06-12-2011, 05:30 AM
|
#1
|
Junior Member
Mid Atlantic Campers
Join Date: Jun 2011
Posts: 7
|
Generator stops after 2 hours
Have a Onan 7 kw it stops after 2 hours with a fault code 36. On the road, need help, thanks.
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
06-12-2011, 06:08 AM
|
#2
|
Senior Member
Join Date: Jul 2010
Location: Omaha, NE
Posts: 398
|
Here is a trouble shooting guide that may give you some ideas:
http://www.smokstak.com/forum/attach...4&d=1248949799
Hope it helps and good luck.
__________________
Bob Adams
2013 Winnebago Aspect 27K
E450, V10, CRV, Blue Ox
|
|
|
06-12-2011, 06:23 AM
|
#3
|
Senior Member
Join Date: Jun 2007
Location: Wisconsin
Posts: 985
|
Maybe you can get your model number and use this link to help u.
Cummins Onan
__________________
Renegade Garage Unit
|
|
|
06-12-2011, 06:37 AM
|
#4
|
Senior Member
Damon Owners Club
Join Date: Jun 2010
Location: Loganville Ga.
Posts: 103
|
A very common problem this time of the year is the low pressure oil switch.
The high temps cause the oil to thin out quickly sending a stop command, It thinks you are low on oil. (I had this problem)Mine would run 5-7 min. the first run, then after a 1-2 min pause it would restart and run for 2-3 min then shut off again.
Increase the weight of your oil. After doing this mine runs flawless.
|
|
|
06-12-2011, 07:08 AM
|
#5
|
Junior Member
Mid Atlantic Campers
Join Date: Jun 2011
Posts: 7
|
The oil was changed two days ago with 15w-40 (the same weight I used for five years) do you use heavier oil? It always runs for about 2 hours. Then will not start until 10-15 min then will run for 2 hour again. The model number is 5.5HGJAB-901D
|
|
|
06-12-2011, 10:30 PM
|
#6
|
Junior Member
Join Date: Feb 2011
Posts: 29
|
I'm dying to see what everyone thinks of this one,.... I have this exact generator acting pretty much the same way,..... Thought it was a fuel issue so I fought with it to run it as much as I could on a recent weekend trip,... Just put filled the tank,... It took 18 gallons,..... Drove it around for 45 minutes to mix up the newer fuel and sea foam,..... Same problem...... Spent today draining the tana into cans...... It seems to run great till I put a good load on it (AC)..... Then a while after (when it's good and warmed up) it cuts out,..... When you start it, sometimes it runs for 1 minute,..... Sometimes 35 minutes,...... But at some point it always cuts out,..... I thought it might be water in fuel or too much ethanol,..... When it runs, it runs great,..... Smooth, stable, no missing or backfiring,..... Then it just surges a couple times and dies,....... I've seen code 3 mostly,..... But also 36 on occasion.
Very frustrating, it's a 2011 with 176 hours on it,..... Oil changed recently and that made no difference,.... Pulled plugs and they're clean,..... Fuel was my next option....
Any suggestions? After I confirm it's not fuel, I'm making the 45 min trip to the dealer and dropping it
|
|
|
06-12-2011, 11:22 PM
|
#7
|
Senior Member
Winnebago Owners Club Ford Super Duty Owner
Join Date: Mar 2010
Location: The Dungeon in Broomfield, CO
Posts: 187
|
Check the rubber fuel line that is clamped to the fuel filter under the genset. (I'll bet it's loose) The rubber degrades and the clamping force is reduced. it starts to suck air, which is easier to move than fuel, as it warms up.
Kerry
__________________
Damn, I'm Good!
"I've got dozzens of friends, and the fun never ends, that is, as long as I'm buying."
|
|
|
06-12-2011, 11:45 PM
|
#8
|
Senior Member
Holiday Rambler Owners Club
Join Date: Jul 2009
Location: Dublin, VA
Posts: 391
|
It's amazing that I saw this post b/c our previous RV had a similar problem. It was a Generac and sometimes would run great. But on occasion, it would start and run a couple of minutes and then stop. Never did figure that one out.
By the way, were do you read the source codes on the Onans?
|
|
|
06-13-2011, 04:37 AM
|
#9
|
Junior Member
Mid Atlantic Campers
Join Date: Jun 2011
Posts: 7
|
You can read the codes after a fault by pressing stop on the start/ stop switch a few times. It will blink three times, press the stop again, then it will blink 3 time and additional blinks. ( code 36 : blink...blink ... Blink ............... (6 more blinks))
|
|
|
06-13-2011, 07:04 AM
|
#10
|
Senior Member
Join Date: Jul 2010
Location: Omaha, NE
Posts: 398
|
Quote:
Originally Posted by Rdakri
The oil was changed two days ago with 15w-40 (the same weight I used for five years) do you use heavier oil? It always runs for about 2 hours. Then will not start until 10-15 min then will run for 2 hour again. The model number is 5.5HGJAB-901D
|
Do you have an inverter, and if so, do you have AGS (auto generator start) on it? If you do, and depending on which brand and model you have, there can be a maximum run time setting in the AGS parameters that you can change. It's there for the purpose of preventing the generator from running forever should it start when you are not around. The fact that it runs for a predictable amount of time, of that extent, points to that as being the issue. If this is the case then tell us which brand and model inverter you have. Then we'll do a little research on it and see if we can walk you through the procedure to reset it. If not the case, well then, disregard this post.
__________________
Bob Adams
2013 Winnebago Aspect 27K
E450, V10, CRV, Blue Ox
|
|
|
06-14-2011, 05:18 AM
|
#11
|
Junior Member
Mid Atlantic Campers
Join Date: Jun 2011
Posts: 7
|
No inverter, it usually will run for days
|
|
|
06-14-2011, 05:35 AM
|
#12
|
Senior Member
Thor Owners Club Ford Super Duty Owner
Join Date: Aug 2010
Posts: 860
|
Can it not be getting proper air flow and overheating. Try running while stopped with basement door open.
__________________
Mike, Janet & Duchess (cavalier King Charles)
2008 35B windsport, Brazel's rear TracBar, Koni shocks & Safe T plus steering
|
|
|
07-19-2011, 11:24 AM
|
#13
|
Junior Member
Join Date: Dec 2010
Posts: 20
|
Check for fuel leaks and if its a diesel check the return line to the tank.
|
|
|
07-19-2011, 03:41 PM
|
#14
|
Senior Member
Damon Owners Club Workhorse Chassis Owner
Join Date: Jul 2010
Location: Anderson,IN
Posts: 407
|
My manual says code 36
Check and fill fuel tank
Secure spark plugs leads on spark plugs
check for blocked exhaust
replace air filter element
Remove spark plugs and conduct ignition systems test
Conduct fuel pump tests
Replsce fuel filter
Service brushes and slip rings
Replace faulty rotor or stator
Replace controller
|
|
|
|
|