Cummins Quiet Diesel 7500

Greetings all

Cummins would have you start the genny under minimal load and stop the genny under minimal load after a 5 minute cool down period.

I have a 2000 Monaco Dynasty with upgraded solar (2000 watts), batteries (680ah lithium) and inverter charger (3000 watts). The charger is 120 amps at 12 Volts (so approx 12 amps @ 115V). (The original was 75 amps at 12 volts).

This seems to mean I can neither start or stop the generator under minimal load (unless the house batteries are fully charged).

First, am I rightly concerned?
Second, what's a body to do?

Thank you for your support.
Denver is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-28-2021, 10:57 PM   #2
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 30,655
Your terminology is not entirely correct. Actually what my owners manual says is do not start or stop while under a heavy load, allow at least 3 minutes under minimal load to cool down.

I would not be concerned about the battery charger load, at its highest the 120A load will be 1/10th of that in AC amps.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG 11B5MX,Infantry retired;Good Sam Life member,FMCA." My fellow Americans, ask not what your country can do for you, ask what you can do for your country. John F. Kennedy
Ray,IN is offline   Reply With Quote
Old 06-01-2021, 07:53 AM   #3
Member
 
Monaco Owners Club
Join Date: Apr 2017
Location: Domiciled in Florida, Full Timer west of the Mississippi
Posts: 44
Send a message via AIM to Denver Send a message via MSN to Denver Send a message via Yahoo to Denver
Quote:
Originally Posted by Ray,IN View Post
Your terminology is not entirely correct. Actually what my owners manual says is do not start or stop while under a heavy load, allow at least 3 minutes under minimal load to cool down.

I would not be concerned about the battery charger load, at its highest the 120A load will be 1/10th of that in AC amps.
so you're suggesting it is OK to start and stop under a 12 Amp load? The load is equivalent to a microwave, toaster oven, resistance heater or washing machine/dryer. Seems to me these are the "appliances" referred to by Cummins.

Thanks, I suppose, but your response doesn't follow from the Cummins directions..
Denver is offline   Reply With Quote
Old 06-01-2021, 08:29 AM   #4
Senior Member
 
caninecop's Avatar
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Dec 2009
Posts: 761
Quote:
Originally Posted by Denver View Post
so you're suggesting it is OK to start and stop under a 12 Amp load? The load is equivalent to a microwave, toaster oven, resistance heater or washing machine/dryer. Seems to me these are the "appliances" referred to by Cummins.

Thanks, I suppose, but your response doesn't follow from the Cummins directions..
Ray gave you the accurate information on starting and shutting down the gen in Chapter 4 of my manual covers this.
__________________
2014 Tiffin Allegro Bus
caninecop is offline   Reply With Quote
Old 06-01-2021, 08:57 AM   #5
Senior Member
 
Tha_Rooster's Avatar
 
Join Date: Aug 2008
Location: Georgia
Posts: 8,638
Quote:
Originally Posted by Denver View Post
Greetings all



Cummins would have you start the genny under minimal load and stop the genny under minimal load after a 5 minute cool down period.



I have a 2000 Monaco Dynasty with upgraded solar (2000 watts), batteries (680ah lithium) and inverter charger (3000 watts). The charger is 120 amps at 12 Volts (so approx 12 amps @ 115V). (The original was 75 amps at 12 volts).



This seems to mean I can neither start or stop the generator under minimal load (unless the house batteries are fully charged).



First, am I rightly concerned?

Second, what's a body to do?



Thank you for your support.


Your putting to much into it. I just turn off ac which is better for them anyway.
__________________
2007 Fleetwood Revolution LE 40V
Tha_Rooster is offline   Reply With Quote
Old 06-01-2021, 09:31 AM   #6
Senior Member
 
Join Date: Jul 2014
Posts: 35,349
Your not starting against any load.

Your ATS, ( auto transfer switch ) has about a 30 second delay before it applies a load to the generator.
twinboat is online now   Reply With Quote
Old 06-02-2021, 10:37 PM   #7
Senior Member
 
National RV Owners Club
Freightliner Owners Club
Join Date: Oct 2002
Location: silverdale wa.
Posts: 1,163
On my Generac quietpac 7500d, the same generator as yours, the manual says to start it with no load and let it run for several minutes to warm up before bringing systems online. When you are ready to turn the gennie off, power off all the systems that were running and let it run for several minutes to cool down
__________________
Bigdog
2001 National Tradewinds 7390 LTC
2002 Subaru Legacy outback Limited stick
bigdog is offline   Reply With Quote
Reply

Tags
diesel, cummins, quiet



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan 7500 quiet generator too quiet!! won't start ?? ToddnRhonda Class A Motorhome Discussions 24 03-12-2022 08:51 AM
Cummins-Onan 7500 quiet diesel generator fault code 25 Bad Bolt Class A Motorhome Discussions 31 01-03-2019 06:05 PM
Replacing the circuit breaker on an Onan 7500 Quiet Diesel Denali Monaco Owner's Forum 9 06-17-2010 10:27 AM
Onan Quiet Diesel 7500 Problem Dr4Film RV Systems & Appliances 2 02-01-2010 07:15 PM