30A GFCI Shore Pedestal Breakers Broke

I recently encountered shore power pedestals with 30A GFCI breakers. One was at an Illinois State Park and the other at a Minnesota State Park. On both occasions, when I plugged my 50A couch into the pedestal via an adapter, I could not put shore power to my 3KW inverter/charger without tripping the pedestal GFCI breaker. Of course, without the charger portion of my inverter available, I could not recharge my batteries.

Note that this power scenario has not been a problem for me with non-GFCI 30A power pedestals, either before or since. Also, my 3KW inverter/charger works great, but it is 2001 technology.

I did some online research and found that this is becoming a significant problem for the marine industry. Boaters may not be able to use updated shore power that employs GFP (ground fault protection), a 2011 NEC mandated technology for marinas and shipyards similar to GFCI. Apparently the power up sequence of an inverter/charger can appear to the pedestal GFCI as a voltage leak, so TRIP.

One article even suggested going through a myriad of power up sequence scenarios from all breakers OFF, but none of those worked unless I left the inverter/charger OFF. (At one park, a tech even replaced the 30A GFCI breaker at the pedestal, but that did not help.) He also said the problem I was experiencing was all too common with their 30A GFCI, but not their 50A GFCI pedestals. Unfortunately, I was not able to test the latter scenario.

My question is, short of investing in a very expensive Isolation Transformer (or other equally expensive changes to the perfectly good power systems on my rig), does anyone have a reasonable solution for this? I hate to avoid state parks in my travels, but apparently many states are early adopters of 30A GFCI pedestal outlets.
__________________
TomAndPeg
TomAndPeg is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-11-2018, 04:33 PM   #2
Senior Member
 
Jthigh's Avatar
 
Join Date: Dec 2017
Location: Charlotte, NC
Posts: 532
I have the same issue with my system. Everything in my coach is original and never have any issue with non-gfi service. If plugged into a GFI outlet it trips as soon as my inverter/battery charger comes online to charge house batteries. I plan to investigate solutions this winter but unable to provide any solutions at this time.
__________________
2002 American Eagle 40M
ISL400 / Spartan MM
2003 Jeep Liberty/2019 Jeep Trailhawk
Jthigh is offline   Reply With Quote
Old 11-11-2018, 04:51 PM   #3
Senior Member
 
Join Date: Jul 2014
Posts: 35,402
Pick up a standalone converter charger.
Something like a GoPower 55 will handle the charging. Just wire it to the battery bank and plug it in. Leave the inverter/charger off.
twinboat is offline   Reply With Quote
Old 11-11-2018, 07:21 PM   #4
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
The problem is the clueless person who specified GFCI's for RV or Marine power connections. They are *NOT* the correct answer as the shore cord is part of the distribution system not a load branch circuit.
nothermark is offline   Reply With Quote
Old 11-11-2018, 07:24 PM   #5
Senior Member
 
TomAndPeg's Avatar
 
Monaco Owners Club
Newmar Owners Club
Fleetwood Owners Club
Join Date: May 2012
Location: Downers Grove, IL
Posts: 541
Blog Entries: 66
Quote:
Originally Posted by twinboat View Post
Pick up a standalone converter charger.
Something like a GoPower 55 will handle the charging. Just wire it to the battery bank and plug it in. Leave the inverter/charger off.


Thanks! I think this is a good workaround for the batteries, but there is an additional problem: the inverter also routes AC power to a bunch of outlets, regardless of the power source. No inverter also means no power to those outlets. That said, in the absence of a better solution, I think I will invest in a stand-alone charging system as a hedge.
__________________
TomAndPeg
TomAndPeg is offline   Reply With Quote
Old 11-11-2018, 08:03 PM   #6
Senior Member
 
Rkesselus's Avatar
 
Tiffin Owners Club
Join Date: Aug 2016
Location: Bastrop Texas
Posts: 1,343
Most building codes require a GFCI breaker for any 20 amp circuit so that is what happens when using a cheater( adaptor) using a 30 amp RV plug and a 20 amp plug to get you 50 Amps. The transfer switch causes the GFCI to read an extra ground and trips. I carry a non GFCI duplex plug and change it out if we stay in one spot for any length of time.
__________________
2000 Allegro Bus 35R 3126 Cat 300 Allison 3060MD 6 speed
Rkesselus is offline   Reply With Quote
Old 11-11-2018, 09:53 PM   #7
Senior Member
 
Props2's Avatar
 
Tiffin Owners Club
Join Date: Apr 2018
Location: McHenry, Illinois
Posts: 392
I can see them wanting gfi's for the 20a circuit. For the 30's, I dont know why they dont use EPD breakers that have a 30ma threshold. I am thinking the rfi suppression filters leak enough to trip the 5ma gfi's? But that's just a guess. I know its all about personal protection,but geez, how many people are plugging hand held appliances in a 30a. Its all about AHJ's.(authority having jurisdiction)

So yes....yes, a transformer would be needed to add to your arsenal or some new fangled device on the market.
__________________
2015 Tiffin Phaeton 40QKH All Electric
2015 Dodge Ram Laramie 4x4
Mark and Lori
Props2 is offline   Reply With Quote
Old 11-12-2018, 05:42 AM   #8
Senior Member
 
