I’m not sure that I am following what you are describing but what I think you are saying is that 1. You discovered that the DC fuse between the batteries and the inverter/Charger was open. OK, well that’s not good and needs to be corrected. 2. Without the generator running you measured 13V on the battery side of the blown fuse and 0V on the I/C side. That’s exactly what you should see. Without AC from generator or shore power the Charger will not work, hence 0V. 3. You fired up the generator and the Charger came on and you still measured 13V on the battery side of the blown fuse and 15V (from the charger) on the charger side. However, the Charger can’t charge the batteries because there is no current, (because the fuse is open). 4. When you turn the generator on the 120VAC stuff comes on but when the generator is off the 120VAC goes away. Yes, the generator AC is being passed thru the inverter and powers the various stuff on the inverted output but when you turn the generator off then the 120VAC goes away because with no connection to the batteries (the fuse is open) the inverter cannot make 120VAC.
My recommendation would be first, replace the fuse with the correct value replacement. Second, then connect to shore power or run the generator so the inverter/Charger can charge the batteries.