Old 01-16-2022, 02:48 PM   #1
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,771
My "dogbone" shorted out!

Our house has a 30A receptacle outside. I have a 30a extension cord plugged into it, then a 30A-50A dogbone adapter to the 50A shorepower cable from the MH.

We were sitting the the den when we saw a HUGE amount of white smoke blowing across the patio from the direction of the MH! I was sure that the MH was on fire! I rushed outside and the dogbone connection to the 30A extension cord was blazing and throwing sparks everywhere! It was laying against the vinyl siding on the house, which was also on fire!

I quickly unplugged the 30A cord from the wall receptacle and used a water hose to extinguish the fire!

I want to install a 50A receptacle on the wall to eliminate the extension and dogbone. Since this is a 120VAC circuit, can I just wire the two "hot" legs on the wall outlet together? I'm assuming that's what the dogbone does but want to be sure. Below is the outlet I plan to order.

https://www.amazon.com/gp/product/B0...KIKX0DER&psc=1

The scary thing about this is that had we not been home we would probably lost the house and the MH! The weird thing about this is that the house circuit breaker did not trip!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is online now   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-16-2022, 02:53 PM   #2
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,820
30A only has ONE Hot, ONE Neutral, ONE Ground
*50A has 2 HOTS

The Dogbone takes the ONE HOT and jumpers it to both Hots on the 50A
*RV is only getting 30A total

50A Receptacle requires TWO hots --each fed from Separate 50A Circuit Breaker

**Need to pull an extra wire (#6 ga) and install double 50A CB in Main AC Panel of house

Should check that 30A CB in house ---sparking/smoking dogbone should have tripped






ON EDIT:
Reading your post again.......you want to use the same 30A CB/circuit currently at receptacle and replace the 30A with a 50A receptacle jumpering the ONE 30A hot to both 50A terminals on receptacle
Correct?
YES that can be done.......not up to code

you can have a 50A Outlet fed by 2 separate 30A CBs
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is online now   Reply With Quote
Old 01-16-2022, 02:56 PM   #3
Senior Member
 
Warhorse6's Avatar
 
Join Date: Jul 2020
Posts: 820
Clearly not an electrician, but I would make sure your wiring gauge for the outlet is sufficient to support 50 amp. Suspect you may also need to upgrade your circuit breaker. Glad you caught the issue in time.
__________________
2018 Phaeton 44OH
2023 Chevy Traverse Toad
Florida
Warhorse6 is offline   Reply With Quote
Old 01-16-2022, 02:57 PM   #4
Senior Member
 
Join Date: Mar 2019
Posts: 471
The dogbone does indeed connect the single hot lead from the 30A 120V outlet to both hots on the 50A cord.

In theory, your plan is better than a dogbone of unknown quality.

Before you proceed, I’d want to see that you do have a 30A breaker protecting your outlet. The likely failure was a poor quality connection overheating, but best to be sure.
Jkwilson1989 is online now   Reply With Quote
Old 01-16-2022, 03:07 PM   #5
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,771
This is what it looks like! Not sure why it's sideways!

Click image for larger version

Name:	IMG_20220116_155151722.jpg
Views:	50
Size:	527.9 KB
ID:	353966
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is online now   Reply With Quote
Old 01-16-2022, 03:11 PM   #6
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,771
Quote:
Originally Posted by Old-Biscuit View Post
30A only has ONE Hot, ONE Neutral, ONE Ground
*50A has 2 HOTS

The Dogbone takes the ONE HOT and jumpers it to both Hots on the 50A
*RV is only getting 30A total

50A Receptacle requires TWO hots --each fed from Separate 50A Circuit Breaker

**Need to pull an extra wire (#6 ga) and install double 50A CB in Main AC Panel of house

Should check that 30A CB in house ---sparking/smoking dogbone should have tripped






ON EDIT:
Reading your post again.......you want to use the same 30A CB/circuit currently at receptacle and replace the 30A with a 50A receptacle jumpering the ONE 30A hot to both 50A terminals on receptacle
Correct?

