I have a 2003 southwind and the electronic climate master controller just starts a clicking noise. It is located behind the breaker panel box.  what is going on with this piece of equipment?
|
The clicking is a common problem with the Intellitec ECC controller.
The most common causes;
- low voltage to the controller. (check voltage at controller, must be avove 11.5v)
- Poor connection on ECC board connectors. (re-seat all connections to ECC controller)
- Electrical Interference (especially from fluorescent lights, MSW Inverters or defective Converters)
I probably should have listed the electrical interference first, as it is the most common. Try turning off any lights or devices that could be suspected.