Old 02-21-2019, 03:58 AM   #15
Member
 
Join Date: Sep 2016
Posts: 54
Quote:
Originally Posted by Desdinova View Post
THAT is a good question. I was sure I tested that and initially posted that it stays at 12v, but just hooked everything up, and it ONLY stays at 12V for a few seconds each time the ignitor engages.

What should give it the signal that ignition has occured and it should continue to keep the valve open?
Flame has current in it. As long as everything is lined up and clean in the burner the current goes back through the wire through the sparkler into the power board. It tells the relay to close and then hold the LP valve open. No voltage bad relay most likely. As long as everything is clean and burner has no holes in it. Replace the board
12rvrepair is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-21-2019, 10:19 PM   #16
Senior Member
 
Vintage RV Owners Club
Join Date: Sep 2018
Posts: 257
Quote:
Originally Posted by 12rvrepair View Post
Flame has current in it. As long as everything is lined up and clean in the burner the current goes back through the wire through the sparkler into the power board. It tells the relay to close and then hold the LP valve open. No voltage bad relay most likely. As long as everything is clean and burner has no holes in it. Replace the board
Board ordered
Desdinova is offline   Reply With Quote
Old 02-27-2019, 12:30 AM   #17
Senior Member
 
Vintage RV Owners Club
Join Date: Sep 2018
Posts: 257
Replaced the board and valve. Re-installed in rig and it's a MUCH smoother operation. Previously, it would sometimes take one or two cycles of the ignitor to fire up. This time, it fired off the first ignition. Both the board and the valve seem much better quality, better components than the original parts they replaced.

Now, unfortunately, I find that my connection to one of the LP tanks from the regulator is leaking. It's always something I guess, but that's an easy replace and the current one I'm pretty sure is the original, so it's time.
__________________
Miles & Lisa
2020 Forest River "Vibe" 26RK
Skagit County, WA
Desdinova is offline   Reply With Quote
Old 02-27-2019, 09:13 AM   #18
Junior Member
 
Join Date: Aug 2012
Location: Fort Collins , CO.
Posts: 2
Check your sail switch.
ronhallam is offline   Reply With Quote
Old 02-28-2019, 04:56 AM   #19
Junior Member
 
jduffey5's Avatar
 
Join Date: Sep 2015
Posts: 28
Quote:
Originally Posted by 12rvrepair View Post
Classic case where you should have called someone that knows what they are doing. You've spent all that money and it is still not fixed. It is ether a $40 dollar t/stat or a relay in the AC $89. easy to find. You start at A testing not at Z.
We did take to someone who knows what they're doing. In fact 2 different ones! Both RV places were Atwood/Dometic approved service centers that I found by calling Atwood.

Now after spending over $1000 with people who know what they're doing I'm trying to figure it out myself.
jduffey5 is offline   Reply With Quote
Old 03-04-2019, 09:36 PM   #20
Senior Member
 
APhotoWizard's Avatar
 
Join Date: Jan 2014
Posts: 390
Quote:
Originally Posted by Desdinova View Post
Replaced the board and valve. Re-installed in rig and it's a MUCH smoother operation. Previously, it would sometimes take one or two cycles of the ignitor to fire up. This time, it fired off the first ignition. Both the board and the valve seem much better quality, better components than the original parts they replaced.

Now, unfortunately, I find that my connection to one of the LP tanks from the regulator is leaking. It's always something I guess, but that's an easy replace and the current one I'm pretty sure is the original, so it's time.
Glad to see you found the problem. Sad that the experts could not fix the problem. I had the same experience. 5 times in the shop, no success, until I finally did it myself.
__________________
My wife and I would travel full time, but we have to sleep occasionally.
2001 Tiffin Allegro Bus 40 ft DP named the Wild Eagle
Followed by the Eaglet - A 2014 Jeep Grand Cherokee.
APhotoWizard is offline   Reply With Quote
Old 03-05-2019, 04:11 AM   #21
Member
 
Join Date: Sep 2016
Posts: 54
Quote:
Originally Posted by APhotoWizard View Post
Glad to see you found the problem. Sad that the experts could not fix the problem. I had the same experience. 5 times in the shop, no success, until I finally did it myself.
An expert did fix it
12rvrepair is offline   Reply With Quote
Reply

Tags
ace, furnace



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Troubleshoot furnace wiring from converter. SaSuVa Travel Trailer Discussion 2 10-08-2017 07:24 AM
Troubleshoot storage bay aux. furnace fan CaptainJerry Newmar Owner's Forum 27 12-23-2016 08:04 PM
Troubleshoot Atwood Hydro flame furnace MSgtNobody RV Systems & Appliances 2 10-06-2015 06:44 AM
Troubleshoot RV Atwood furnace 8500 IV maxwell18 Monaco Owner's Forum 2 10-04-2015 02:18 PM
Low 12v voltage warning - help troubleshoot dmurdock 5th Wheel Discussion 7 11-19-2005 03:01 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 04:25 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.