50 Amp Power Distribution in RV

Just a couple of curious questions here.

I understand that the standard RV "50" amp receptacle provides two 50 amp 120 volt legs. So when a properly wired RV is connected to the "50" amp service are the two legs recombined somehow inside the RV as one 100 amp service or are they kept separate into two separate power circuits? Or, is it done either way depending on the manufacturer?

I assume that 30 amp service provided at the pole is just one of the 50 amp legs on a 30 amp circuit breaker. Does a reasonably managed campground ensure that there is a balanced distribution of sites wired to use either leg or does that matter at all?
__________________
Rosie and Bob (SFC USA Ret. 1998) FMCA No. F474327 - Boondockers Welcome
2015 Tiffin Allegro Open Road 36LA, 2015 Ford Edge Titanium
There are three types of people. Those that can count and those that cannot.
oldSarge98 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-12-2018, 07:51 AM   #2
Senior Member
 
FlyingDiver's Avatar
 
Newmar Owners Club
Join Date: May 2007
Location: Somewhere....
Posts: 4,054
No, it's not combined into a 100amp feed. It's always two 50 amp feeds. If you have any 240V loads (like a residential style dryer), then the panel will be set up basically the same as a home 240V panel with a double breaker for the dryer. In any case, the various loads in the RV will be split between the two legs. How even the split is really depends on your usage of the loads. I moved a couple of mine around in the panel to even them up for our "normal" usage.

A properly wired campground will alternate legs for the 30amp plugs. It does matter.
__________________
2008 King Aire 4562, Spartan K3(GT) w/ Cummins ISX 600
2014 Jeep Grand Cherokee Overland 5.7L V8 Hemi w/ Blue Ox Aventa LX Tow Bar and baseplate, SMI Air Force One brake
FlyingDiver is offline   Reply With Quote
Old 06-12-2018, 08:00 AM   #3
Senior Member
 
oldSarge98's Avatar
 
Tiffin Owners Club
Ford Super Duty Owner
Join Date: Feb 2010
Location: Terrell County, Georgia
Posts: 206
Quote:
Originally Posted by FlyingDiver View Post
No, it's not combined into a 100amp feed . . .
A properly wired campground will alternate legs for the 30amp plugs. It does matter.
Thank you! Curios mind satiated.
__________________
Rosie and Bob (SFC USA Ret. 1998) FMCA No. F474327 - Boondockers Welcome
2015 Tiffin Allegro Open Road 36LA, 2015 Ford Edge Titanium
There are three types of people. Those that can count and those that cannot.
oldSarge98 is offline   Reply With Quote
Old 06-12-2018, 08:08 AM   #4
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
Kept separate in the RV breaker box as in a home breaker box. Every other breaker slot on one leg. Branch circuits are balanced. For example if two air conditioners, one connected to each leg.

Few RV have 240v appliances. Laundry dryers are Typically 120v appliances, etc. However some do have 240v cooktop or laundry dryer.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 06-12-2018, 08:26 AM   #5
Senior Member
 
Join Date: Jul 2014
Posts: 35,415
Actually the power box should be wired for 80 amps. A 50 and 30 on one leg and a 50 and 20 on the other.
twinboat is offline   Reply With Quote
Old 06-12-2018, 08:37 AM   #6
RV Mutant #14
 
Wayne M's Avatar


 
Winnebago Owners Club
Texas Boomers Club
Freightliner Owners Club
iRV2 No Limits Club
Join Date: Aug 2008
Location: Texas
Posts: 17,208
For future use, I found this web site very informative:
RV Electric
__________________
Wayne MSGT USMC (Ret) & Earlene (CinCHouse) RVM14 (ARS: KE5QG)
Lexi - Goldendoodle
2015 Winnebago Tour 42QD - 2020 Lincoln Nautilus Reserve
It is what it is, and then it is what you make of it.
Wayne M is offline   Reply With Quote
Old 06-12-2018, 09:10 AM   #7
Senior Member
 
oldSarge98's Avatar
 
Tiffin Owners Club
Ford Super Duty Owner
Join Date: Feb 2010
Location: Terrell County, Georgia
Posts: 206
Quote:
Originally Posted by Wayne M View Post
For future use, I found this web site very informative:
RV Electric
Yes, I have viewed that site on many occasions but I may have missed it but I believe most if not all information is about the electrical supply and not the internal RV circuits.
__________________
Rosie and Bob (SFC USA Ret. 1998) FMCA No. F474327 - Boondockers Welcome
2015 Tiffin Allegro Open Road 36LA, 2015 Ford Edge Titanium
There are three types of people. Those that can count and those that cannot.
oldSarge98 is offline   Reply With Quote
Old 06-12-2018, 09:19 AM   #8
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
Quote:
Originally Posted by twinboat View Post
Actually the power box should be wired for 80 amps. A 50 and 30 on one leg and a 50 and 20 on the other.
Huh? Which "power box" do you mean?
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Old 06-12-2018, 09:29 AM   #9
Senior Member
 
FlyingDiver's Avatar
 
Newmar Owners Club
Join Date: May 2007
Location: Somewhere....
Posts: 4,054
Quote:
Originally Posted by twinboat View Post
Actually the power box should be wired for 80 amps. A 50 and 30 on one leg and a 50 and 20 on the other.
I think you're referring to to a park pedestal. That is correct if the pedestal has all three outlets on it. Not all do. Some only have 50 and 30, some only have 50, depending on the park.

