Generator Automatic Fail Over

Greetings All,

I did a search before posting here, so my apologies if this has been asked and answered...

Is it possible to have the onboard Onan 5500 generator automatically start if shore power goes out? I am looking for a way to have this fail safe method occur if we are away from the rig while off exploring an area.

I know this is possible with residential/commercial generators, and would like to have this insurance for our Grand Design Momentum 351M Toy Hauler.

Thanks in advance,
__________________
We-R-B.O.B. (Boomers on Bikes)
2022 Grand Design Momentum 351M (on order)
2019 Ford F450 6.7L Power Stroke Diesel
We-R-B.O.B. is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-14-2021, 06:17 PM   #2
Senior Member
 
Join Date: Jul 2014
Posts: 35,420
Yes, its called a AGS system ( Automatic Generator Start )

https://www.donrowe.com/Magnum-Energ...hoCbJ0QAvD_BwE
twinboat is offline   Reply With Quote
Old 07-14-2021, 08:35 PM   #3
Senior Member
 
HarryStone's Avatar


 
Damon Owners Club
Join Date: Apr 2020
Location: Clovis NM
Posts: 4,389
Blog Entries: 4
Technically, the AGS won't start the generator when power goes off. You can set the Air Conditioning to on, and the temp setting on the AGS to a medium temp, and if the power goes off, and the temp goes up, then the AGS will start the generator.
__________________
2006 Damon Daybreak 3276 35'with 5 Star Tuner. 3 200 Amp Lithium batteries and 2000 watt PSW inverter/charger. 2013 Elantra on a Master Tow dolly.
Retired USAF
HarryStone is offline   Reply With Quote
Old 07-14-2021, 10:11 PM   #4
Senior Member
 
Join Date: Mar 2016
Location: Arizona
Posts: 1,134
Quote:
Originally Posted by HarryStone View Post
Technically, the AGS won't start the generator when power goes off. You can set the Air Conditioning to on, and the temp setting on the AGS to a medium temp, and if the power goes off, and the temp goes up, then the AGS will start the generator.
Or if the batteries drop to a level that you set. Assume this accomplishes the objectives you would have if the power drops.
__________________
2016 Fleetwood Bounder 33C. Towing 2017 Jeep Wrangler Unlimited.
Elwood58 is offline   Reply With Quote
Old 07-14-2021, 10:29 PM   #5
Senior Member
 
UFO Pilot's Avatar
 
Winnebago Owners Club
Workhorse Chassis Owner
Join Date: Aug 2007
Location: Sonoma County, CA
Posts: 6,401
I have a 5500 and a Magnum 2012 inverter and I added the AGS myself. It was pretty easy except for pulling in all of the wiring required.
__________________
Wayne & Roberta

08 Winnebago Destination 39W Gas UFO Workhorse Chassis......It's really weird being the same age as old people. I thought getting old would take much longer.
UFO Pilot is offline   Reply With Quote
Old 07-15-2021, 08:54 AM   #6
Member
 
Freightliner Owners Club
Jayco Owners Club
Join Date: Nov 2013
Posts: 37
Kind of brut force but what about using the AGS and setting for battery voltage of anything below 13 volts.
My guess is when you have power the converter/charger keeps your batteries above 13 volts and when power goes out it will drop below 13 quickly. Have it set for an hour and hopefully the power will be back on by then.
__________________
Bob and Angel Instagram @wanderingpeaches
2006 Seneca 34SS (sold)
2018.5 Seneca 37HJ w/2013 GMC Sierra
repeach is offline   Reply With Quote
Old 07-15-2021, 10:10 AM   #7
Senior Member
 
Join Date: Jul 2014
Posts: 35,420
Quote:
Originally Posted by repeach View Post
Kind of brut force but what about using the AGS and setting for battery voltage of anything below 13 volts.

