Quote:
Originally Posted by Old Scout View Post
Tfryman--who mentioned European????? ….the OP did!!! but the "real" question is: is it 208-230v double-pole or single-pole? I "assume" OP's split AC is double-pole US std but not all RV breaker boxes accommodate phased 240v double-pole breakers....that is, below the main breaker...also, typical 7500 watt genset isn't phased either, believe 10 and 12k are?????? without knowing the "electrical IQ" of the OP, providing advice on this forum is always problematic.....
I am an electrical mechanic for rotary wing aircraft. I know electrical theory and aircraft systems. When it comes to residential, I am not as familiar.
C5c5 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-01-2020, 08:00 PM   #16
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 7,400
C5c5….no offense to you at all.....you are asking the right questions...key here is that residential 240v appliances are two phased hots, a ground, and sometimes a neutral. Many RVs are wired for 50 amp service [two hots, neutral and ground], but most RV wiring doesn't support phased 240v applications.
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
Old Scout is offline   Reply With Quote
Old 06-02-2020, 09:50 AM   #17
Senior Member
 
Join Date: Jun 2017
Posts: 2,807
Quote:
Originally Posted by Old Scout View Post
Tfryman--who mentioned European????? ….the OP did!!! but the "real" question is: is it 208-230v double-pole or single-pole? I "assume" OP's split AC is double-pole US std but not all RV breaker boxes accommodate phased 240v double-pole breakers....that is, below the main breaker...also, typical 7500 watt genset isn't phased either, believe 10 and 12k are?????? without knowing the "electrical IQ" of the OP, providing advice on this forum is always problematic.....
Yes, he did ask about a "European power setup" but his mini-split is not European standard - 60 Hz is NA.
aether_one is offline   Reply With Quote
Old 06-02-2020, 09:55 AM   #18
Senior Member
 
paul65k's Avatar


 
Alpine Owners Club
Join Date: Nov 2015
Location: Lake Havasu City, AZ
Posts: 3,015
Quote:
Originally Posted by jacwjames View Post
One problem you may have is trying to run the mini split on the generator. You would need a generator that actually makes the 230/240 volt power >>> two 120 volt circuits with the correct phasing.

My generator provides two 120 volt circuits on the same phase so I cannot run a 240-volt appliance.
This is a major consideration

Typically true 240V RV generators start at 12KW
__________________
Paul & Jean
2001 Alpine 36FDDS (74291)-3900W Solar, 13,440Wh (525Ah @24V) LiFePO4
2019 Jeep Grand Cherokee Trailhawk (Hemi)
2006 Alpenlite 32RL - Sold
paul65k is offline   Reply With Quote
Old 06-05-2020, 01:55 PM   #19
Senior Member
 
C5c5's Avatar
 
Join Date: Sep 2019
Location: Minne-so-cold
Posts: 708
Thank all for the input!

There are some conflicting opinions here, but it seems the general idea is yes, I can install a 208/230V single phase 60Hz minisplit in my motorhome.

I've spoken to others who have suggested that so long as the minisplit is on its own dedicated properly sized inverter, it should work. This would for shore power use only.

If I wanted to have generator back-up, then I might run into problems from phasing.
C5c5 is offline   Reply With Quote
Old 06-05-2020, 02:06 PM   #20
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 7,400
…"dedicated properly sized inverter???????"..... have no idea what this is about--you are not going to run off bats?
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
Old Scout is offline   Reply With Quote
Old 06-05-2020, 02:26 PM   #21
Senior Member
 
C5c5's Avatar
 
Join Date: Sep 2019
Location: Minne-so-cold
Posts: 708
Quote:
Originally Posted by Old Scout View Post
…"dedicated properly sized inverter???????"..... have no idea what this is about--you are not going to run off bats?
Yes, I will be getting a very large solar system in a few months. I however for the short future will be running everything on shorepower. I am getting on the road full-time sooner than anticipated and can't install everything in time.

As far as the inverter, I'm told that it needs to be able to handle 208/230V.
C5c5 is offline   Reply With Quote
Old 06-05-2020, 02:37 PM   #22
Senior Member
 
KanzKran's Avatar
 
Join Date: Sep 2018
Posts: 1,944
The 208V is referring to a Y-connected 208Y/120V three-phase system, which is common in places like apartment buildings and small commercial spaces. You get 208V phase-to-phase, and 120V phase-to-neutral.

But the 208V is single-phase, just like 240V in your house panel is single-phase. So all that 208/230V means is that it's '208V compatible'. Many induction motors show something similar on the nameplate, like 208-230/115V for a dual-voltage motor. It just means it's rated for full output at 208V, as well as 230V, and 115V when reconnected for low voltage. Many if not most small induction motors are NOT 208V rated, unless it says so on the nameplate. Your unit is.

So in a nutshell, if you can connect to a 240V circuit (see the post above about the quad breaker with handle ties), you can run it on your 120/240V power.

Edit: By the way, induction motors built to the NEMA MG-1 standard are rated 115V, 200V, 230V, 460V, and 575V, and are intended to operate on 120V, 208V, 240V, 480V, and 600V (mostly in Canada), respectively, systems. Many motors still show 208V for a 208V system, though it should be 200V to conform to the 4%+ voltage allowance that's built into these motors, so those are a bit of an oddity.
__________________
Tom & Jeri
2018 Coachmen Galleria 24T Li3
KanzKran is offline   Reply With Quote
Old 06-05-2020, 02:43 PM   #23
Senior Member
 
C5c5's Avatar
 
Join Date: Sep 2019
Location: Minne-so-cold
Posts: 708
Quote:
Originally Posted by KanzKran View Post
The 208V is referring to a Y-connected 208Y/120V three-phase system, which is common in places like apartment buildings and small commercial spaces. You get 208V phase-to-phase, and 120V phase-to-neutral.