In any case, the the 30 amp outlet should alternate between legs around the park.

And normally they would only be wired for 50 amps because MOST RV lots are only designed for one unit. So either the 50 amp OR the 30 amp would be in use at any one time.
__________________
2008 King Aire 4562, Spartan K3(GT) w/ Cummins ISX 600
2014 Jeep Grand Cherokee Overland 5.7L V8 Hemi w/ Blue Ox Aventa LX Tow Bar and baseplate, SMI Air Force One brake
FlyingDiver is offline   Reply With Quote
Old 06-12-2018, 09:33 AM   #10
RV Mutant #14
 
Wayne M's Avatar


 
Winnebago Owners Club
Texas Boomers Club
Freightliner Owners Club
iRV2 No Limits Club
Join Date: Aug 2008
Location: Texas
Posts: 17,208
Quote:
Originally Posted by oldSarge98 View Post
Yes, I have viewed that site on many occasions but I may have missed it but I believe most if not all information is about the electrical supply and not the internal RV circuits.

Sarge, absolutely correct.



I think my point was that things have to be correct up to the point where one plugs into the pedestal. From there on it is a complete different set of schematics.
__________________
Wayne MSGT USMC (Ret) & Earlene (CinCHouse) RVM14 (ARS: KE5QG)
Lexi - Goldendoodle
2015 Winnebago Tour 42QD - 2020 Lincoln Nautilus Reserve
It is what it is, and then it is what you make of it.
Wayne M is offline   Reply With Quote
Old 06-12-2018, 09:43 AM   #11
Senior Member
 
oldSarge98's Avatar
 
Tiffin Owners Club
Ford Super Duty Owner
Join Date: Feb 2010
Location: Terrell County, Georgia
Posts: 206
Quote:
Originally Posted by FlyingDiver View Post
No, it's not combined into a 100amp feed . . . In any case, the various loads in the RV will be split between the two legs. How even the split is really depends on your usage of the loads.
Thanks to all for handling my curiosity to this point. Now concerning the idea that the two legs are routed to two circuits within the RV how then is a 30 amp supply routed to both circuits in the RV so you can use both AC units? Am I correct to guess that the RV transfer switch has some kind of relay that jumps the two circuits when 30 amp service is detected?
__________________
Rosie and Bob (SFC USA Ret. 1998) FMCA No. F474327 - Boondockers Welcome
2015 Tiffin Allegro Open Road 36LA, 2015 Ford Edge Titanium
There are three types of people. Those that can count and those that cannot.
oldSarge98 is offline   Reply With Quote
Old 06-12-2018, 09:48 AM   #12
Senior Member
 
FlyingDiver's Avatar
 
Newmar Owners Club
Join Date: May 2007
Location: Somewhere....
Posts: 4,054
Quote:
Originally Posted by oldSarge98 View Post
Thanks to all for handling my curiosity to this point. Now concerning the idea that the two legs are routed to two circuits within the RV how then is a 30 amp supply routed to both circuits in the RV so you can use both AC units? Am I correct to guess that the RV transfer switch has some kind of relay that jumps the two circuits when 30 amp service is detected?
No, it's done in the dog-bone adapter. The one hot lead from the pedestal is connected to both hot leads in the 50 amp outlet on the adapter.
__________________
2008 King Aire 4562, Spartan K3(GT) w/ Cummins ISX 600
2014 Jeep Grand Cherokee Overland 5.7L V8 Hemi w/ Blue Ox Aventa LX Tow Bar and baseplate, SMI Air Force One brake
FlyingDiver is offline   Reply With Quote
Old 06-12-2018, 11:36 AM   #13
Senior Member
 
oldSarge98's Avatar
 
Tiffin Owners Club
Ford Super Duty Owner
Join Date: Feb 2010
Location: Terrell County, Georgia
Posts: 206
Quote:
Originally Posted by FlyingDiver View Post
No, it's done in the dog-bone adapter. The one hot lead from the pedestal is connected to both hot leads in the 50 amp outlet on the adapter.
Thanks. Goes to show the simplest solution is the best.
__________________
Rosie and Bob (SFC USA Ret. 1998) FMCA No. F474327 - Boondockers Welcome
2015 Tiffin Allegro Open Road 36LA, 2015 Ford Edge Titanium
There are three types of people. Those that can count and those that cannot.
oldSarge98 is offline   Reply With Quote
Reply

Tags
power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
February "Celebrity Classic" Meal Signups Madame Boomer Texas Boomers 29 02-06-2018 06:55 PM
Partial power loss on Power Distribution panel MikeandBecky Class A Motorhome Discussions 16 02-17-2015 06:01 PM
RVupgrades - New Battery Chargers, Weight Distribution & Deal of the Day Warpath Vendor Spotlight (Deals, Announcements & More) 0 11-04-2011 09:03 AM
Modern Weight Distribution & Sway Control ???? clarkgriswold Travel Trailer Discussion 3 09-26-2011 07:35 PM
WFCO 55 AMP distribution center mx842 MH-General Discussions & Problems 14 05-18-2010 08:19 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 01:07 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.