Electrical Question - 208/230V

Greetings,

The mini-split that I will be installing in my motorhome has power requirement of 208/230V , 1 phase 60 Hz. I'm told this cannot be installed into a 120/240V system for my RV. Is this true & why? Can the European power set up be used in the American?
__________________

C5c5 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-01-2020, 05:34 PM   #2
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 19,902
I think you were told correctly. A qualified electrician should be along shortly to explain the details and differences between North American and European electrical systems.
__________________

__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG 11B5MX,Infantry retired;Good Sam Life member,FMCA." My fellow Americans, ask not what your country can do for you, ask what you can do for your country. John F. Kennedy
Ray,IN is offline   Reply With Quote
Old 06-01-2020, 05:45 PM   #3
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 5,687
….don't think we have 1 phase 208/230 volt power in the US....that is European specs....might be a transformer solution available...…"back in the day" US military folks used transformers to convert 220v to 110v for US appliances but it seemed to be hard on our appliances with motors [maybe it was 50 or 55 cycles]....I am sure you will get many more posts on 120v vs 240v as it is a "favorite" topic for the forum......
__________________
Old Scout
2003 Alpine 40' MDTS
New Braunfels, Texas
Old Scout is offline   Reply With Quote
Old 06-01-2020, 05:49 PM   #4
Senior Member
 
Join Date: Jun 2017
Location: Bryan Tx
Posts: 539
60 hz is the US frequency. Europe is 50 HZ. Difference between 230 and 240 is negligible. Question is how is your breaker box set up and how is the split system set up. Need to have a knowledgeable person look at both. It could be you are ok but need to be sure as damage and be done. Do you have drawings on how your breaker box is set up. Also be aware that when you shift from shore power to generator grounds and neutral references can change.
__________________
“06” Beaver Patriot Thunder , 525 HP C13 Cat
MH 4000 Allison
42 ft Vicksburg, 4 slides
kenwyatt is online now   Reply With Quote
Old 06-01-2020, 05:59 PM   #5
Senior Member
 
paul65k's Avatar


 
Alpine Owners Club
Join Date: Nov 2015
Location: Lake Havasu City, AZ
Posts: 900
Don't give up on your idea of a 240V mini-split, it can be achieved....find yourself a qualified electrician who can re-wire your box to achieve a 240 (230V) circuit.

Youll need to change out your breaker box but not that big a job if you know what you're doing

PS all north American electrical grids operate on 60Hz.....50Hz is the European standard
__________________
Paul & Jean
2001 Alpine 36FDDS - 1600W Solar, 10,752 Wh (840Ah) LifePO4
2014 Jeep Wrangler Unlimited Rubicon
2006 Alpenlite 32RL - Sold
paul65k is online now   Reply With Quote
Old 06-01-2020, 06:07 PM   #6
Member
 
Join Date: Jan 2020
Posts: 92
There are some good offering in 110/120V mini splits. I think they are limited to 12K BTU but they are high seer.
TMyers17 is offline   Reply With Quote
Old 06-01-2020, 06:09 PM   #7
Senior Member
 
C5c5's Avatar
 
Join Date: Sep 2019
Location: Minne-so-cold
Posts: 599
Quote:
Originally Posted by paul65k View Post
Don't give up on your idea of a 240V mini-split, it can be achieved....find yourself a qualified electrician who can re-wire your box to achieve a 240 (230V) circuit.



Youll need to change out your breaker box but not that big a job if you know what you're doing



PS all north American electrical grids operate on 60Hz.....50Hz is the European standard
I have removed all coach electrical am going to install a new system. I was thinking of using a standard residential box from Home Depot etc.

Advice on how to do it so it can accomodate the 208/230V?
C5c5 is offline   Reply With Quote
Old 06-01-2020, 06:11 PM   #8
Senior Member
 
C5c5's Avatar
 
Join Date: Sep 2019
Location: Minne-so-cold
Posts: 599
Quote:
Originally Posted by TMyers17 View Post
There are some good offering in 110/120V mini splits. I think they are limited to 12K BTU but they are high seer.
The SEER of the Mitsubishi I'd like is 30. I'd like to stick with it if all possible
C5c5 is offline   Reply With Quote
Old 06-01-2020, 06:15 PM   #9
Senior Member
 
powercat_ras's Avatar
 
Winnebago Owners Club
Solo Rvers Club
Join Date: May 2015
Posts: 1,491
In the USA, Canada, and Mexico, your RV power source choices are 15/20 Amp or 30 Amp 3-Pin Plugs which is single phase 120 Volts AC or 50 Amp 4 Pin Plug which is split phase 120 Volts AC with 240 Volts AC possible with a double breaker that feeds both phases to a load.