But the 208V is single-phase, just like 240V in your house panel is single-phase. So all that 208/230V means is that it's '208V compatible'. Many induction motors show something similar on the nameplate, like 208-230/115V for a dual-voltage motor. It just means it's rated for full output at 208V, as well as 230V, and 115V when reconnected for low voltage. Many if not most small induction motors are NOT 208V rated, unless it says so on the nameplate. Your unit is.

So in a nutshell, if you can connect to a 240V circuit (see the post above about the quad breaker with handle ties), you can run it on your 120/240V power.

Edit: By the way, induction motors built to the NEMA MG-1 standard are rated 115V, 200V, 230V, 460V, and 575V, and are intended to operate on 120V, 208V, 240V, 480V, and 600V (mostly in Canada), respectively, systems. Many motors still show 208V for a 208V system, though it should be 200V to conform to the 4%+ voltage allowance that's built into these motors, so those are a bit of an oddity.
Thank you!
C5c5 is offline   Reply With Quote
Old 06-05-2020, 02:59 PM   #24
Senior Member
 
KanzKran's Avatar
 
Join Date: Sep 2018
Posts: 1,944
Just for completeness, here's a 1 hp motor nameplate showing 115/208-230V, with full load current numbers that correspond to the different line voltages, and the reduced service factor at 208V from 1.15 down to 1.0, since it's basically an undervoltage condition. But it's still designed and rated for continuous full hp output at 208V line voltage as well as 240V. As is yours, even though it'll be working on a 240V system since RVs aren't typically connected to 208V power.

Yours just can't be connected for 120V systems, while this motor can.

And here's a 208-230V (only) motor nameplate, which is more like yours.
Attached Thumbnails
Click image for larger version

Name:	Motor Nameplate.jpg
Views:	32
Size:	141.3 KB
ID:	288384   Click image for larger version

Name:	Motor Nameplate 1.jpg
Views:	42
Size:	22.6 KB
ID:	288386  

__________________
Tom & Jeri
2018 Coachmen Galleria 24T Li3
KanzKran is offline   Reply With Quote
Old 06-05-2020, 04:47 PM   #25
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 7,400
…."big solar panels"...and big battery bank and big inverter with phase output????....and big$$$$$$$ too.....yes, you will certainly going "big"!!!!!!
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
Old Scout is offline   Reply With Quote
Old 06-05-2020, 04:59 PM   #26
Senior Member
 
Xmcdog's Avatar
 
Join Date: Dec 2019
Location: Alberta
Posts: 1,976
As long as you are roughly within range you will be fine. Most local domestic supply is around 242 volts 60 hz.

I have installed hundreds of mini splits with no voltage issues. Max limit I am told is 253 volts.
__________________
Jeff and Annette Smith. Sparky, lemon Beagle.
2022 Chevy Equinox RS.
2007 Dutch Star
Xmcdog is offline   Reply With Quote
Old 06-06-2020, 07:55 AM   #27
Senior Member
 
Xmcdog's Avatar
 
Join Date: Dec 2019
Location: Alberta
Posts: 1,976
Just a little more trivia for you. The compressor motors in a mini split are 3 phase DC motors running on about 360 volts.
This gives them a soft start and the initial amp draw is about 0.92 amps on startup for a 15 k btu unit.
__________________
Jeff and Annette Smith. Sparky, lemon Beagle.
2022 Chevy Equinox RS.
2007 Dutch Star
Xmcdog is offline   Reply With Quote
Old 06-06-2020, 08:06 AM   #28
Senior Member
 
Xmcdog's Avatar
 
Join Date: Dec 2019
Location: Alberta
Posts: 1,976
Quote:
Originally Posted by KanzKran View Post
Just for completeness, here's a 1 hp motor nameplate showing 115/208-230V, with full load current numbers that correspond to the different line voltages, and the reduced service factor at 208V from 1.15 down to 1.0, since it's basically an undervoltage condition. But it's still designed and rated for continuous full hp output at 208V line voltage as well as 240V. As is yours, even though it'll be working on a 240V system since RVs aren't typically connected to 208V power.

Yours just can't be connected for 120V systems, while this motor can.

And here's a 208-230V (only) motor nameplate, which is more like yours.
Sorry to disagree but mini splits are using 3 phase DC motors with inverter control. Different animal.
__________________
Jeff and Annette Smith. Sparky, lemon Beagle.
2022 Chevy Equinox RS.
2007 Dutch Star
Xmcdog is offline   Reply With Quote
Reply

Tags
electric, electrical



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
208 Monoco Diplomat 40 PDQ fuel guage Mit12 Monaco Owner's Forum 2 07-22-2018 10:34 PM
1996 Firan Raven XL 34ft-F53=208"WB flbicyclist MH-General Discussions & Problems 4 05-16-2013 04:13 AM
230v wiring question lonestarace iRV2.com General Discussion 3 06-02-2012 06:16 PM
208 to 220 knebrdr Workhorse and Chevrolet Chassis Motorhome Forum 8 10-16-2007 07:13 PM
208 Flagstaff Popup Newfie Pop Up, Tent Trailer and Teardrop Topics 1 01-22-2005 04:02 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 04:19 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.