Electrical Question

We're sitting in a park with 50 amp power hooked up. Power keeps fading just enough to shut off the TV or microwave then comes right back on. This happens repeatedly at different intervals between events. The breakers never pop and the power always returns to normal until next power dip. My inverter and surge protector seems to be functioning normally. Any ideas? Thanks much!
__________________
Snoopkat
2021 Newmr Bay Star Sport 3014
Snoopkat is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-21-2018, 07:51 AM   #2
bnb1313@aol.com
 
BigSkyBob's Avatar


 
Monaco Owners Club
Join Date: Feb 2008
Location: Western Montana on the Divide
Posts: 1,561
I'd try to determine first if it was the park power fluctuating or your coach systems. If it happens on a regular basis I'd put a meter on the power post to see if in fact the incoming power is the problem. Can you quiz others nearby to see if they experience the same thing? If your surge guard is cutting the power off due to a low voltage condition then the issue lies with the incoming power.
__________________
Bob Retired Army Traveling alone now, had to put Charlie the Beagle down :(.
2008 Camelot 40 PDQ 4 slides ISL400 towing a 2020 1500 GMC Sierra Denali 4x4 Crewcab
Western MT in summer, AZ, NV in winter
BigSkyBob is offline   Reply With Quote
Old 09-21-2018, 07:55 AM   #3
Senior Member
 
Join Date: Oct 2014
Location: Port Orchard, WA
Posts: 4,217
Quote:
Originally Posted by Sofakleez View Post
We're sitting in a park with 50 amp power hooked up. Power keeps fading just enough to shut off the TV or microwave then comes right back on. This happens repeatedly at different intervals between events. The breakers never pop and the power always returns to normal until next power dip. My inverter and surge protector seems to be functioning normally. Any ideas? Thanks much!
You need to go to the office and ask them what the heck is up with their electricity!

Doesn't sound like a coach problem to me. Do you have an electrical monitoring system? If so, it should be telling you what is going on.
__________________
Scot & Laura Kellersberger, U.S. Army (ret)
Newmar 4 wheel drive Dutch Star 3891, SOLD
Now RV'ing on the water in a Trawler!
Hit_the_Rhod is offline   Reply With Quote
Old 09-21-2018, 08:12 AM   #4
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
Inverter????? What may be happening is the pedestal power drops below the threshold of your "surge protector," it shuts down and the inverter picks up your TVs and other devices. Then the power comes back and the whole thing starts again.
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 09-21-2018, 08:17 AM   #5
Senior Member
 
docj's Avatar
Official iRV2 Sponsor
 
Join Date: May 2011
Posts: 8,305
Here's a situation in which Progressive power management system's ability to display the "previous fault" (which is shown by "PE" and a number) is essential to being able to diagnose what is going on compared to a SurgeGuard

We had exactly the same thing occur at an RV site we actually own in south TX. At the time I had a SurgeGuard power management device and it kept turning off the power and then turning it back on. Since I couldn't find anything wrong and the voltages seemed normal I attributed it to something wrong with the SurgeGuard.

However, the problem continued after I replaced the SurgeGuard with a Progressive but I was then able to use the Previous Fault feature to figure out what was going on. It turned out that the problem wasn't low voltage at all, it was momentarily high voltage caused by loose neutral connections in the pedestal. On split phase circuits such as used to develop 120V from a 240 V feed, loose connections can increase the resistance in the circuit which raises the voltage on one leg while lowering it on the other. If the resistance increase is intermittent it can lead to the erratic behavior I was experiencing. Having the power company tighten all the connections solved the problem.

IMO, the problem you have is real, but it may be difficult to figure it out unless you have a device that can tell you what is happening.
__________________
Joel (AKA docj)--
RV Technology Specialist
docj is offline   Reply With Quote
Old 09-21-2018, 08:22 AM   #6
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
Loose or floating neutral on a 50 amp connection is a bad, bad thing to have...especially without a good surge protector or PD smart transfer switch!!!!
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 09-22-2018, 08:35 AM   #7
Senior Member
 
Snoopkat's Avatar
 
Join Date: Sep 2011
Posts: 136
Thanks to all who shared your experience/ideas/knowledge on this electrical issue. Very much appreciated! I'll pursue that neutral idea first and hope it takes care of it. Thanks again!
__________________
Snoopkat
2021 Newmr Bay Star Sport 3014
Snoopkat is offline   Reply With Quote
Reply

Tags
electric, electrical



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
No electrical power at one lug (3) Left Front Electrical Center RobRoy Monaco Owner's Forum 18 03-31-2017 11:59 AM
Weird electrical/noise question Carnles Winnebago Industries Owner's Forum 3 10-15-2007 01:55 PM
Electrical Question gator67 Alpine Coach Owner's Forum 4 09-19-2007 01:02 PM
2004 Brave electrical system question skipsor Winnebago Industries Owner's Forum 3 01-28-2007 08:22 AM
Electrical question Matt1616 MH-General Discussions & Problems 7 03-02-2006 05:36 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 07:33 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.