I want to add a 50 amp female receptacle powered by my generator

I have a nice big generator on my 2019 Thor Ace.

What I want to do is install a female 50 amp receptacle to my rig that is powered by my generator.

I would like to run my rig's generator and be able to plug a 50 amp cord into it to power a second RV.

I think I know the basics about how to do this, but would welcome any advice, do's and don'ts.

thanks in advance
__________________

__________________
2019 Thor A.C.E. 30.3 - Aspect 26' - '78 Cortez
Lon, Anne and Coco, the very brown Chocolate Lab
DAV Lifetime Member
woodbender is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-22-2020, 07:12 PM   #2
Senior Member
 
Jon_C's Avatar
 
Join Date: Jul 2018
Location: Southeast Texas
Posts: 472
I did same thing except i wanted to power my house 110v ( genny is 2 circuits of 110v not 220v) if needed and works great.

I wired my inverter to where the genny was connected in the transfer switch. I plug in my shore power to the genny outlet when on road in case its needed.

Could just as easy power another rv from the plug as well.

I bought everything off amazon.

It was straightforward to do, I probably spent more time studying the circuits and how to do it than actually doing it.
__________________

Jon_C is offline   Reply With Quote
Old 05-23-2020, 09:21 AM   #3
Member
 
Thor Owners Club
Join Date: Jun 2019
Posts: 97
Quote:
I wired my inverter to where the genny was connected in the transfer switch. I plug in my shore power to the genny outlet when on road in case its needed.
Could you elaborate on this a bit?

I'm stuck in the "studying the circuits and how to do it" phase.
__________________
2019 Thor A.C.E. 30.3 - Aspect 26' - '78 Cortez
Lon, Anne and Coco, the very brown Chocolate Lab
DAV Lifetime Member
woodbender is offline   Reply With Quote
Old 05-23-2020, 11:23 AM   #4
Senior Member
 
Jon_C's Avatar
 
Join Date: Jul 2018
Location: Southeast Texas
Posts: 472
Ill make you a sketch but ill try to explain it.

The transfer switch has 2 inputs and 1 output. The inputs on mine were shore power cable and genny. The switch always selects genny if its running, otherwise it selects shore power and makes The connection to the output ( coach breaker box)

I removed the genny wires from the switch and routed to a new 50a box mounted near the switch. So now gen output goes only to the new box.

I wired my inverter to the transfer switch input vacated by the gen.

Now if i turn on inverter it gets selected by xfer sw and powers breaker box ( all circuits)

When i travel, i plug the shore power cable to the new gen box, if i turn inverter off and start gen the xfer sw selects genny to power the breaker box, all circuits.

This also allows gen to power other things such as house, another rv etc by plugging into the new gen box.
Jon_C is offline   Reply With Quote
Old 05-23-2020, 11:30 AM   #5
YC1
Senior Member
 
YC1's Avatar


 
Holiday Rambler Owners Club
Join Date: Jun 2011
Posts: 7,531
Jon, that is pretty clever. Are you 30 amp or 50? If 50, did you just parallel the old generator inputs with the inverter output?

Might make for a heck of a brown out if the AC's try to come on.
__________________
Myron & Deborah
08 HR Endeavor 40 SKQ
2012 Ford Edge Limited FWD 3.5L
Aluminator tow bar, Demco base plate
YC1 is offline   Reply With Quote
Old 05-23-2020, 02:46 PM   #6
Member
 
Thor Owners Club
Join Date: Jun 2019
Posts: 97
Jon, the part I'm having difficulty getting my brain around is how the inverter plays into this mod.

My initial thought was to in essence clip the 4 wires going from the generator to the transfer switch.

I would put a male plug on the wires leading back to the generator output. Then I would install a female receptacle on the wires leading to the switch.

When plugged in, it would operate like it does now. When unplugged, it would allow me to plug in the 50amp cord from the other rv.

Seems like then I could power up either rv but not both at the same time.

Am I missing something....?
__________________
2019 Thor A.C.E. 30.3 - Aspect 26' - '78 Cortez
Lon, Anne and Coco, the very brown Chocolate Lab
DAV Lifetime Member
woodbender is offline   Reply With Quote
Old 05-23-2020, 02:57 PM   #7
Senior Member
 
Join Date: Jul 2014
Posts: 21,942
Quote:
Originally Posted by woodbender View Post
Jon, the part I'm having difficulty getting my brain around is how the inverter plays into this mod.

My initial thought was to in essence clip the 4 wires going from the generator to the transfer switch.

I would put a male plug on the wires leading back to the generator output. Then I would install a female receptacle on the wires leading to the switch.

When plugged in, it would operate like it does now. When unplugged, it would allow me to plug in the 50amp cord from the other rv.

Seems like then I could power up either rv but not both at the same time.

Am I missing something....?
What your suggesting is fine.

Female plug on generator output.

