Old 12-02-2015, 01:41 PM   #1
AJB
Junior Member
 
Join Date: Feb 2013
Location: Here & There
Posts: 27
Electrical service 50 amp

I heard something for the first time today that left me scratching my head and wondering if I have been wrong. If you have a 240 volt 50 amp breaker supplying power to your RV how many total amps do I have to use. I always thought it was 50 amps but someone told me today that you have a total of 100 amps (50 amps per leg). You have two hot legs (120 volts 50 amps x two legs). So let's here the correct answer please.
AJB is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-02-2015, 02:28 PM   #2
Senior Member
 
Steve Ownby's Avatar
 
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,587
Quote:
Originally Posted by AJB View Post
I heard something for the first time today that left me scratching my head and wondering if I have been wrong. If you have a 240 volt 50 amp breaker supplying power to your RV how many total amps do I have to use. I always thought it was 50 amps but someone told me today that you have a total of 100 amps (50 amps per leg). You have two hot legs (120 volts 50 amps x two legs). So let's here the correct answer please.

The 240 VAC 50 amp RV service utilizes a double pole 50 amp main breaker. Since most RVs don't have any 240 VAC circuits, that means that there is a total of 100 amps available to use at 120 VAC. This is exactly like a residential electric service. A normal residential service is more likely to be 200 amp but the wiring is the same.

This basically gives a 50 amp RV 12,000 watts to use. If this is all used as 120 circuits then that yields 100 amps. If the 12,000 watts were utilized as 240 circuits then that yields 50 amps.
__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
Steve Ownby is offline   Reply With Quote
Old 12-02-2015, 02:36 PM   #3
Senior Member
 
MRUSA14's Avatar
 
Entegra Owners Club
Join Date: Nov 2012
Posts: 8,149
That is correct. Which means a 50 Amp hookup has more than 3 times the power than a 30 amp hookup.
__________________
Marc and Jill, Wellington FL
2013 Entegra Anthem 44SL
2018 Lincoln MKX
MRUSA14 is offline   Reply With Quote
Old 12-02-2015, 07:47 PM   #4
Junior Member
 
Join Date: Aug 2015
Location: Gypsum, CO
Posts: 22
Technically you can only use 80% of the circuit/ breaker rating. So on a 50A you can use 40A on each leg. On the 30A you can use 24A of the one leg.

So a typical RV 50A you have 120VAC * 40A = 4,800 watts on each leg or 9,600 watts with both at 120VAC. On the 30A you have 24A * 120VAC = 2,880 watts on the 30A single leg.
elundquist is offline   Reply With Quote
Old 12-03-2015, 07:38 AM   #5
Senior Member
 
Join Date: Oct 2015
Location: Brighton, MI
Posts: 775
Quote:
Originally Posted by elundquist View Post
Technically you can only use 80% of the circuit/ breaker rating. So on a 50A you can use 40A on each leg. On the 30A you can use 24A of the one leg.

So a typical RV 50A you have 120VAC * 40A = 4,800 watts on each leg or 9,600 watts with both at 120VAC. On the 30A you have 24A * 120VAC = 2,880 watts on the 30A single leg.
I think you've interpreted the NEC specs incorrectly. The 80% rule applies to sizing a circuit breaker. An OCPD (circuit breaker) can only be loaded to 80% of it's rating for continuous loads. A continuous load being a load running non interrupted at it's max current draw for a minimum of 3 hours.

For non-continuous or interrupted loads the circuit breaker can be sized for 100% of it's rating.

What this means is you can absolutely draw 50 amps per leg, or for 30 amp breaker, 30amps. As you would expect the loads in an RV are not considered continuous loads.

You're the 2nd person to post this misinterpretation of the specs. Do some research and post facts, not hearsay.
__________________
Hank & Lynda
2003 Winnebago Adventurer 35U, Workhorse W22
70ChevelleSS is offline   Reply With Quote
Old 12-03-2015, 11:47 AM   #6
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,024
Dual voltage (Center tapped) systems like the 120/240 volt 50 amp RV system or your 150 or 200 or 400 amp home supply (all work the same way) are a bit confusing to folks who do not work with them or who are not trained in them.

It is 50 amp service, but you have the ability to use each amp twice so it is UP TO 100 amp EFFECTIVE, but it is still proper to call it 50 amp.


