Aquahot 400D Issue
Motorhome: 2019 Fleetwood Discovery 38K
System: Aquahot 400D
House batteries: 2 x SOK 206AH (parallel)
I'm having an odd Aquahot issue... We're currently dry camping and using the Aquahot on diesel. Annual maintenance performed in November and have tested the system on diesel several times since. For the most part, everything works as advertised. However, last night (temps in the low 40's), the Aquahot was not igniting. Auxiliary batteries were at about 70% charged (LiFePo4). Tried cycling Aquahot on/off several times. I could hear it trying to start, but it never fully ignites. We're not really close to anyone else, so I fired up the generator at about 0630 this morning (since the wife needs something that resembles hot water for a shower), and bam! The diesel burner ignites and starts working. I verified that in the drawings that the Aquahot uses the auxiliary batteries for power, but no idea why it wouldn't fire last night/this morning... Any suggestions? Thanks!
|
|
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
03-22-2023, 11:01 AM
|
#2
|
Senior Member
Join Date: Mar 2019
Posts: 1,411
|
What does 70% charged mean when expressed as voltage?
|
|
|
03-22-2023, 11:03 AM
|
#3
|
Junior Member
Join Date: May 2020
Posts: 29
|
Quote:
Originally Posted by bentjm
What does 70% charged mean when expressed as voltage?
|
IIRC, it was around 13.1 volts at the time. However, that's not a good indicator as that will fluctuate with varying loads.
|
|
|
03-22-2023, 11:24 AM
|
#4
|
Senior Member
Join Date: Nov 2014
Location: Somewhere
Posts: 827
|
We have the same Aqua-Hot 400D in our 2019 Discovery, but have not had those issues when on battery (but we are mostly on shore power, less often on battery).
Following to see where this ends up.
__________________
2019 Fleetwood Discovery LXE 40D
2017 Ford F-150 LTE FX4 SuperCrew Towed
Full-Timers since 2018
|
|
|
03-22-2023, 03:37 PM
|
#5
|
Senior Member
Join Date: Apr 2018
Posts: 3,226
|
Check the voltage entering the aqua hot control board while on batteries/ with the inverter on if it normally is. Then check it when on shore power. If it’s low on batteries you’ll have to find the voltage drop. Fuse is the best place to start. I get low voltage to the fridge once a year or so, cleaning the fuse contacts in the rear run box always fixes it.
__________________
2004 Dynasty 4
|
|
|
03-22-2023, 06:34 PM
|
#6
|
Junior Member
Join Date: May 2020
Posts: 29
|
Quote:
Originally Posted by shootist
Check the voltage entering the aqua hot control board while on batteries/ with the inverter on if it normally is. Then check it when on shore power. If it’s low on batteries you’ll have to find the voltage drop. Fuse is the best place to start. I get low voltage to the fridge once a year or so, cleaning the fuse contacts in the rear run box always fixes it.
|
Thank you for the suggestion. I'm getting House battery +/- .05 volts on the primary + input. However, I also have (apparently) a + input from my chassis batteries as the "optional" input +. This was reading +/- .05 volts compared to the chassis battery voltage... I reviewed the readings from my SmartShunt last night and indeed, the chassis batteries dropped to about 12.23 volts (while the house batteries dropped to 13.15). I'm assuming it opted for the "optional" input voltage instead of the primary input voltage, which also doesn't make sense to me. I'm working on resolving the chassis battery SOC issue... I was using a Precision Circuits Li BIM-225, but I'm having issues with it staying latched 100% of the time. So I've disconnected that and I'm waiting for a Victron 12/12-18 to come in as my charging solution for my chassis batteries while on shore power. If I need to charge my house batteries while off-grid, I'll just use the generator.
|
|
|
03-24-2023, 09:42 AM
|
#7
|
Senior Member
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 9,462
|
AH 'should' run with as little as 11v.
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
|
|
|
03-31-2023, 09:29 AM
|
#8
|
Junior Member
Join Date: May 2020
Posts: 29
|
I did some further troubleshooting... For troubleshooting the diesel burner, the service manual states:
NOTE: Before troubleshooting the Diesel Burner Control-ler, verify that the Aqua-Hot’s Electronic Controller has voltage at both the C1(orange) & C7(white) wires on the JP4 Plug. Both the C1 & C7 wires will only have power when both the Diesel Burner Status Light and the Heating Status Light are illuminated.
Here's the issue: Initially, I do get 12+ volts at C1 and C7. The circulation pumps engage for about 18 seconds, then I can hear the diesel burner ignite for another 18 seconds. However, at that point, the voltage on C1 and C7 drop to around 7.9-8.4 vdc.
Further in the manual, it states:
If the C7 (White - #23) Wire does not have 12VDC, and both the Diesel Burner Status Light and the Heating Sta-tus lights are illuminated, the electronic controller will need to be replaced.
If the C1 (Orange - #22) wire does not have 12VDC Re-fer to the Webasto Diesel Burner Controller Trouble-shooting, in section 10.
It sounds like either 1) this is normal operation and something is telling the electronic controller to reduce the voltage to the diesel burner, or 2) the electronic controller is bad.
