Old 10-20-2009, 08:30 AM   #1
Junior Member
 
Join Date: Jan 2003
Location: Mn
Posts: 17
Generac no output.

I have an np-66g Generac and trying to troubleshoot a problem with no a/c output. Shore power works and the inverter works. The generator starts but doesn’t have output it has two circuits a 20 amp and a 30 amp. I can’t find any info on testing the timed delay on the Todd power switch to try to determine if the delay is not functioning or the generator itself is defective. The belt is fine. The windings for the generator have .5 ohms on each winding and all circuit breakers on the generator have continuity. Any tecs out there that can give me a tip on testing the time delay?
firemanmn is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-20-2009, 06:37 PM   #2
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,713
Can't you open up the transfer switch and simply test for 120v on each of the generator hot leads? On most of them the cover is readily removable to access the lugs where the genrator and shore power connect up.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is online now   Reply With Quote
Old 10-20-2009, 08:41 PM   #3
Junior Member
 
Join Date: Jan 2003
Location: Mn
Posts: 17
I checked at the switch and at the circuit breakers on the generator and there is no a/v voltage, so it must be the generator or its components. I don't know if the regulator would cause this problem or how to check the regulator. any ideas?
firemanmn is offline   Reply With Quote
Old 12-27-2009, 03:46 PM   #4
Junior Member
 
Join Date: Dec 2009
Posts: 5
Did you ever resolve this problem? I have the same problem.
glunger is offline   Reply With Quote
Old 12-27-2009, 04:49 PM   #5
Junior Member
 
Join Date: Jan 2003
Location: Mn
Posts: 17
Quote:
Originally Posted by glunger View Post
Did you ever resolve this problem? I have the same problem.
I downloaded the PDF file at generac web site and ohm'd out the windings and determined the stator was shorted between two separate windings. I found a replacement stator on line for $310.00!! I haven't replaced it as of today. I plan on doing it next week or the week after.
firemanmn is offline   Reply With Quote
Old 01-20-2010, 05:18 PM   #6
Junior Member
 
Join Date: Aug 2006
Posts: 10
How did you check ohms across the windings. Did you check between 2a & 6 & 22s & 11 ?
grglunger is offline   Reply With Quote
Old 01-20-2010, 06:04 PM   #7
Junior Member
 
Join Date: Jan 2003
Location: Mn
Posts: 17
Quote:
Originally Posted by grglunger View Post
How did you check ohms across the windings. Did you check between 2a & 6 & 22s & 11 ?
I ohmed across windings with wires disconnected including ground. 2&6, 22s &11,33&44, then 2&11, then 2&33. 2 was shorted to winding 33.

Hope this helps.
firemanmn is offline   Reply With Quote
Old 01-21-2010, 09:56 AM   #8
Junior Member
 
Join Date: Aug 2006
Posts: 10
Thanks for the info
grglunger is offline   Reply With Quote
Old 07-07-2010, 08:33 AM   #9
Junior Member
 
Join Date: Jul 2010
Posts: 1
np-66g Generac no ac output

Quote:
Originally Posted by firemanmn View Post
I ohmed across windings with wires disconnected including ground. 2&6, 22s &11,33&44, then 2&11, then 2&33. 2 was shorted to winding 33.

Hope this helps.
Hi I have a mobile rv repair service. i really think i got a reguator problem . i checked the windings they show good .But i have no power to the voltage regulator .does field have to be excited or do i need to another diretion ?
Rob101087 is offline   Reply With Quote
Old 07-09-2010, 11:11 AM   #10
Junior Member
 
Join Date: Aug 2006
Posts: 10
You should have some voltage tru the reg when gen is running. My problem was the reg.
grglunger is offline   Reply With Quote
Old 07-12-2010, 09:29 PM   #11
Senior Member
 
Ford Super Duty Owner
Join Date: Feb 2002
Posts: 509
I had a like problem low volts on each breaker turned out to be a bad voltage regulator.
__________________
2001 Sea View 31' F53 1 slide 8310 133,000+mi
2012 Jeep Liberty Smi stay and play Duo brake system
Security by Bentley, KF6HCH, God Bless
John Wayne is offline   Reply With Quote
Old 07-12-2010, 09:33 PM   #12
Senior Member
 
ChrisNiemann's Avatar
 
Workhorse Chassis Owner
Join Date: Jul 2010
Location: Oklahoma City, OK
Posts: 235
well great! i just posted a new thread cause i coudn't find anything about mine, come to find out i mis remembered the name of the generator! LOL IDIOT!! anyway, i'm having the exact same problem. Gen starts, runs great, but i don't have any 110V coming out... now after reading all this, i'm nervous about finding out what is wrong with it! would you be willing to email me the pdf for this?

niemannenterprises@hotmail.com

if not i understand, but never hurts to ask!

Thank You,
Chris
ChrisNiemann is offline   Reply With Quote
Old 07-12-2010, 10:04 PM   #13
Senior Member
 
Join Date: Mar 2010
Posts: 124
Generac-no output

Chris - you can download all the service manuals from this site -www.generator-parts.com - you will need your model number to identify which manual you need.
RV Mech Tech is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generac choke irwin Class A Motorhome Discussions 5 07-22-2009 06:31 AM
Output problem with Generac 55G Primepact Generator purplbee MH-General Discussions & Problems 5 08-27-2008 06:14 PM
Changing Coolant in Generac Generator???? Ragman MH-General Discussions & Problems 3 06-17-2008 03:30 AM
Generac Generator Replacement Junior 913 MH-General Discussions & Problems 5 01-13-2008 07:18 AM
DVD sound output walt7474 RV Systems & Appliances 4 04-14-2005 02:01 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:28 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.