Amazing how many do not read a thread except for initial post.......
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-24-2022, 09:03 AM   #86
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,794
Quote:
Originally Posted by red raby View Post
Just curious : Why do you need 50a when parked at home ? Is someone living in it or is there a certain piece of equipment that won't work when using 30A ? If the latter is the case just go into your breaker box and swap the breaker to the other side of your breaker box. 30A is plenty for a MH unless you have three ACS or are using two AC'S and a range with an oven .I know a lot of people will tell you you can't run two ac's on a 30 amp breaker but I have done so many times .
I never need 50A service at home. I am very, very careful to never run anywhere close to the 30A capability that I have. If I'm running a space heater during extremely cold weather then that a one 100W light bulb in the wet bay are the only things on. In the summer I run one A/C unit.
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is offline   Reply With Quote
Old 01-24-2022, 09:04 AM   #87
Junior Member
 
National RV Owners Club
Join Date: Dec 2017
Location: Fresno’ cs
Posts: 11
Dog bone

Same thing here. Sent it back for a refund Amazon
Philliprn2 is offline   Reply With Quote
Old 01-24-2022, 10:17 AM   #88
Member
 
National RV Owners Club
Freightliner Owners Club
Join Date: Jan 2016
Location: Boise, ID
Posts: 78
IF you have room in the breaker box for a 50amp....they take up TWO spaces as there are TWO hot leads......................
__________________
2004 National Tropic-Cal 350
National 350 is offline   Reply With Quote
Old 01-24-2022, 10:34 AM   #89
Senior Member
 
96 Wideglide's Avatar
 
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 9,751
Quote:
Originally Posted by red raby View Post
I know a lot of people will tell you you can't run two ac's on a 30 amp breaker but I have done so many times .
Yeah, I managed that for a short time until I melted the plug on a 30A extension !
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
96 Wideglide is offline   Reply With Quote
Old 01-24-2022, 11:50 AM   #90
Senior Member
 
Steve 716's Avatar
 
Entegra Owners Club
Spartan Chassis
Join Date: Jul 2016
Location: Box Elder, SD
Posts: 845
A different way to consider

Other than trying to convert your circuit to 50 amps with a dog bone, just use a 30 amp to 50 amp plug adaptor (not corded). Your 30 amp cord plugs into one end and your RV 50 amp receptacle plugs into your RV power input at the other end. This will give you a maximum 30 amp RV input, assuming your circuit breaker is rated for 30 amps. Always use 50 amp gauge rated wiring. I assume your dog bone either used the wrong gauge internal wiring or a lug inside it came loose. I’m surprised that if a lug was the issue your house breaker did not open to break the circuit and prevent your fire. I’m not sure why you need 50 amps when storing your coach.

The other alternative, and the one I recommend, is a 15 amp to 50 amp plug adaptor (not corded). A 15 amp receptacle is on one end and the 50 amp plug on the other. This will give you a maximum 15 amp RV input and will accommodate a standard 15 amp circuit breaker. 15 amps are more than sufficient to run a residential refrigerator full time and keep your batteries charged with a few amps left over.

The second option is what I did. I drilled a hole in my house exterior wall in my garage, ran standard house wiring through it, and mounted it to the side of my house with a weatherproof housing. I ran a 30 amp extension cord to my 15/50 adaptor, plugged them in that was all there was to it.

There are two more steps. First, if you don’t have maintenance free batteries you will need to check the water level once or twice a month. Second, run your generator periodically to test it. You should be doing those things anyway.

On another topic, I sent a lengthy reply to your computer replacement inquiry. Did you receive it?
__________________
2016 Entegra Anthem 42RBQ
2019 Ford Fusion Titanium Hybrid
Steve 716 is offline   Reply With Quote
Old 01-24-2022, 12:04 PM   #91
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,794
Quote:
Originally Posted by Steve 716 View Post
Other than trying to convert your circuit to 50 amps with a dog bone, just use a 30 amp to 50 amp plug adaptor (not corded). Your 30 amp cord plugs into one end and your RV 50 amp receptacle plugs into your RV power input at the other end. This will give you a maximum 30 amp RV input, assuming your circuit breaker is rated for 30 amps. Always use 50 amp gauge rated wiring. I assume your dog bone either used the wrong gauge internal wiring or a lug inside it came loose. I’m surprised that if a lug was the issue your house breaker did not open to break the circuit and prevent your fire. I’m not sure why you need 50 amps when storing your coach.