I did apply 12+ vdc directly to those pins and everything stays running as normal.
I'm awaiting a call back from Airxcel/Aqua Hot to get their opinion before I spend $561 on a part that may not resolve the issues... Wish me luck!
|
|
|
03-31-2023, 06:23 PM
|
#9
|
Senior Member
Join Date: Apr 2018
Posts: 3,226
|
So the voltage drop happens when the circulation pumps are on? That is still sounding like a power supply problem.
__________________
2004 Dynasty 4
|
|
|
04-02-2023, 11:55 AM
|
#10
|
Junior Member
Join Date: May 2020
Posts: 29
|
Quote:
Originally Posted by shootist
So the voltage drop happens when the circulation pumps are on? That is still sounding like a power supply problem.
|
After talking with Aquahot support, the controller was just doing its job, as something else was telling it to cut the voltage to the burner. He recommended that I take a look at the high limit thermostats. I found that when I wiggled any of the four terminals (two on each of the two thermostats), the resistance across the four would jump around. After connecting/disconnecting all four terminals several times, I ended up with stable continuity across both thermostats. Fired everything up, works like a charm. HOWEVER, after it cycled, it failed to turn on the next time. So, I'm having a second issue and that was with low voltage on the chassis batteries (again). I've since moved a couple of accessories that I had mistakenly installed on the chassis battery side over to the house battery side and my chassis batteries are staying rock solid 100% charged.
I'm still curious as to where the Firefly reads its voltage readings? I would assume from the inputs at the G6A panel, but I've verified the voltage on the backside of my G6A panel and I'm getting within 0.1 vdc of what my smart shunt is reading for chassis and house batteries (at the actual batteries). However, the Firefly sometimes reports as much as 0.4-0.5 volts LOWER than what my shunt is reading.
|
|
|
04-02-2023, 12:15 PM
|
#11
|
Senior Member
Join Date: Apr 2018
Posts: 3,226
|
Quote:
Originally Posted by JeromeS13
After talking with Aquahot support, the controller was just doing its job, as something else was telling it to cut the voltage to the burner. He recommended that I take a look at the high limit thermostats. I found that when I wiggled any of the four terminals (two on each of the two thermostats), the resistance across the four would jump around. After connecting/disconnecting all four terminals several times, I ended up with stable continuity across both thermostats. Fired everything up, works like a charm. HOWEVER, after it cycled, it failed to turn on the next time. So, I'm having a second issue and that was with low voltage on the chassis batteries (again). I've since moved a couple of accessories that I had mistakenly installed on the chassis battery side over to the house battery side and my chassis batteries are staying rock solid 100% charged.
I'm still curious as to where the Firefly reads its voltage readings? I would assume from the inputs at the G6A panel, but I've verified the voltage on the backside of my G6A panel and I'm getting within 0.1 vdc of what my smart shunt is reading for chassis and house batteries (at the actual batteries). However, the Firefly sometimes reports as much as 0.4-0.5 volts LOWER than what my shunt is reading.
|
If your firefly is reading voltage from an area further from the batteries it will show lower voltage when a load is present. My water pump will draw my voltage down to 12.6 or 12.7 as shown on the garnet see level as the two are in close proximity and probably the see level was wired in on the same circuit. As soon as the pump shuts off I see whatever my charging voltage is again.
__________________
2004 Dynasty 4
|
|
|
04-02-2023, 12:31 PM
|
#12
|
Senior Member
Join Date: Jul 2008
Location: Pennsylvania
Posts: 2,441
|
I know that my Aquahot 450 sucks the juice. When it’s on it’s drawing heavy juice.
I don’t think my 6 AGMs can handle a period of time by them self, I have AutoGen and my generator kicks in when the Aquahot is going full with all three zones running. I think when it kicks it there is a big amp draw. My AutoGen is set at 12.1 volts.
__________________
2020 Winnebago Horizon 42Q
2022 Jeep Wrangler Sahara Unlimited
99 Storm 30H, 04 Southwind 32 VS, 07 Ellipse 40FD
|
|
|
04-02-2023, 01:17 PM
|
#13
|
Senior Member
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 9,462
|
Highest draw I've seen on my Magnum remote panel with burner and all heat exchangers / pumps running (other than engine pre-heat), is 17A-DC.
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
|
|
|
 |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
Similar Threads
|
Thread |
Thread Starter |
Forum |
Replies |
Last Post |
400D AquaHot challenge
|
dsamford |
RV Systems & Appliances |
0 |
09-07-2019 11:31 AM |
Aquahot 400D Question
|
kevinantholt |
Entegra Owner's Forum |
39 |
11-30-2017 10:58 AM |
Aqua Hot 400D
|
riders |
Thor Industries Owner's Forum |
6 |
05-16-2017 01:55 PM |
Aqua Hot 400D
|
captain rich |
iRV2.com General Discussion |
5 |
01-30-2017 01:26 PM |
Aqua Hot 400D
|
GAS 13 |
MH-General Discussions & Problems |
17 |
04-12-2016 07:17 AM |
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|