Heated outside storage and fresh water tank area

We recently purchased a used MH from a private party. It has flexible ductwork in 3 of the outside storage bins and one in the fresh water bin/area. We do not plan on camping when the weather would get below freezing so why heat them.

Question: If I cap the ends of the ductwork in the bins, would it force more heated air into the main areas of the MH? That would be nice and/or more efficient for spring/fall camping.

Do they make a cap for flexible ductwork?

Thoughts.....

Thanks
Beeper is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-13-2020, 03:07 PM   #2
Senior Member
 
Join Date: Jan 2015
Location: Prescott, Arizona
Posts: 3,240
Blog Entries: 6
Quote:
Originally Posted by Beeper View Post
We recently purchased a used MH from a private party. It has flexible ductwork in 3 of the outside storage bins and one in the fresh water bin/area. We do not plan on camping when the weather would get below freezing so why heat them.

Question: If I cap the ends of the ductwork in the bins, would it force more heated air into the main areas of the MH? That would be nice and/or more efficient for spring/fall camping. Makes sense to me. It would be like closing a register.

Do they make a cap for flexible ductwork? I don't know of a cap but a bag placed over the end and taped in place should work.

Thoughts.....

Thanks

Good Luck!!
__________________
'04 Newmar MADP, 1100w of solar, towing a lifted Rubicon
ByeTheWay is offline   Reply With Quote
Old 10-13-2020, 04:10 PM   #3
Senior Member
 
Join Date: Jul 2014
Location: Sheboygan WI
Posts: 106
ByeTheWay

I'm thinking the bag might melt? One of the ductwork runs is only about 4 feet off the main run from the furnace.

I was thinking maybe I'd just pinch the ends shut and staple and tape them with foil tape.

This will be a Spring job since it getting cold here in WI.
Beeper is offline   Reply With Quote
Old 10-13-2020, 05:15 PM   #4
Senior Member
 
Join Date: Oct 2020
Posts: 661
My concern would be a bit different. Possible restricting air flow too much and shortening the life of the furnace. If those compartments are fairly air tight than the difference in air flow would be insignificant, but so would the difference in heat up time. Is there a way you could maybe remove one or both and then run new ducting somewhere else within the RV?

I only have one such duct and it empties out under the refrigerator/sink cabinets, so it's not really a loss of heat inside the unit.
Goodspike is offline   Reply With Quote
Old 10-14-2020, 10:16 AM   #5
Senior Member
 
Join Date: Jul 2014
Location: Sheboygan WI
Posts: 106
Goodspike...that is a concern. I think the next time I go by the RV dealership I'll stop in and see what they have to say.

Thanks
Beeper is offline   Reply With Quote
Old 10-14-2020, 10:41 AM   #6
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 24,902
If you don't have a manual for your furnace , please find one and read through it .
RV furnaces use a sail switch , to prove to the control board there is good blower operation and air flow through the furnace heat exchanger, before the control board lights the burner .
Closing off furnace outlets can cause back pressure in the system , effecting operation of the sail switch , and the furnace might never light.
Unlike a house system where heat registers can be shut down , and the 120 volt blower motor will just force air flow to open registers , the 12 volt set up in an RV doesn't have the power to overcome a restriction , that's why RV heat registers don't close.
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 10-14-2020, 10:45 AM   #7
Senior Member
 
Join Date: Oct 2020
Posts: 661
Quote:
Originally Posted by Skip426 View Post
Unlike a house system where heat registers can be shut down , and the 120 volt blower motor will just force air flow to open registers , the 12 volt set up in an RV doesn't have the power to overcome a restriction , that's why RV heat registers don't close.
As I mentioned, shutting down too many vents in a house system can damage the furnace. Maybe this sail system is also designed to prevent that type of damage (and/or perhaps a fire in the case of an RV furnace).
Goodspike is offline   Reply With Quote
Old 10-14-2020, 10:55 AM   #8
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 24,902
Quote:
Originally Posted by Goodspike View Post
As I mentioned, shutting down too many vents in a house system can damage the furnace. Maybe this sail system is also designed to prevent that type of damage (and/or perhaps a fire in the case of an RV furnace).
Hopefully all the RV furnace safety features are operational , in order to prevent any fires . The control board logic for burner ignition/ operation , runs through the sail switch AND a heat exchange chamber temp sensor .
Poor air flow the burner won't light , overheated heat exchange chamber , the burner is shut off .
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 10-14-2020, 10:59 AM   #9
Senior Member
 
