Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
RV Trip Planning Discussions

Go Back   iRV2 Forums > RV SYSTEMS AND TECHNOLOGIES FORUMS > RV Systems & Appliances
Click Here to Login
Register FilesVendors Registry Blogs FAQ Community Calendar Today's Posts Search Log in
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 07-06-2016, 08:51 PM   #1
Member
 
Join Date: Jan 2016
Posts: 72
Inverter breaker/ wire size

I recently added a 2000 watt inverter to my rig. The inverter manufacturer recommend AWG 1/0 cable for runs up to 9 feet. I used AWG 1/0 cable and my run is about 5 feet from inverter to battery bank. I installed a 250 amp breaker on this run. My battery bank is 420Ahr.

The inverter runs fine except when I try to run my 1500 watt microwave. The microwave works fine but the 250 amp breaker pops after about 30-40 seconds despite the inverter showing its only at about 75% capacity. It's my understanding a 250 amp breaker should be able to handle up to 3000 watts.

Is my issue the 1/0 cable creating too much resistance? If so I guess I could double up the runs with two 1/0 cables for each leg.
Wdeertz is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-06-2016, 11:11 PM   #2
Senior Member
 
MtnTrek's Avatar
 
Join Date: Jul 2015
Location: Currently; SW Cali. Sunny & warm!
Posts: 1,323
Hi,
We only have a 1000W inverter (Magnum) but in reviewing the manual they are requesting the # 1/0 AWG up to 5ft.. Then 5-10ft., #2/0 AWG with a 300A fuse (*rated for DC) protection device.


Best of luck.
__________________
J & J, DRV Suites ES-38RSSA #9679
GM Denali, 3500HD-Max, 4x CC, 8' DRW,
EZGo-TXT, Clubcar Precedent
MtnTrek is offline   Reply With Quote
Old 07-07-2016, 10:08 AM   #3
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2005
Location: Buxton, North Dakota
Posts: 3,940
I suspect that the breaker isn't suited for the application. A fuse may work better for you or a different or larger breaker.
__________________
2003 Winnebago Adventurer 38G F53/ V10 605 watts of Solar
1999 Winnebago Brave 35C F53V10 Handicap Equipped
1999 Jeep Cherokee, 1991 Jeep Wrangler Renegade and 2018 Chevrolet Equinox Diesel
John Hilley is offline   Reply With Quote
Old 07-07-2016, 09:32 PM   #4
Member
 
Join Date: Jan 2016
Posts: 72
Quote:
Originally Posted by John Hilley View Post
I suspect that the breaker isn't suited for the application. A fuse may work better for you or a different or larger breaker.
Thanks for the input. I think the wire size was too small and creating excessive heat causing the breaker to pop. I doubled up the cables and all seems ok now.
Wdeertz is offline   Reply With Quote
Old 07-08-2016, 03:18 PM   #5
Senior Member
 
MtnTrek's Avatar
 
Join Date: Jul 2015
Location: Currently; SW Cali. Sunny & warm!
Posts: 1,323
Good deal, thanks for the update!


Happy motoring.
__________________
J & J, DRV Suites ES-38RSSA #9679
GM Denali, 3500HD-Max, 4x CC, 8' DRW,
EZGo-TXT, Clubcar Precedent
MtnTrek is offline   Reply With Quote
Old 07-08-2016, 03:58 PM   #6
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
FWIW I'm trying to figure out how a warm wire would cause the breaker to pop. 1/0 copper has 0.09827 ohms/1000 ft. so 5 ft is ~0.0005 ohms.

1500 W @ 12 VDC = 1500/12 = 125 A

line drop = 125 x 0.0005=0.0625 V

line drop @ 250 A = 0.125 V

pwr loss @ 250 A = 31.25 W

The line drop does not look like enough to be an issue. OTOH you are dissipating enough power in the wire at a very low resistance to get me looking at the actual connection to the breaker. I would be cleaning and/or tightening up any screw type connectors as the contact resistance could be an issue. That is a good place for a non contact thermometer or an educated finger.
nothermark is offline   Reply With Quote
Old 07-08-2016, 04:08 PM   #7
Senior Member
 
MtnTrek's Avatar
 
Join Date: Jul 2015
Location: Currently; SW Cali. Sunny & warm!
Posts: 1,323
"I would be cleaning and/or tightening up any screw type connectors as the contact resistance could be an issue."


Good observation.
This can often be an issue with other RV electrical related problems. Shore power, pedestal connections etc. another example.
MtnTrek is offline   Reply With Quote
Old 07-08-2016, 04:14 PM   #8
Senior Member
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Aug 2014
Posts: 1,899
Agree that it is not a wire problem.
By adding cable, you actually reconnected the breaker, probably a poor connection the first time.
Be sure you use copper wire.

