Good Morning - first cold morning in a while and I am having some issues with my AquaHot heating system.
When I went to bed last night, I was using the AquaHot to heat my Tiffin. I was only using the electrical element. It was working well when we went to sleep. Upon waking, my RV was a little cold (around 60 degrees - thermostat set to 70) and I noticed the fans (that pump the heat into the RV) for the aquahot were no longer running. I turned on the Diesel Source for the Aquahot and the fans and heat started back up, but only ran about 5 minutes before the diesel shut itself off and the fans stopped again.
It appears that the diesel won't run for more than a few minutes before clicking off.
So, unsure why the heat stopped when using the electric (checked the fuses - no 120V switch tripped) and not sure why the diesel is not working. I am still getting plenty of hot water.
Any advice or insight?
__________________
Nick & Peggy
2008 Tiffin Allegro Bus 42QRP "The Old Lady"
Toad - 2019 Jeep Cherokee Trailhawk
|
|
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
12-02-2020, 06:44 AM
|
#2
|
Senior Member
Newmar Owners Club Carolina Campers Spartan Chassis
Join Date: Apr 2019
Location: China Grove, NC
Posts: 403
|
This happened to me and I just kept turning it back on until it stay on. Had it serviced later with new nozzle\cleaning\etc and hasn't happened since.
I guess mind just clogged up a bit and had to burn it off to keep it going.....
__________________
Randy Goodman - 2006 Newmar Mtn Aire 4032 DP, Spartan, Blue OX Avail, 2018 Jeep JLU Sport 35/12.5s. 2020 Jeep JLU Sahara stock.1st RV 3/19. Looking for a much nicer\NEW ride!!
|
|
|
12-02-2020, 10:06 AM
|
#3
|
Member
Join Date: Mar 2019
Posts: 74
|
The electric element does not provide enough BTUs to heat your coach - that is what your diesel burner is for.
You probably need to do a general service on the diesel side.
|
|
|
12-02-2020, 10:56 AM
|
#4
|
Senior Member
Monaco Owners Club
Join Date: Mar 2018
Location: Blairsville, GA & WPB, FL
Posts: 3,749
|
The fans should not stop running if everything is OK. On the control board, what lights are on? Sounds like a fault is shutting it down... low voltage, liquid level low, or high temperature sensor defective.
__________________
This post is my opinion, worth what you paid for it.
Our ”New” ride...08 HR Navigator 45’. A nice upgrade after 14 years with a 04 Dynasty 42’.
|
|
|
12-02-2020, 11:00 AM
|
#5
|
Senior Member
Join Date: Dec 2019
Posts: 275
|
Quote:
Originally Posted by bentjm
The electric element does not provide enough BTUs to heat your coach - that is what your diesel burner is for.
You probably need to do a general service on the diesel side.
|
^ This ^
|
|
|
12-02-2020, 11:26 AM
|
#6
|
Senior Member
Join Date: Jun 2012
Location: NorCal
Posts: 2,139
|
Have you tried moving temp setting up, may be stat has a problem.
__________________
Outbound
2002 Monaco Executive 500 ISM
2004 GMC 2500HD 4X4
|
|
|
12-02-2020, 11:28 AM
|
#7
|
Moderator Emeritus
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 23,567
|
The electric heat may indeed be insufficient for really cold weather, but that shouldn't cause a fault and stop the fans. Something is wrong with both electric and diesel modes, maybe the same thing or maybe two different things. I'd start with Ivylog's suggestions to figure it out.
There are service manuals with troubleshoot info on the Aquahot website.
Aqua-Hot Manuals
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is in the Ocala Nat'l Forest near Ocala, FL
Summers in Black Mountain, NC
|
|
|
12-02-2020, 11:38 AM
|
#8
|
Senior Member
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 6,936
|
Did the burner start back up?
The burner shutting down after only a few min is normal. The electric element almost had the boiler fluid up to full temp. The heat exchanger fans shutting down while the burner is running, and your inside temp about 10deg below thermostat set temp, that shouldn't have happened.
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
|
|
|
12-02-2020, 01:09 PM
|
#9
|
Senior Member
Entegra Owners Club
Join Date: Jun 2004
Location: Cambridge, Ontario
Posts: 4,322
|
There is nothing wrong with your electric heating element on your Aquahot. It does not have very many btu’s so when cold outside it will not be able to keep up with the heating demand. If the Aquahot fluid is not hot enough it will not circulate thus the pumps will not run and the heat exchanger fans will not run.
Think of it this way, when your Aquahot is first turned on it does not start circulating fluid nor do the heat exchanger fans turn on and blow cold air. When the fluid reaches temperature everything turns on and circulates.