Jthigh's Avatar
 
Join Date: Dec 2017
Location: Charlotte, NC
Posts: 532
Quote:
Originally Posted by nothermark View Post
The problem is the clueless person who specified GFCI's for RV or Marine power connections. They are *NOT* the correct answer as the shore cord is part of the distribution system not a load branch circuit.
Agreed, as a former technician the main power distribution panel is in the coach not the pedestal.
__________________
2002 American Eagle 40M
ISL400 / Spartan MM
2003 Jeep Liberty/2019 Jeep Trailhawk
Jthigh is offline   Reply With Quote
Old 11-12-2018, 06:03 AM   #9
Senior Member
 
Monaco Owners Club
Join Date: Sep 2013
Posts: 2,497
I have had that problem when I first connect and the charger starts a bulk or equalizing charge. I have found if I leave everything but the charger off for 15 minutes or so when the charger reduces its amp load it resolves the problem. The other work around I do if I want A/C immediately is turn the charger off until the A/C load is reduced.
__________________
2014 Newell 2020P 45'8" ISX 600 HP
hypoxia is offline   Reply With Quote
Old 11-12-2018, 07:09 AM   #10
Senior Member
 
TomAndPeg's Avatar
 
Monaco Owners Club
Newmar Owners Club
Fleetwood Owners Club
Join Date: May 2012
Location: Downers Grove, IL
Posts: 541
Blog Entries: 66
Quote:
Originally Posted by Rkesselus View Post
Most building codes require a GFCI breaker for any 20 amp circuit so that is what happens when using a cheater( adaptor) using a 30 amp RV plug and a 20 amp plug to get you 50 Amps. The transfer switch causes the GFCI to read an extra ground and trips. I carry a non GFCI duplex plug and change it out if we stay in one spot for any length of time.
Thanks Rkesseslus: I actually thought about making a run to Home Depot to buy a 30A non-GFCI breaker to swap out, but went to another campground instead. I have no doubt that any state park would frown on doing a breaker swap. And if I did it, I would surely forget to re-swap when I left.
__________________
TomAndPeg
TomAndPeg is offline   Reply With Quote
Old 11-12-2018, 07:14 AM   #11
Senior Member
 
TomAndPeg's Avatar
 
Monaco Owners Club
Newmar Owners Club
Fleetwood Owners Club
Join Date: May 2012
Location: Downers Grove, IL
Posts: 541
Blog Entries: 66
Quote:
Originally Posted by hypoxia View Post
I have had that problem when I first connect and the charger starts a bulk or equalizing charge. I have found if I leave everything but the charger off for 15 minutes or so when the charger reduces its amp load it resolves the problem. The other work around I do if I want A/C immediately is turn the charger off until the A/C load is reduced.
Thanks, hypoxia. I'm not sure if I can turn the charger portion of the inverter OFF/ON, but if I can I'll certainly try this.
__________________
TomAndPeg
TomAndPeg is offline   Reply With Quote
Old 11-29-2018, 09:30 PM   #12
Senior Member
 
TomAndPeg's Avatar
 
Monaco Owners Club
Newmar Owners Club
Fleetwood Owners Club
Join Date: May 2012
Location: Downers Grove, IL
Posts: 541
Blog Entries: 66
Quote:
Originally Posted by thomaspryan View Post
Thanks, hypoxia. I'm not sure if I can turn the charger portion of the inverter OFF/ON, but if I can I'll certainly try this.


As a follow-up, it turns out that I can run my inverter with the charge function OFF. Next time I encounter a 30A GFCI, I will try Hypoxia’s method of power-up the inverter functions. If that doesn’t work, I’ll invest in an independent charging system.
__________________
TomAndPeg
TomAndPeg is offline   Reply With Quote
Old 11-30-2018, 07:06 AM   #13
Senior Member
 
Fiesta48's Avatar
 
Fleetwood Owners Club
Freightliner Owners Club
Join Date: Nov 2010
Location: Texas
Posts: 4,283
I also had this 30A GFCI problem. Ft Peck MT. Electrician said they were having this problem with newer 50A systems. Finally moved to a 50A pedistal.
__________________
Full Timers.
2015 Fleetwood Discovery 40E on a Freightliner XCS chassis with a Cummins ISL9 pulling 1 and/or 2 motorcycles, '07 Honda Accord OR a 17' Runabout Boat.
Fiesta48 is offline   Reply With Quote
Reply

Tags
breaker



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bounder: 2016 Bounder 33C - GFCI keeps tripping (Internal to RV, not house GFCI) nehmia Fleetwood Owner's Forum 8 10-22-2016 07:34 AM
Use of 50A Surge Protector with 30A Pigtail for 30A Shore Power hugh37 Newmar Owner's Forum 9 07-08-2016 01:14 PM
Coach GFCI breakers trip on inverter steined Monaco Owner's Forum 2 10-20-2015 05:26 PM
A/C breakers trip constantly...even on 50a shore power MisterT Palazzo Motorhomes 9 07-18-2015 11:20 AM
Genset 20a and 30a breakers '04 Southwind Agility57 RV Systems & Appliances 48 07-25-2013 07:27 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 03:58 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.