As was also noted, North America is 60 Hertz and Europe is 50 Hertz in addition to the voltage differences.

You need to change your plan, it won't go well.
__________________
Randy - Manhattan, Kansas
2015 Vista 27N
2016 Honda HR-V
powercat_ras is offline   Reply With Quote
Old 06-01-2020, 06:25 PM   #10
Senior Member


 
Join Date: Jun 2017
Posts: 2,580
Who said anything about a European system? All 240 VAC mini-split A/C systems say 230 volt single phase. Just like 120 VAC used to be 110 VAC, 240 VAC used to be 220 VAC. So 230 VAC just splits the difference. Here's an example from Home Depot:

tfryman is offline   Reply With Quote
Old 06-01-2020, 06:48 PM   #11
Senior Member
 
Join Date: Jul 2014
Posts: 22,373
If you have a 50 amp RV, 240 volts is at the main breaker panel, in the RV.

To tap into it, you remove the main 50 amp double pole breaker and install a double pole, tandem breaker.
They are 2 double pole breakers in one one double space.

The 50 amp set powers the 2 bus bars, and the other set ( what ever the units amp rating ) power the mini split system.

Here is a double, tandem breaker.
Name:   MP240240CT2-Murray_2.jpeg
Views: 15
Size:  13.5 KB
twinboat is online now   Reply With Quote
Old 06-01-2020, 06:58 PM   #12
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 6,736
One problem you may have is trying to run the mini split on the generator. You would need a generator that actually makes the 230/240 volt power >>> two 120 volt circuits with the correct phasing.

My generator provides two 120 volt circuits on the same phase so I cannot run a 240 volt appliance.
__________________
Jim J
2002 Monaco Windsor 38 PKD
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is offline   Reply With Quote
Old 06-01-2020, 07:00 PM   #13
Senior Member
 
C5c5's Avatar
 
Join Date: Sep 2019
Location: Minne-so-cold
Posts: 599
Quote:
Originally Posted by jacwjames View Post
One problem you may have is trying to run the mini split on the generator. You would need a generator that actually makes the 230/240 volt power >>> two 120 volt circuits with the correct phasing.

My generator provides two 120 volt circuits on the same phase so I cannot run a 240 volt appliance.
TY for the heads up!
C5c5 is offline   Reply With Quote
Old 06-01-2020, 07:38 PM   #14
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 5,687
Tfryman--who mentioned European????? ….the OP did!!! but the "real" question is: is it 208-230v double-pole or single-pole? I "assume" OP's split AC is double-pole US std but not all RV breaker boxes accommodate phased 240v double-pole breakers....that is, below the main breaker...also, typical 7500 watt genset isn't phased either, believe 10 and 12k are?????? without knowing the "electrical IQ" of the OP, providing advice on this forum is always problematic.....
__________________

__________________
Old Scout
2003 Alpine 40' MDTS
New Braunfels, Texas
Old Scout is offline   Reply With Quote
Reply

Tags
electric, electrical



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
208 Monoco Diplomat 40 PDQ fuel guage Mit12 Monaco Owner's Forum 2 07-22-2018 10:34 PM
1996 Firan Raven XL 34ft-F53=208"WB flbicyclist MH-General Discussions & Problems 4 05-16-2013 04:13 AM
230v wiring question lonestarace iRV2.com General Discussion 3 06-02-2012 06:16 PM
208 to 220 knebrdr Workhorse and Chevrolet Chassis Motorhome Forum 8 10-16-2007 07:13 PM
208 Flagstaff Popup Newfie Pop Up, Tent Trailer and Teardrop Topics 1 01-22-2005 04:02 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:50 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
×