Might be easier if we converted to watts. 12000 watts. (V/s 3600 for 30 amp service)..

But wait. there's more.. In order to get all the power possible your system MUST BE BALANCED, Exactly BALANCED.. and that.. is all but impossible.. (It can be done... but the odds are like one in several million).
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 12-03-2015, 12:00 PM   #7
Senior Member
 
docj's Avatar
Official iRV2 Sponsor
 
Join Date: May 2011
Posts: 8,305
You've now stumbled onto a topic that causes endless confusion even among supposedly knowledgeable types. What you've been told in this thread is correct, but don't be surprised when you hear someone in the future vociferously argue that it's really only 50A not 100A. Believe me, I've had to walk away even from some so-called RV technicians who don't properly understand the issue.

It's a shame that the industry uses the "50A terminology" rather than calling them 100A. Since the industry started with 30A RVs it would have made a lot more sense and would have been a lot less confusing to have done that instead of calling them 50A. Maybe there's some historical perspective I'm unaware of.
__________________
Joel (AKA docj)--
RV Technology Specialist
docj is offline   Reply With Quote
Old 12-03-2015, 12:23 PM   #8
Senior Member
 
Steve Ownby's Avatar
 
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,587
Quote:
Originally Posted by docj View Post
You've now stumbled onto a topic that causes endless confusion even among supposedly knowledgeable types. What you've been told in this thread is correct, but don't be surprised when you hear someone in the future vociferously argue that it's really only 50A not 100A. Believe me, I've had to walk away even from some so-called RV technicians who don't properly understand the issue.

It's a shame that the industry uses the "50A terminology" rather than calling them 100A. Since the industry started with 30A RVs it would have made a lot more sense and would have been a lot less confusing to have done that instead of calling them 50A. Maybe there's some historical perspective I'm unaware of.

Very true post. So many owners don't understand this topic & seem to believe that RV electric service is somehow different from standard residential service.

Here is a pic of a decal at the entrance cable of my coach:


Name:   ImageUploadedByiRV2 - RV Forum1449170329.044522.jpg
Views: 513
Size:  100.4 KB

It refers to 3 pole 4 wire, which would be 2 hot wires controlled by a 50 amp double pole breaker, a neutral wire and a ground wire. A look at this decal would be all the info that an electrician would need to know what service was required. I don't have access to a 30 amp RV today to see what that decal says.
__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
Steve Ownby is offline   Reply With Quote
Old 12-03-2015, 01:33 PM   #9
Senior Member
 
mriderLeon's Avatar
 
Monaco Owners Club
Join Date: Mar 2015
Location: Prince William, VA
Posts: 157
Quote:
Originally Posted by docj View Post

It's a shame that the industry uses the "50A terminology" rather than calling them 100A. Since the industry started with 30A RVs it would have made a lot more sense and would have been a lot less confusing to have done that instead of calling them 50A. Maybe there's some historical perspective I'm unaware of.
I suppose the correct way to call it would be "50 amp 2 phase " vs "30 amp single phase" or "20 amp single phase"

Do the generators on RVs supply the two legs of service in different phases? And are they phased such that they could be used for a 220 appliance? I guess I need to get out my voltmeter and hit the hot wires in a few different places.
__________________
Leon and Karen
Was - '02 Monaco Dynasty Chancellor
Burned and destroyed Dec 15, 2017
mriderLeon is offline   Reply With Quote
Old 12-03-2015, 01:42 PM   #10
Senior Member
 
Steve Ownby's Avatar
 
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,587
Quote:
Originally Posted by mriderLeon View Post
I suppose the correct way to call it would be "50 amp 2 phase " vs "30 amp single phase" or "20 amp single phase"

Do the generators on RVs supply the two legs of service in different phases? And are they phased such that they could be used for a 220 appliance? I guess I need to get out my voltmeter and hit the hot wires in a few different places.