Dan
__________________
2014 40QBH Phaeton DP Cummins 380HP ISL, Freightliner XC, 2019 Jeep Grand Cherokee Trailhawk TOAD
Blue Ox Aventa tow bar, SMI Air Force One -Cave Creek, AZ.
dpinvidic is offline   Reply With Quote
Old 07-08-2016, 07:55 PM   #9
Member
 
Join Date: Jan 2016
Posts: 72
All new wires and connections so corrosion wasn't an issue. I can confirm all connections were tight and solid. I also ran the math and would have thought a single 1/0 wire was sufficient but all I know it wouldn't work. In hindsight I should have just used 2/0 or 3/0 cable as my starting position.
Wdeertz is offline   Reply With Quote
Old 07-09-2016, 07:13 AM   #10
Senior Member
 
Join Date: Jun 2016
Location: South Jersey
Posts: 113
My 2000W inverter requires 2/0 cable.
Sehc is offline   Reply With Quote
Old 07-09-2016, 09:08 AM   #11
Community Moderator
 
CountryFit's Avatar


 
Join Date: Sep 2011
Location: Between the Oceans
Posts: 8,034
Blog Entries: 4
typically a 2000 w inverter requires 2/0 wires with 300a class t fuse. mine is that. i'd rewire if i were you.
__________________
Steven & Polly
2000 Country Coach Intrigue 40' ISC 350
2018 Ford Explorer 4WD
CountryFit is offline   Reply With Quote
Old 07-09-2016, 07:33 PM   #12
Senior Member
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Aug 2014
Posts: 1,899
Darn...I don't want to start an argument...

But the reason you would use a larger wire is to have less voltage drop across the wire. Having too small of a wire will also cause the wire to heat up because of the power dissipated (P=E x I)

A circuit breaker actually has a bi-metal strip inside which heats up as current increases through it. When the current gets high enough, the Bi-Metal strip bends enough to trip the switch (breaker).

The resistance is given as ohms/foot, so this is why you would pick a larger wire if it was a longer run.

There may be other factors at play here on your installation, and a larger wire can't cause any problems.

It is possible the breaker is a little weak, and the larger wire is acting more like a heat sink and keeping the breaker cool. However, the coffee maker was still well below the trip point of the breaker.

But if you ask any electrician, they would never say you can fix a tripping breaker by using a larger wire....it is just ohms law stuff.

Important thing is it is working

Regards,

Dan
__________________
2014 40QBH Phaeton DP Cummins 380HP ISL, Freightliner XC, 2019 Jeep Grand Cherokee Trailhawk TOAD
Blue Ox Aventa tow bar, SMI Air Force One -Cave Creek, AZ.
dpinvidic is offline   Reply With Quote
Old 07-09-2016, 09:34 PM   #13
Senior Member
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Aug 2014
Posts: 1,899
A few other numbers.

The average efficiency of an inverter is 10% or better.
Assuming 10%, supplying 2000 watts, would be using 2200 watts from your batteries.

2200 watts from 12V requires 183.3 amps

Dan
__________________
2014 40QBH Phaeton DP Cummins 380HP ISL, Freightliner XC, 2019 Jeep Grand Cherokee Trailhawk TOAD
Blue Ox Aventa tow bar, SMI Air Force One -Cave Creek, AZ.
dpinvidic is offline   Reply With Quote
Old 07-09-2016, 10:45 PM   #14
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 4,514
The Magnum MS 2012 recommends 2/0 up to 5 feet and 4/0 from 5'-10". I would say that 1/0 is too small for any 2000W inverter.
__________________
Scotty and Kristen, Airedales Dagny and Wyatt
2007 Newmar Mountain Aire 4528, 450 HP ISM, Allison 4000, 8 Lifeline AGM's
2019 F250 King Ranch 4x4 Powerstroke - SOLD
2022 F350 DRW King Ranch 4 x 4
Scottybdivin is online now   Reply With Quote
Reply

Tags
inverter



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker Breaker hibypass Newmar Owner's Forum 6 08-26-2015 08:58 AM
No breaker on Post - Can I use RV breaker instead? RichK MH-General Discussions & Problems 14 05-11-2012 10:14 AM
Wire and Fuse Size for Inverter CYingling RV Systems & Appliances 6 07-01-2011 06:06 PM
Which Wire? Brake Light Wire Off Switch mickey53usa Freightliner Motorhome Chassis Forum 2 04-14-2009 03:05 PM
6 wire motorhome, 4 wire toad?? smlranger Toads and Motorhome Related Towing 3 02-27-2005 06:03 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 07:30 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.