The other alternative, and the one I recommend, is a 15 amp to 50 amp plug adaptor (not corded). A 15 amp receptacle is on one end and the 50 amp plug on the other. This will give you a maximum 15 amp RV input and will accommodate a standard 15 amp circuit breaker. 15 amps are more than sufficient to run a residential refrigerator full time and keep your batteries charged with a few amps left over.

The second option is what I did. I drilled a hole in my house exterior wall in my garage, ran standard house wiring through it, and mounted it to the side of my house with a weatherproof housing. I ran a 30 amp extension cord to my 15/50 adaptor, plugged them in that was all there was to it.

There are two more steps. First, if you don’t have maintenance free batteries you will need to check the water level once or twice a month. Second, run your generator periodically to test it. You should be doing those things anyway.

On another topic, I sent a lengthy reply to your computer replacement inquiry. Did you receive it?
Yes I did! Your comments are appreciated!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is offline   Reply With Quote
Old 01-24-2022, 12:15 PM   #92
Senior Member
 
96 Wideglide's Avatar
 
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 9,751
Quote:
Originally Posted by Steve 716 View Post

The other alternative, and the one I recommend, is a 15 amp to 50 amp plug adaptor (not corded). A 15 amp receptacle is on one end and the 50 amp plug on the other. This will give you a maximum 15 amp RV input and will accommodate a standard 15 amp circuit breaker. 15 amps are more than sufficient to run a residential refrigerator full time and keep your batteries charged with a few amps left over.
Why would you want to knock a 30A circuit down to 15A?
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
96 Wideglide is offline   Reply With Quote
Old 01-24-2022, 12:25 PM   #93
Senior Member
 
GypsyR's Avatar
 
Join Date: Jul 2019
Location: Upstate SC
Posts: 2,977
I added a 50 amp breaker, the wiring, and an outlet to my car garage so I could park the RV next to it. Though I have "dogbones" it quite frankly never occurred to me to wire it up any lesser way than 50 amp. I have used my coach with a 30 amp hookup and found that I could not run both roof AC's at the same time with it. In my case I like to go out and hang out in the coach whenever I feel like, year round. (I do jigsaws on the table, for one thing.) I also like to run the AC full blast to pre-cool the coach before leaving on summer trips. I've even decided to run a second 50 amp outlet. I keep the coach behind the garage but before leaving on a trip I relocate it to the front for easier loading and water systems service and checks. So I'm putting another more conveniently located for that stuff. Jeez, heavy Romex is expensive these days!
GypsyR is offline   Reply With Quote
Old 01-24-2022, 12:28 PM   #94
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,794
Quote:
Originally Posted by GypsyR View Post
I added a 50 amp breaker, the wiring, and an outlet to my car garage so I could park the RV next to it. Though I have "dogbones" it quite frankly never occurred to me to wire it up any lesser way than 50 amp. I have used my coach with a 30 amp hookup and found that I could not run both roof AC's at the same time with it. In my case I like to go out and hang out in the coach whenever I feel like, year round. (I do jigsaws on the table, for one thing.) I also like to run the AC full blast to pre-cool the coach before leaving on summer trips. I've even decided to run a second 50 amp outlet. I keep the coach behind the garage but before leaving on a trip I relocate it to the front for easier loading and water systems service and checks. So I'm putting another more conveniently located for that stuff. Jeez, heavy Romex is expensive these days!
Man, you got that right! I couldn't believe the price of $5.77 per linear foot for 6-3 at Lowes!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is offline   Reply With Quote
Old 01-24-2022, 01:49 PM   #95
Senior Member
 
mikeh2obury's Avatar
 
Join Date: May 2013
Posts: 420
Do it right.

