LP tank hoses leaking help?
a 15 yr old Montana 5th wheel all original
1 propane tank just ran out.
Flipped lever towards 2nd tank, open its valve and removed empty tank.
5 mins later the RED (empty) flag is still RED and furnace wont fire.
I open door where i just removed the empty and hear hissing--GAS LEAKING OUT OF THE HOSE that connects to tank.
I replace empty, keep its valve closed and in a minute GREEN flag.
Apparently the valve that directs which tank feeds is NOT SEALING.
Can it be serviced/oiled/sealed......somehow?
If NOT,
What is it called and where do i get one?
Thanks
Trapper John
__________________
Buy a soldiers meal next chance you get!
The 10 Commandments are NOT suggestions.
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
12-02-2020, 04:23 PM
|
#2
|
Senior Member
Join Date: Mar 2019
Location: Waco, TX
Posts: 201
|
Both tanks have to be in place to pressurize the system or your leaking propane. That’s what I have always been told.
|
|
|
12-02-2020, 09:12 PM
|
#3
|
Senior Member
Monaco Owners Club Freightliner Owners Club Holiday Rambler Owners Club
Join Date: Sep 2019
Location: Thornville, Ohio
Posts: 3,687
|
The valve that you mention is call a change over valve. Now if its pointed to the tank you remove, I think the other tank will leak out of the hose on the tank removed.
You should be able to point the arm to a tank and remove the opposite tank with out it leaking. I have removed a tank and taken it into town, while the other tank provided propane to heat.
Now there is a third setting on this valve. Straight up or down. In this mode it will use from both tanks at the same time. Not sure what happens in this mode if you remove one tank. Does it close that side, or does it leak.
__________________
Art & Joyce
Thornville, OH
Kia Soul pushing a 36' DP Endeavor
|
|
|
12-02-2020, 10:13 PM
|
#4
|
Senior Member
Join Date: Nov 2015
Posts: 26,820
|
They are NOT serviceable
You should be able to remove a cylinder w/o propane leaking out
1st cylinder you OPEN/Place in service is the primary cylinder
Lever points to in service cylinder
You can then OPEN the second cylinder valve
When primary goes empty (vapor pressure is roughly 10#) the Auto Changeover Reg will swap to the secondary cylinder.
Indicator goes RED
Change lever to secondary cylinder...Indicator goes Green
Then Close primary/empty cylinder valve, disconnect pigtail and take to get filled
After the Auto Swap...secondary becomes primary and refilled cylinder becomes secondary
15 yr old.....
Time for a New Auto Changeover Regulator and 2 new pigtail hoses
You got your monies worth...buy new and go camping
Side Note:
Never position lever up/down
Drawing from both cylinders will cause BOTH to be empty at same time
And if you did disconnect the pigtail the other cylinder would blow thru hose at full cylinder pressure
Also
When Opening the Service/OPD valve do it SLOWLY so you do not trip the 'excess flow limiter' device inside the ACME Green Nut on the pigtail
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
|
|
|
12-02-2020, 10:17 PM
|
#5
|
Senior Member
Join Date: Aug 2001
Location: North America somewhere
Posts: 30,903
|
Sounds like the automatic changeover regulator. Does it look like this? That is the automatic changeover regulator assy. If it is leaking it must be replaced. Any RV supplies store will have one.
__________________
2000 Winnebago Ultimate Freedom USQ40JD , ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG 11B5MX,Infantry retired;Good Sam Life member,FMCA. " My fellow Americans, ask not what your country can do for you, ask what you can do for your country. John F. Kennedy
|
|
|
12-03-2020, 10:09 AM
|
#6
|
Senior Member
Join Date: Nov 2018
Location: Beaver Dam, Wisconsin
Posts: 5,147
|
Change over valves come in different sizes and shapes. Make sure the new one fits in place of the old. I replaced the original CAMCO on my Kodiak Cub. I picked a new one that might be more reliable than the CAMCO. I had to build a new mounting bracket for everything to work properly.
__________________
Paul Bristol
Kodiak Cub 176RD
Nissan Pathfinder 2015
|
|
|
12-06-2020, 11:53 AM
|
#7
|
Member
Join Date: Aug 2015
Location: NC
Posts: 75
|
Quote:
Originally Posted by Old-Biscuit
roughly 10#) the Auto Changeover Reg will swap to the secondary cylinder.