My guess is when you have power the converter/charger keeps your batteries above 13 volts and when power goes out it will drop below 13 quickly. Have it set for an hour and hopefully the power will be back on by then.
You would still need a short delay. If the battery volts dips from moving a slide or inverter, you don't want false starts.
twinboat is offline   Reply With Quote
Old 07-15-2021, 04:11 PM   #8
Member
 
Join Date: Oct 2019
Location: Tucson, AZ
Posts: 43
Quote:
Originally Posted by twinboat View Post
Yes, its called a AGS system ( Automatic Generator Start )

https://www.donrowe.com/Magnum-Energ...hoCbJ0QAvD_BwE

Thanks, Twinboat. This looks like a great device to have, as it monitors not only loss of power, but temps, and battery drain as well.
__________________
We-R-B.O.B. (Boomers on Bikes)
2022 Grand Design Momentum 351M (on order)
2019 Ford F450 6.7L Power Stroke Diesel
We-R-B.O.B. is offline   Reply With Quote
Old 07-15-2021, 04:15 PM   #9
Member
 
Join Date: Oct 2019
Location: Tucson, AZ
Posts: 43
Quote:
Originally Posted by HarryStone View Post
Technically, the AGS won't start the generator when power goes off. You can set the Air Conditioning to on, and the temp setting on the AGS to a medium temp, and if the power goes off, and the temp goes up, then the AGS will start the generator.
Thanks, HarryStone. Makes sense
__________________
We-R-B.O.B. (Boomers on Bikes)
2022 Grand Design Momentum 351M (on order)
2019 Ford F450 6.7L Power Stroke Diesel
We-R-B.O.B. is offline   Reply With Quote
Old 07-15-2021, 04:17 PM   #10
Member
 
Join Date: Oct 2019
Location: Tucson, AZ
Posts: 43
Quote:
Originally Posted by UFO Pilot View Post
I have a 5500 and a Magnum 2012 inverter and I added the AGS myself. It was pretty easy except for pulling in all of the wiring required.
Thanks, UFO Pilot. I am hoping that whatever AGS i get, the wiring will not be too daunting of task.
__________________
We-R-B.O.B. (Boomers on Bikes)
2022 Grand Design Momentum 351M (on order)
2019 Ford F450 6.7L Power Stroke Diesel
We-R-B.O.B. is offline   Reply With Quote
Old 07-30-2021, 01:34 PM   #11
Senior Member
 
Join Date: Aug 2017
Posts: 258
There is a product that will start the generator in the event of a power failure, has nothing to do with temperature or battery voltage and works independent of the inverter/charger. I can't remember the name of it at the moment.
pdeinc is offline   Reply With Quote
Old 07-30-2021, 02:22 PM   #12
Senior Member
 
HarryStone's Avatar


 
Damon Owners Club
Join Date: Apr 2020
Location: Clovis NM
Posts: 4,389
Blog Entries: 4
https://rvautomations.com/features/

Pdeinc, I believe this is what you are talking about.
__________________
2006 Damon Daybreak 3276 35'with 5 Star Tuner. 3 200 Amp Lithium batteries and 2000 watt PSW inverter/charger. 2013 Elantra on a Master Tow dolly.
Retired USAF
HarryStone is offline   Reply With Quote
Old 07-31-2021, 05:00 AM   #13
Senior Member
 
Join Date: Aug 2017
Posts: 258
Quote:
Originally Posted by HarryStone View Post
https://rvautomations.com/features/

Pdeinc, I believe this is what you are talking about.
Actually that's not the one I was remembering but it certainly does what I described plus has the ability to send a text alert which is even better yet. I haven't found the one I was referring to but paused in my search to read about this one.
pdeinc is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
AC system fail- extension cord fail Geoffpruett RV Systems & Appliances 3 07-01-2018 05:32 PM
Automatic generator start system/Generator/shoreline automatic changeover switc Rac912 RV Systems & Appliances 14 01-12-2016 11:51 AM
Generator pickup tube-fail crah Monaco Owner's Forum 18 01-23-2014 01:38 PM
Alternator fail light/chime with engine running and generator/solar on CrazyKnight Monaco Owner's Forum 16 06-18-2013 11:02 PM
Auxilliary Generator Fail? Wolfpack Fan iRV2.com General Discussion 4 08-17-2011 06:25 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 04:40 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.