
|
|
06-28-2022, 09:19 AM
|
#4
|
Senior Member
Join Date: Nov 2005
Posts: 7,301
|
Generally speaking, a 20-amp 220v stove shouldn't be an issue with a 50-amp RV. However, this assumes pedestal is properly wired for 50-amp phased power [true 220v measured across the two hots]. Modern wiring usually requires two hots, a neutral, and a ground, so OEM wiring may be an issue. Have seen some RV breaker boxes not set up for phased power, so a std double pole breaker doesnt achieve the required 220v phased power. IMHO, this is a bit beyond the typical DIY project--if in doubt, get a professional involved.
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
|
|
|
06-28-2022, 10:01 AM
|
#5
|
Senior Member
Join Date: Jul 2014
Posts: 34,251
|
Quote:
Originally Posted by deedeeg
Thanks for your quick reply. I have another question: In the breaker box, there is a two pole breaker, each pole 20. One pole is marked a/c, which she doesn't use, and the other pole, marked Conv, has been switched off since she bought the rv. So could that breaker be used for the stove?
|
It depends on the layout of the panel but probably not.
If the main 50 amp breaker is in the center with breakers right and left, then that 50 amp breaker needs to come out and relpaced with a quad breaker.
The quad breaker will have a linked pair of 50 amp breakers and a pair of linked 20 amp breakers.
|
|
|
06-28-2022, 10:32 AM
|
#6
|
Senior Member
Fleetwood Owners Club Workhorse Chassis Owner
Join Date: Feb 2000
Location: San Jose, Ca, USA
Posts: 2,539
|
Quote:
Originally Posted by twinboat
It depends on the layout of the panel but probably not.
If the main 50 amp breaker is in the center with breakers right and left, then that 50 amp breaker needs to come out and relpaced with a quad breaker.
The quad breaker will have a linked pair of 50 amp breakers and a pair of linked 20 amp breakers. Attachment 369551
|
And simply replacing the breaker won't complete the installation - you need to find the other end of the wires fed by the breakers and reroute them to the stove.
__________________
Alan Hepburn - San Jose, Ca
2007 Bounder 35E being pushed by a 2020 Jeep Gladiator Sport S or a 2022 Jeep Wrangler Unlimited (JLU) Sport S
|
|
|
 |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|