Speaking of Onan generators, the 10kw and 12.5kw generators produce true 240 power consisting of two out of phase 120VAC legs. The smaller generators produce two legs of 120VAV which are on the same phase so can't be used for 240VAC.
__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
Steve Ownby is offline   Reply With Quote
Old 12-03-2015, 01:53 PM   #11
Senior Member
 
PushedAround's Avatar
 
Tiffin Owners Club
Join Date: Sep 2012
Location: Ambler, PA
Posts: 2,853
Blog Entries: 7
Quote:
Originally Posted by mriderLeon View Post
I suppose the correct way to call it would be "50 amp 2 phase " vs "30 amp single phase" or "20 amp single phase"
No that is incorrect. Both 120 volts (L1 to neutral) or 240 volts (L1 to L2) are single phase power. Commercial power is typically 3 wire where you have L1, L2 and L3, typically plus a neutral. There is such a thing as 2 phase power that was found in older cities like New York and Philadelphia where there are 4 wires that supply power and had to be properly connected, but that is an obsolete technology that is pretty much gone now.
__________________
Larry & Cheryl Oscar, Louie, Ranger & Henry (our Springers)
PushedAround is offline   Reply With Quote
Old 12-03-2015, 02:59 PM   #12
Senior Member
 
Join Date: Oct 2015
Location: Brighton, MI
Posts: 775
Just have to remember that a 50 amp RV outlet is a 240 volt supply. So it can supply 50 amps at 240 volts or 12,000 watts. A 30 amp RV outlet is 120 volts and can supply 30 amps at 120 volts or 3,600 watts.

The amp rating of the breaker is based on the supply voltage. True most loads are 120 volts and that's what we think of but if it's a 240 volt breaker then it's rated amps are at 240 volts not 120.
__________________
Hank & Lynda
2003 Winnebago Adventurer 35U, Workhorse W22
70ChevelleSS is offline   Reply With Quote
Old 12-03-2015, 03:14 PM   #13
Senior Member
 
mriderLeon's Avatar
 
Monaco Owners Club
Join Date: Mar 2015
Location: Prince William, VA
Posts: 157
Quote:
Originally Posted by PushedAround View Post
No that is incorrect. Both 120 volts (L1 to neutral) or 240 volts (L1 to L2) are single phase power. Commercial power is typically 3 wire where you have L1, L2 and L3, typically plus a neutral. There is such a thing as 2 phase power that was found in older cities like New York and Philadelphia where there are 4 wires that supply power and had to be properly connected, but that is an obsolete technology that is pretty much gone now.
Ok. Are we talking the same thing? I thought that normal house current gets any two of the three phases of commercial power.

My house gets L1 and L2 plus neutral. L1 to L2 is 240 single phase, L1 or L2 to neutral is 120v single phase. The house across town gets L1 and L3 for the same connections. But the commercial building gets L1, L2 and L3 for 3 phase power.
__________________
Leon and Karen
Was - '02 Monaco Dynasty Chancellor
Burned and destroyed Dec 15, 2017
mriderLeon is offline   Reply With Quote
Old 12-03-2015, 03:36 PM   #14
Senior Member
 
Join Date: Oct 2015
Location: Brighton, MI
Posts: 775
Quote:
Originally Posted by mriderLeon View Post
Ok. Are we talking the same thing? I thought that normal house current gets any two of the three phases of commercial power.

My house gets L1 and L2 plus neutral. L1 to L2 is 240 single phase, L1 or L2 to neutral is 120v single phase. The house across town gets L1 and L3 for the same connections. But the commercial building gets L1, L2 and L3 for 3 phase power.
It can be confusing. 3 phase wiring in residential areas is not common. It's not possible to have 3 hot legs that are all 180* out of phase with each other, do the math. 2 120v hot legs, 180* out of phase is what is used in residential areas to supply 240v power. Upstream, prior to the step down transformers is a different subject and I don't think we want to go there. Let's stay on this side of the transformer supplying 240v.
__________________
Hank & Lynda
2003 Winnebago Adventurer 35U, Workhorse W22
70ChevelleSS is offline   Reply With Quote
Reply

Tags
electrical, service



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
No 50 AMP service when connected to 50 AMP shore power. Bowlex RV Systems & Appliances 3 10-09-2015 08:01 AM
50 amp electrical plug seperation Mody n Domy MH-General Discussions & Problems 11 06-08-2015 06:16 AM
50 amp service for RV Rog1965char iRV2.com General Discussion 19 05-18-2014 02:09 PM
Lost 50 amp service in coach. jcaab RV Systems & Appliances 21 01-12-2014 01:53 PM
Upgrade Travel Trailer Electrical BassinDmax Boondocking 2 04-23-2013 08:53 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:47 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.