With just the electric element on when it is reheating fluid the circulation pumps and heat exchanger fans turn off until the fluid is heated back up and then will turn back on for a few minutes until the fluid cools off.
__________________
Don & Gerri
2014 Entegra Anthem 44B
2014 Honda CRV Touring
1300W Solar, 1200AH LiFePO4 FMCA F443497
|
|
|
12-02-2020, 08:39 PM
|
#10
|
Senior Member
Tiffin Owners Club Spartan Chassis
Join Date: Mar 2019
Location: Orlando FL
Posts: 253
|
Quote:
Originally Posted by 96 Wideglide
Did the burner start back up?
The burner shutting down after only a few min is normal. The electric element almost had the boiler fluid up to full temp. The heat exchanger fans shutting down while the burner is running, and your inside temp about 10deg below thermostat set temp, that shouldn't have happened.
|
No. The switch where I turn on the Diesel is illuminated. Even though the switch was on, the light turned off. I have not seen the system do that before.
The system was also producing a lot more smoke running on diesel than usual. It looked I was spraying the campground for mosquitos.
__________________
Nick & Peggy
2008 Tiffin Allegro Bus 42QRP "The Old Lady"
Toad - 2019 Jeep Cherokee Trailhawk
|
|
|
12-02-2020, 08:49 PM
|
#11
|
Community Administrator
Tiffin Owners Club Pond Piggies Club LA Gulf Coast Campers Outdoors RV Owners Club Entegra Owners Club
Join Date: Mar 2002
Posts: 33,416
|
Quote:
Originally Posted by bentjm
The electric element does not provide enough BTUs to heat your coach - that is what your diesel burner is for.
You probably need to do a general service on the diesel side.
|
 The electric element is about the equivalent of a blow dryer or space heater on high. You won't be able to heat your whole coach with either.
When was the last time your unit was serviced? That'd be where I'd start. There's a whole bunch of other things that could be checked (that's in another AquaHot issues thread in the Systems & Appliances Forum) for the burner shutting down, but first things first with maintenance.
Lori-
__________________
Lori & Dave - FMCA #F419886 | RV/MH Hall of Fame Lifetime Member
2018 Phaeton XSH 40 IH & 2014 CRV EX-L AWD, My iRV2 Photo Albums
2006 Bounder 36Z, 2004 Cougar 285EFS 5-r, 2000 Aerolite 25FBR TT
There is great need for a sarcasm font.
|
|
|
12-02-2020, 08:51 PM
|
#12
|
Community Administrator
Newmar Owners Club
Join Date: Apr 2014
Location: Southern Indiana
Posts: 14,839
|
Diesel light going out is an indication of a fault on the Webasto Burner Control Unit.
The fault could be from multiple locations.
__________________
Steve
2002 Newmar Mountain Aire 4095
Wash your Hands, Wear a Mask, Social Distance
|
|
|
12-02-2020, 08:51 PM
|
#13
|
Senior Member
Tiffin Owners Club Spartan Chassis
Join Date: Mar 2019
Location: Orlando FL
Posts: 253
|
Quote:
Originally Posted by 757driver
There is nothing wrong with your electric heating element on your Aquahot. It does not have very many btu’s so when cold outside it will not be able to keep up with the heating demand. If the Aquahot fluid is not hot enough it will not circulate thus the pumps will not run and the heat exchanger fans will not run.
Think of it this way, when your Aquahot is first turned on it does not start circulating fluid nor do the heat exchanger fans turn on and blow cold air. When the fluid reaches temperature everything turns on and circulates.
With just the electric element on when it is reheating fluid the circulation pumps and heat exchanger fans turn off until the fluid is heated back up and then will turn back on for a few minutes until the fluid cools off.
|
Makes sense...Thanks for the explanation!
__________________
Nick & Peggy
2008 Tiffin Allegro Bus 42QRP "The Old Lady"
Toad - 2019 Jeep Cherokee Trailhawk
|
|
|
12-03-2020, 11:45 AM
|
#14
|
Member
Join Date: Mar 2019
Posts: 74
|
Quote:
Originally Posted by pete5016
No. The switch where I turn on the Diesel is illuminated. Even though the switch was on, the light turned off. I have not seen the system do that before.
The system was also producing a lot more smoke running on diesel than usual. It looked I was spraying the campground for mosquitos.
|
The smoke is a big indicator that the diesel side needs some attention. Most likely, your nozzle needs to be replaced. It is a pretty simple job to do yourself.
|
|
|
 |
|