50amp to 30amp adapter
I booked a 50 amp site by mistake. I went and purchased the dog bone adapter that goes from 50amp to 30amp. Can I plug the dog bone into my surge protector and the my surge protector into my camper? Or does the dog bone go straight from the box to the camper? Thanks!
|
|
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
06-17-2022, 08:43 PM
|
#2
|
Junior Member
Join Date: Apr 2022
Posts: 20
|
We put our surge protector between the camper and dogbone.
|
|
|
06-17-2022, 08:55 PM
|
#3
|
Senior Member
Join Date: Nov 2015
Posts: 23,569
|
IF it is a 50A site it probably has 30A receptacle also
But if just 50A
Adapter from 50A to 30A then Surge Protector then RV power cord
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor & NUWA 5vr
US NAVY---USS Decatur DDG-31
|
|
|
06-18-2022, 10:12 AM
|
#4
|
Senior Member
Join Date: Jul 2006
Location: Boise Valley (SW Idaho)
Posts: 1,894
|
Old Biscuit is spot on. I do not recall ever encountering an RV pedestal that had a 50 amp receptacle and breaker that did not also have a 30 amp receptacle and breaker.
I would be very careful with any adapters that would allow you to plug a 30 amp cord into a 50 amp outlet. The primary function of the breaker in the pedestal is to protect your cable from the pedestal to your coach and a 50 amp breaker will not adequately protect your 30 amp cable and service entrance.
__________________
Jim & Angie, Boise, ID
2021 Entegra Esteem 27U
2017 GMC Acadia Denali
|
|
|
06-18-2022, 10:38 AM
|
#5
|
Senior Member
Join Date: Nov 2006
Location: Western NY
Posts: 5,512
|
Ive seen this argument often re boats & MHs. The only situation where the cord is not protected and in danger is if the cord shorts between the adapter and the MH main and produces a current greater than 30A AND less than 50A... pretty hard to imagine how that would happen. GT 50A and the pedestal trips and LT 30A and there is no issue.
How would you produce a 40A short in the cord?
__________________
Don & Marge
'13 Newmar Ventana 3433 - '14 CR-V TOAD
'03 Winnebago Adventurer 31Y - SOLD
|
|
|
06-18-2022, 11:15 AM
|
#6
|
Senior Member
Join Date: Dec 2021
Location: Benicia, CA
Posts: 1,054
|
Quote:
Originally Posted by natureman
.....Can I plug the dog bone into my surge protector and the my surge protector into my camper?.......
|
Yes, you can plug in the 50 amp to 30 amp adapter (50 Amp Male to 30 Amp Female Dogbone Adapter RV Electrical Converter Cord Cable https://www.amazon.com/Female-Dogbon...NsaWNrPXRydWU=) to your 30 amp surge protector then connect the surge protector to your 30 amp camper power cord. Just make sure your adapter has the same voltage as the shore power connection.
Do it all the time on my boat, which has 30 amp 125 volt power supply connected to 50 amp 125/250 volt shore power.
__________________
2020 Montana 3780RL fifth wheel (41 ft) / 2016 F-350 6.7L diesel crew cab long bed 4x2 DRW
2022 Thor Palazzo 33.6 diesel pusher / 2021 Chevy Equinox LT AWD toad
|
|
|
06-18-2022, 11:41 AM
|
#7
|
Senior Member
Join Date: Jul 2014
Posts: 32,187
|
Quote:
Originally Posted by K7JV
Old Biscuit is spot on. I do not recall ever encountering an RV pedestal that had a 50 amp receptacle and breaker that did not also have a 30 amp receptacle and breaker.
I would be very careful with any adapters that would allow you to plug a 30 amp cord into a 50 amp outlet. The primary function of the breaker in the pedestal is to protect your cable from the pedestal to your coach and a 50 amp breaker will not adequately protect your 30 amp cable and service entrance.
|
My home outlets are on 15 amp breakers. My lamps are wired with 16 or 18 gauge wire, well under a 15 amp rating, do I not plug them in ?
|
|
|
06-18-2022, 11:49 AM
|
#8
|
Senior Member
Join Date: Nov 2015
Posts: 23,569
|
Quote:
Originally Posted by K7JV
Old Biscuit is spot on. I do not recall ever encountering an RV pedestal that had a 50 amp receptacle and breaker that did not also have a 30 amp receptacle and breaker.