Indicator goes RED
Change lever to secondary cylinder...Indicator goes Green
Then Close primary/empty cylinder valve, disconnect pigtail and take to get filled
After the Auto Swap...secondary becomes primary and refilled cylinder becomes secondary
l
|
historically, that's what we did, run on 1 while having other filled.
THanks
__________________
Buy a soldiers meal next chance you get!
The 10 Commandments are NOT suggestions.
|
|
|
12-06-2020, 11:56 AM
|
#8
|
Member
Join Date: Aug 2015
Location: NC
Posts: 75
|
Quote:
Originally Posted by Ray,IN
Sounds like the automatic changeover regulator. Does it look like this? That is the automatic changeover regulator assy. If it is leaking it must be replaced. Any RV supplies store will have one.
|
nosir, that is what's on our Jayco travel trailer where both tanks are next to each other.
This is on a 5th wheel where tanks are 8 ft apart, on opposite sides of the camper..
__________________
Buy a soldiers meal next chance you get!
The 10 Commandments are NOT suggestions.
|
|
|
12-06-2020, 09:02 PM
|
#9
|
Senior Member
Join Date: Aug 2001
Location: North America somewhere
Posts: 30,903
|
Quote:
Originally Posted by 41magnum
nosir, that is what's on our Jayco travel trailer where both tanks are next to each other.
This is on a 5th wheel where tanks are 8 ft apart, on opposite sides of the camper..
|
So you don't have a changeover valve with a manual lever? Length of hoses to cylinders is immaterial.
__________________
2000 Winnebago Ultimate Freedom USQ40JD , ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG 11B5MX,Infantry retired;Good Sam Life member,FMCA. " My fellow Americans, ask not what your country can do for you, ask what you can do for your country. John F. Kennedy
|
|
|
12-07-2020, 09:13 AM
|
#10
|
Member
Join Date: Aug 2015
Location: NC
Posts: 75
|
Quote:
Originally Posted by Ray,IN
So you don't have a changeover valve with a manual lever? Length of hoses to cylinders is immaterial.
|
not like the one pictured
but yes, and the changeover lever is above 1 tank and the other tank is 8 ft on the other side of the unit.
__________________
Buy a soldiers meal next chance you get!
The 10 Commandments are NOT suggestions.
|
|
|
12-07-2020, 09:27 AM
|
#11
|
Senior Member
Join Date: Aug 2001
Location: North America somewhere
Posts: 30,903
|
LP changeover valves are made in different designs by different mfgrs., were mine leaking I'd replace it ASAP. If a hose is leaking it would stop when the manual changeover valve is moved to the in-use cylinder.
__________________
2000 Winnebago Ultimate Freedom USQ40JD , ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG 11B5MX,Infantry retired;Good Sam Life member,FMCA. " My fellow Americans, ask not what your country can do for you, ask what you can do for your country. John F. Kennedy
|
|
|
12-07-2020, 09:29 AM
|
#12
|
Member
Join Date: Aug 2015
Location: NC
Posts: 75
|
ours looks like this Fairview model
__________________
Buy a soldiers meal next chance you get!
The 10 Commandments are NOT suggestions.
|
|
|
12-07-2020, 09:49 AM
|
#13
|
Member
Join Date: Aug 2015
Location: NC
Posts: 75
|
Quote:
Originally Posted by Ray,IN
LP changeover valves are made in different designs by different mfgrs., were mine leaking I'd replace it ASAP. If a hose is leaking it would stop when the manual changeover valve is moved to the in-use cylinder.
|
that's what I was thinking, one should stop when the valve is ON to the other cylinder.
Making me think its only the regulator not sealing and the hoses are ok.
When the changeover is pushed ALL THE WAY over to select a tank, it is kind of mushy and springs back a lil bit too....NOT staying in place anymore.
__________________
Buy a soldiers meal next chance you get!
The 10 Commandments are NOT suggestions.
|
|
|
12-07-2020, 10:04 PM
|
#14
|
Senior Member
Join Date: Nov 2015
Posts: 26,820
|
Quote:
Originally Posted by 41magnum
that's what I was thinking, one should stop when the valve is ON to the other cylinder.
Making me think its only the regulator not sealing and the hoses are ok.
When the changeover is pushed ALL THE WAY over to select a tank, it is kind of mushy and springs back a lil bit too....NOT staying in place anymore.
|
It is BROKE....Buy a replacement
And you might want to buy a replacement for that 30# Red Top reg on side where cylinder is opposite of changeover reg
It's 15+ yrs old
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|