Male plug, just like shore power plug on end of wire, going to auto transfer switch.

Another option is to just wire a female plug at the generator to RV junction box. If none add one.
With that you can run both RVs, within limits of the generator breakers. There is no need to disconnect the wire going to your auto transfer switch.
twinboat is offline   Reply With Quote
Old 05-23-2020, 03:08 PM   #8
Member
 
Thor Owners Club
Join Date: Jun 2019
Posts: 97
Ah yes, Twin. I had the male and female reversed.

But I like what you suggest about simply wiring in a new female receptacle and calling it a day.
__________________
2019 Thor A.C.E. 30.3 - Aspect 26' - '78 Cortez
Lon, Anne and Coco, the very brown Chocolate Lab
DAV Lifetime Member
woodbender is offline   Reply With Quote
Old 05-23-2020, 03:28 PM   #9
Senior Member
 
Jon_C's Avatar
 
Join Date: Jul 2018
Location: Southeast Texas
Posts: 472
Quote:
Originally Posted by YC1 View Post
Jon, that is pretty clever. Are you 30 amp or 50? If 50, did you just parallel the old generator inputs with the inverter output?

Might make for a heck of a brown out if the AC's try to come on.
50 amp. I wired the inverter output to where the gen was connected inside the xfer sw. I jumpered both hots together as my inverter has only 1 output circuit. I hope that answers your question.

I can run both a/c on inverter with no brownout but thats not what i intend to do
Jon_C is offline   Reply With Quote
Old 05-23-2020, 03:55 PM   #10
Senior Member
 
Jon_C's Avatar
 
Join Date: Jul 2018
Location: Southeast Texas
Posts: 472
Quote:
Originally Posted by woodbender View Post
Jon, the part I'm having difficulty getting my brain around is how the inverter plays into this mod.

My initial thought was to in essence clip the 4 wires going from the generator to the transfer switch.

I would put a male plug on the wires leading back to the generator output. Then I would install a female receptacle on the wires leading to the switch.

When plugged in, it would operate like it does now. When unplugged, it would allow me to plug in the 50amp cord from the other rv.

Seems like then I could power up either rv but not both at the same time.

Am I missing something....?
Sorry for the confusion, you dont have to do anything with the inverter, but that was part of my project so i thought i would include it.

What your describing Will work, or if you parallel the new box with existing wiring you could run 2 rvís up to your gen capacity. Just note the neutral wire is larger gauge
Jon_C is offline   Reply With Quote
Old 05-23-2020, 05:56 PM   #11
Member
 
Thor Owners Club
Join Date: Jun 2019
Posts: 97
Thanks everyone.
__________________
2019 Thor A.C.E. 30.3 - Aspect 26' - '78 Cortez
Lon, Anne and Coco, the very brown Chocolate Lab
DAV Lifetime Member
woodbender is offline   Reply With Quote
Old 05-23-2020, 07:32 PM   #12
YC1
Senior Member
 
YC1's Avatar


 
Holiday Rambler Owners Club
Join Date: Jun 2011
Posts: 7,531
You must have a big inverter and plenty of batteries to run AC's. Thanks for responding to my question.
__________________
Myron & Deborah
08 HR Endeavor 40 SKQ
2012 Ford Edge Limited FWD 3.5L
Aluminator tow bar, Demco base plate
YC1 is offline   Reply With Quote
Old 05-24-2020, 10:57 AM   #13
Senior Member
 
Jon_C's Avatar
 
Join Date: Jul 2018
Location: Southeast Texas
Posts: 472
Quote:
Originally Posted by YC1 View Post
You must have a big inverter and plenty of batteries to run AC's. Thanks for responding to my question.
Your welcome!
5kw inverter and 4 T-105ís about 2 hr runtime on 1 a/c, probably only 1 hr on 2 but I havenít tested.
Jon_C is offline   Reply With Quote
Old 05-25-2020, 09:41 AM   #14
Member
 
Thor Owners Club
Join Date: Jun 2019
Posts: 97
Pardon getting off topic a bit....

Can someone tell me what size output wires (awg) you have for your 50 amp generator?
__________________

__________________
2019 Thor A.C.E. 30.3 - Aspect 26' - '78 Cortez
Lon, Anne and Coco, the very brown Chocolate Lab
DAV Lifetime Member
woodbender is offline   Reply With Quote
Reply

Tags
generator, power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Inverter powered fridge receptacle DAJO Newmar Owner's Forum 16 08-22-2014 03:20 AM
Single female looking for another single female to go on Mexico RV Caravan trip Paul Beddows Solo RV'ers 0 05-23-2014 11:41 PM
non-powered receptacle dwmcg Newmar Owner's Forum 7 10-17-2012 05:26 PM
30 amp male to 50 amp female adapter arnoldjf9191 Class A Motorhome Discussions 33 10-13-2011 05:07 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 10:07 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
×