I would be very careful with any adapters that would allow you to plug a 30 amp cord into a 50 amp outlet. The primary function of the breaker in the pedestal is to protect your cable from the pedestal to your coach and a 50 amp breaker will not adequately protect your 30 amp cable and service entrance.
|
50A to 30A Adapter
*Only One Hot leg used
*Pull more then 30A and the RV Main 30A CB trips
*RV Power Cord shorts (gets run over by lawnmower) then the Power Pedestal 50A CB trips
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor & NUWA 5vr
US NAVY---USS Decatur DDG-31
|
|
|
06-18-2022, 12:56 PM
|
#9
|
Senior Member
Join Date: Jul 2006
Location: Boise Valley (SW Idaho)
Posts: 1,894
|
Our current coach has a "Main" breaker in the A/C panel, but not all have an actual main. It is easy to run one or two air conditioners, have the water heater come on, have a good load on the converter (charger) and make a pot of coffee or try to heat a bowl of soup in the microwave and exceed 30 amps of load, though not likely for very many minutes at a time. I will admit that it is not likely that damage will be done, even if the load on the cable and load center of the RV does exceed 30 amps, maybe even by a fair amount for short durations. (Check out the current/time curves on your circuit breaker's). It is just a good idea to design and plan based on good practices. I would personally be totally OK with it, but I would be conscious of what I was doing. As my kids would say, "Just say'n".
__________________
Jim & Angie, Boise, ID
2021 Entegra Esteem 27U
2017 GMC Acadia Denali
|
|
|
06-18-2022, 01:07 PM
|
#10
|
Senior Member
Join Date: Jul 2008
Location: Pennsylvania
Posts: 2,243
|
Quote:
Originally Posted by Old-Biscuit
IF it is a 50A site it probably has 30A receptacle also
But if just 50A
Adapter from 50A to 30A then Surge Protector then RV power cord
|
As usual Old Biscuit has the correct answer
__________________
2020 Winnebago Horizon 42Q
2022 Jeep Wrangler Sahara Unlimited
99 Storm 30H, 04 Southwind 32 VS, 07 Ellipse 40FD
|
|
|
06-18-2022, 01:14 PM
|
#11
|
Senior Member
Join Date: May 2018
Posts: 2,073
|
The 50 to 30 amp adapter is just as safe as many home HVAC circuits that are wired with 30 amp wire and protected with a 50 amp breaker, the HVAC disconnect will have fuses to protect the wire from overload and the 50 amp breaker in the panel will protect it from short circuit, all code compliant and safe. In 30 years as an electrician I have never seen this cause a problem (except with home inspectors who call it out because they don't understand it).
As far as an RV without a main, I have not seen that but it would probably be a small one with not enough loads in it to exceed 30 amps. Sure it could be overloaded if you brought in more loads and tried hard enough but you can only go so far in protecting the public against their own stupidity. If there were documented fires and injuries or deaths then the codes would change but that hasn't been the case.
__________________
Brian, 2011 Winnebago Via Class A on Sprinter Chassis
Tucson, AZ
|
|
|
06-18-2022, 01:19 PM
|
#12
|
Senior Member/RVM #90
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 52,083
|
Try not to use the dog bone adapter unless you have to! I had one catch fire recently!
https://www.irv2.com/forums/f54/my-d...ut-567428.html
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
|
|
|
06-18-2022, 02:25 PM
|
#13
|
Senior Member
Join Date: Feb 2012
Posts: 343
|
Let's get this understood. Fisr, you have a 50 amp pedestal. You have a dog bone with a 50 amp male plug on one end and a 30amp female socket on the other. If that's the case plug the 50 amp into the pedestal. Now when you say surge protector, I hope you mean EMS. Plug the EMS info the dogbone. Then plug in your RV cord into the EMS. Now turn on the pedestal circuit breaker. The EMS will protect the RV cord. There should be a 30 amp breaker in the RV power panel. So you have redundancy. If you only have a surge suppressor the the only protection is the RV circuit breaker.
__________________
Annette and Cliff
2019 Jayco Northpoint 315RLTS
Prescott Valley, AZ
|
|
|
06-18-2022, 02:35 PM
|
#14
|
Senior Member
Join Date: Jul 2014
Posts: 32,187
|
Quote:
Originally Posted by K7JV
Our current coach has a "Main" breaker in the A/C panel, but not all have an actual main. It is easy to run one or two air conditioners, have the water heater come on, have a good load on the converter (charger) and make a pot of coffee or try to heat a bowl of soup in the microwave and exceed 30 amps of load, though not likely for very many minutes at a time. I will admit that it is not likely that damage will be done, even if the load on the cable and load center of the RV does exceed 30 amps, maybe even by a fair amount for short durations. (Check out the current/time curves on your circuit breaker's). It is just a good idea to design and plan based on good practices. I would personally be totally OK with it, but I would be conscious of what I was doing. As my kids would say, "Just say'n".
|
Wow, quite the claim, an RV without a main breaker.
Unless it's homemade, RVIA wouldn't allow it.
|
|
|
 |