Wire it up for what you need. In this case 50 amp DP breaker in your box, correct size wire for the run from the box and 50 amp outlet on garage. Your Class A investment is worth having a qualified electrician set you up for success.
mikeh2obury is offline   Reply With Quote
Old 01-24-2022, 05:15 PM   #96
Senior Member
 
featherlite's Avatar
 
Join Date: Sep 2016
Location: huntsville ontario canada
Posts: 116
I have a similar set up in my garage

org. was a 3 wire 30 amp receptical on a 30 amp single braker for the old rv ( red wire not used ) than the power hog came along so for the at home power I used the red wire of the 3 wire 10 gauge old set up and changed the braker to a double 30 amp braker so now I have 30 amps on each leg of the 50 amp receptical . never in the 6 years I have been using it have I had any problem or braker trips . 30 amp is marked on the receptical

but I have 2 amp meters in the coach at the drivers seat , 1 for each leg so I can tell how much power I am using at any time

at our cottage I wired the 50 amp receptical ( marked 40 amps )up with 8 gauge stove wire and a 40 amp braker .
I have 3 a/c units and a ton of other power hog stuff but unless I am driving into the sun on a super hot day I have never used all 3 a/c's at the same time and 40 amps is lots of power for my wife and I



it is all in the power management
Attached Thumbnails
Click image for larger version

Name:	rv control center ac,inverter remote.JPG
Views:	21
Size:	150.9 KB
ID:	354626  
__________________
dave , karen
2000 featherlite vogue cat 550 hp
home base huntsville ont canada
featherlite is offline   Reply With Quote
Old 01-25-2022, 05:41 PM   #97
Member
 
Newmar Owners Club
Ford Super Duty Owner
Join Date: Aug 2011
Location: Springfield, OR
Posts: 45
20 amp to 50 amp?

Quote:
Originally Posted by 96 Wideglide View Post
Why would you want to knock a 30A circuit down to 15A?

Maybe he meant 20 amp. While at my sisters house over the holidays, i had to connect my 50 amp coach to her 20 amp (only) outlet for some minimal power while in her driveway. I used an extension cord connected to a 20 to 30 amp dog bone, and then connected that to my 30 to 50 amp dog bone!...then to my 50 amp surge protector finally connected to my RV's 50 amp power cord!


That seems like a lot of connections that could fail. Is there a better way? Maybe at least a 20 to 50 bone? With that setup, my surge protector also seemed to behave strangely. It would show all three lights green for about half a day, but the last light would show red for a few hours every day! What's with that?


At home I also have a 30 amp connector on the side of my house. Would it be safer to use a 30 amp extension cord so that the 30/50/surge connection is farther from the house (but not under the RV)??
__________________
Murray
2013 30' Newmar Bay Star (2901)
(1993 25' Fleetwood Flair, 2003 27' Itasca Sunova)
murraymcleod is offline   Reply With Quote
Old 01-26-2022, 06:33 AM   #98
Senior Member
 
Join Date: Mar 2019
Posts: 474
Quote:
Originally Posted by red raby View Post
Just curious : Why do you need 50a when parked at home ? Is someone living in it or is there a certain piece of equipment that won't work when using 30A ? If the latter is the case just go into your breaker box and swap the breaker to the other side of your breaker box. 30A is plenty for a MH unless you have three ACS or are using two AC'S and a range with an oven .I know a lot of people will tell you you can't run two ac's on a 30 amp breaker but I have done so many times .
He’s not wanting 50A, just 30A wired to a 50A plug protected by a 30A breaker.

People concerned about this don’t understand electricity.
Jkwilson1989 is offline   Reply With Quote
Reply

Tags
dog



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Outlets have shorted out Kcontres Class A Motorhome Discussions 6 10-07-2016 05:34 PM
Shorted out Diesel Batteries pawolverine Class A Motorhome Discussions 1 06-22-2013 08:07 PM
Shorted out the TriMark power lock system Johnontheroad Monaco Owner's Forum 8 02-14-2010 04:15 PM
Batteries shorted out -- all 8 of them granny MH-General Discussions & Problems 21 10-16-2006 07:39 AM