Air Conditioner Cuts Out After 2 Minutes

I have a Dometic/Duo Therm air conditioner, model 630035.321. I think it is referred to as a Penguin. The unit starts fine and cools, and using the heat pump heats fine, but only for about 4 minutes. It then shuts down, and just hums. When this happens, I shut the breaker off as it doesn't trip by itself. The same thing happens if I just run the fan on the unit.

I have replace both capacitors, and it has made no difference at all. Everything is clean and all cooling fins are clear as I wash them out twice a year.

While testing the unit, I have observed the motor getting extremely hot. I am guessing over 200 degrees as I can only touch it for a second. The motor spins very freely by hand, and makes no noise at all when it spins. I think all the bearings are fine, but I believe it is getting way too hot and there may be some type of thermal protection that shuts it off when it gets too hot.

Any thoughts on where to check next, or just try a new motor?
__________________
2002 Diplomat
2017 F-150 Toad
Krash is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-05-2020, 11:05 PM   #2
Senior Member
 
Join Date: Nov 2015
Posts: 14,541
Fan Motor 'thermal cutout' is shutting it down
Fan air wheel turns freely....motor starts ok then overheats

Bad Motor...
*check AC Voltage
Low AC Voltage can also cause motor high temps
Lower Voltage/higher amps==HEAT

*Check Fan Motor Continuity
The motor leads are white (common), black (high speed), red (low speed) and yellow (medium speed). Some units are 2-speed.
If you are checking a 2-speed system, disregard the yellow wire.

To check the motor, turn the unit circuit breaker to OFF.
With an AC volt meter, verify that the circuit has no AC volts.

Set your VOM to the ohms scale. You will perform a continuity test. *Check for continuity between the white wire and each of the other wires.
Lack of continuity between the white wire and any of the
other wires indicates an open circuit and requires that the
motor be changed.

*Next, check for continuity between each wire and the green/yellow wire. (Casing Ground Wire)
If you get continuity, you have a grounded motor and it must be replaced.
__________________
Is it time for YOUR Medication or Mine?
Dodge 3500 w/Tractor Motor & NUWA 5vr
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 12-06-2020, 06:01 AM   #3
Senior Member
 
cruizerEd's Avatar
 
Winnebago Owners Club
Join Date: Apr 2014
Location: Florida Keys
Posts: 464
Nice rundown. That should sort it out.
__________________
2013 Winnebago Journey 36M DP.
1987 FJ60 Flat Towed, Blue Ox Tow Bar (not recommend), SMI Air Force One, 2000 Watts Solar, 600AH LifeBlue LiFePO4 batteries (excellent).
cruizerEd is offline   Reply With Quote
Old 12-06-2020, 07:33 PM   #4
Senior Member
 
Join Date: Sep 2019
Location: NW Arkansas
Posts: 129
Quote:
Originally Posted by Old-Biscuit View Post

Set your VOM to the ohms scale. You will perform a continuity test. *Check for continuity between the white wire and each of the other wires.
Lack of continuity between the white wire and any of the
other wires indicates an open circuit and requires that the
motor be changed.
Even if you have continuity between all the wire you still could have a shorted winding. Shorted meaning a short between the run and start winding or short in either winding in it's self. Both conditions will cause the motor to overheat and shut down. I would guess that what you have. Usually if you have a open winding (no continuity) the motor will not start but hum.
Jayco19 is offline   Reply With Quote
Old 12-07-2020, 02:28 AM   #5
Senior Member
 
Krash's Avatar
 
Join Date: Nov 2014
Posts: 125
Thanks for the replies. My meter leads broke, so I am off to buy another one today.

One additional clue. My unit has two fan speeds. I have never tried to run it on anything but AUTO that I can remember. Just for a test, I switched the fan to LOW and it immediately tripped the breaker. I did this several times and the breaker always tripped. On HI it runs for about two minutes and then stops without tripping the breaker. (I always shut the breaker off myself).

Does that add any clues as to the problem?
__________________
2002 Diplomat
2017 F-150 Toad
Krash is offline   Reply With Quote
Reply

Tags
air, air conditioner



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Class A dash air cuts out from vacuum loss Dntsdad Class A Motorhome Discussions 4 06-13-2016 12:01 AM
Generac cuts off after 15 minutes Splendorian MH-General Discussions & Problems 10 01-01-2012 07:03 PM
dash air cuts out trainwreck Class A Motorhome Discussions 7 10-21-2011 06:58 PM
Fan on AC cuts off after running 10 min jbushon2004 Monaco Owner's Forum 4 06-13-2011 08:43 AM
QD generator stopping after 2 minutes use Stretch Alpine Coach Owner's Forum 12 02-04-2006 07:55 PM


All times are GMT -6. The time now is 06:37 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.