Join Date: Oct 2020
Posts: 661
Quote:
Originally Posted by Skip426 View Post
Hopefully all the RV furnace safety features are operational , in order to prevent any fires . The control board logic for burner ignition/ operation , runs through the sail switch AND a heat exchange chamber temp sensor .
Poor air flow the burner won't light , overheated heat exchange chamber , the burner is shut off .
I was suggesting the sail switch may be such a safety feature.

But more specifically what I was thinking, an RV furnace tends to be in a smaller tighter enclosure than a house furnace, which is also likely surrounded by either concrete or drywall (attic installations the exception). You don't really need to worry about the heat from a home furnace catching a neighboring surface on fire. I'm thinking of more the type of fire risk that a cast iron wood stove presents for close surfaces.
Goodspike is offline   Reply With Quote
Old 10-14-2020, 12:53 PM   #10
Senior Member
 
Join Date: Sep 2004
Location: Olympic Peninsula
Posts: 430
If I wanted to restrict airflow to those three hoses I would put one of these or something similar on the end of each. You can configure/adjust it to whatever you need...all open, all closed, one open, two closed, all three half open...you get the picture. You could even fab up a bracket out of sheet metal and screw it to the ceiling, wall or floor if so inclined.
https://www.etrailer.com/RV-Vents-an...SABEgIp1fD_BwE
__________________
I'm Jammin
02 Itasca Horizon 36LD, Cat 3126E, Allison MD3000MH
09 Colorado Z71 Ex Cab, SMI AF1, Demco Base Plate & Tow Bar.
JaminSamin is online now   Reply With Quote
Old 10-15-2020, 04:24 PM   #11
Senior Member
 
Join Date: Jul 2014
Location: Sheboygan WI
Posts: 106
JaminSamin....Thanks for the great idea.

Skip426...We have a 2004 Thor Four Winds 31P. It didn't come with a furnace manual but I'll see if I can goggle one. Thanks for the safety concern.
Beeper is offline   Reply With Quote
Old 10-15-2020, 10:14 PM   #12
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 24,411
Quote:
Originally Posted by Skip426 View Post
If you don't have a manual for your furnace , please find one and read through it .
RV furnaces use a sail switch , to prove to the control board there is good blower operation and air flow through the furnace heat exchanger, before the control board lights the burner .
Closing off furnace outlets can cause back pressure in the system , effecting operation of the sail switch , and the furnace might never light.
Unlike a house system where heat registers can be shut down , and the 120 volt blower motor will just force air flow to open registers , the 12 volt set up in an RV doesn't have the power to overcome a restriction , that's why RV heat registers don't close.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG 11B5MX,Infantry retired;Good Sam Life member,FMCA." My fellow Americans, ask not what your country can do for you, ask what you can do for your country. John F. Kennedy
Ray,IN is offline   Reply With Quote
Reply

Tags
fresh water, heat, storage, tank, water



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water pressure issue from pump and slow drip from fresh tank area JPaTV National RV Owner's Forum 12 05-22-2019 06:30 AM
Side Mirrors, heated vs non heated? RickNC Vintage RV's 4 05-29-2018 07:07 PM
Water pump pumping water from fresh water tank into grey tank?? Amen Monaco Owner's Forum 16 09-13-2017 05:15 PM
Fresh water tank and storage 1361 Travel Trailer Discussion 19 07-23-2016 05:25 AM
Heated floor or no heated floor ??? StuartS Newmar Owner's Forum 6 11-28-2014 12:35 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 11:16 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.