The Cap'n Obvious stuff first: reset circuit breakers (turn fully off, back on). Failure only on shore power or genset, or both? Is this circuit powered by the inverter? If so, check the inverter for small, push button/pop out circuit breakers on 120VAC input and output. They may be on the side of back of the inverter (usually where you can't see them).
*Some* coaches with large inverters (3000w) may have a smaller circuit breaker box that distributes inverter output to multiple branch circuits. Those breakers will need to be reset, if your Revolution is wired that way.
Inverters usually have a Pass-Through feature that when on shore power or generator, the inverter directly connects the 120VAC input to the 120VAC output terminals and reverts to battery charging. If the pass through relay has failed you will get 120VAC while the inverter runs from the house batteries but not on shore power or genny.
Another possibility is that one Line on your transfer switch is not conducting. Are there other loads in your coach that get power from the same Line of the 50 amp service, and if so, do they work?