YES that can be done.......not up to code

you can have a 50A Outlet fed by 2 separate 30A CBs
Yes, that's the plan. Wouldn't that be the same thing that the dogbone is doing? I don't have any way to run two 120VAC circuits to the outlet.
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is online now   Reply With Quote
Old 01-16-2022, 03:12 PM   #7
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,771
Quote:
Originally Posted by Jkwilson1989 View Post
The dogbone does indeed connect the single hot lead from the 30A 120V outlet to both hots on the 50A cord.

In theory, your plan is better than a dogbone of unknown quality.

Before you proceed, I’d want to see that you do have a 30A breaker protecting your outlet. The likely failure was a poor quality connection overheating, but best to be sure.
I plan to replace that 30A breaker for sure!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is online now   Reply With Quote
Old 01-16-2022, 03:15 PM   #8
Senior Member
 
Join Date: May 2018
Posts: 3,204
The connection most likely overheated either at the plug blades or the dogbone had some broken strands at the blade connection from repeated use/bending or from poor construction and the load was sufficient to cause it to get hot enough over time to start a fire. The breaker didn't trip because there was no overload. This happens with engine block heaters when the cords get old, strands break inside the cord and the connection eventually becomes what is known as a "glowing connection". Over several hours a glowing connection gradually starts burning the plastics around it with a very hot fire which, if undetected, can burn the entire vehicle down. The breaker doesn't trip until enough plastic burns to expose bare conductors which then make contact and trip it, but by then the fire is well under way. Were you running heat pumps or space heaters?
__________________
Brian, 2011 Winnebago Via Class A on Sprinter Chassis
2000 Jeep TJ toad
Tucson, AZ
bigb56 is online now   Reply With Quote
Old 01-16-2022, 03:20 PM   #9
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,771
Quote:
Originally Posted by bigb56 View Post
The connection most likely overheated either at the plug blades or the dogbone had some broken strands at the blade connection from repeated use/bending or from poor construction and the load was sufficient to cause it to get hot enough over time to start a fire. The breaker didn't trip because there was no overload. This happens with engine block heaters when the cords get old, strands break inside the cord and the connection eventually becomes what is known as a "glowing connection". Over several hours a glowing connection gradually starts burning the plastics around it with a very hot fire which, if undetected, can burn the entire vehicle down. The breaker doesn't trip until enough plastic burns to expose bare conductors which then make contact and trip it, but by then the fire is well under way. Were you running heat pumps or space heaters?
Only one space heater.
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is online now   Reply With Quote
Old 01-16-2022, 04:14 PM   #10
Senior Member
 
ArtJoyce's Avatar
 
Monaco Owners Club
Freightliner Owners Club
Holiday Rambler Owners Club
Join Date: Sep 2019
Location: Thornville, Ohio
Posts: 3,687
I have seen through the years the different dogbone's melt including one I had. Most of them just are not made well.

What happens is inside they develop a poor connection with a micro gap. The connection continues to work through micro arching which is where the heat comes from. The circuit is not overloading so no breaker is tried.

I still use dogbone's. But now I come back and fell the dogbone for heat. Any heat, even warm I trash the dogbone.

You could do what you were thinking of on your 30 outlet. Its not to code and would be very confusing. I would label the outlet with a sticker as to what it is. I have a 50 amp out that has two phase 30 amp wire and breaker. It was an old welder circuit and I never replaces the 10 guage wire with #6.
__________________
Art & Joyce
Thornville, OH
Kia Soul pushing a 36' DP Endeavor
ArtJoyce is offline   Reply With Quote
Old 01-16-2022, 04:24 PM   #11
Senior Member
 
Xmcdog's Avatar
 
Join Date: Dec 2019
Location: Alberta
Posts: 1,976
Joe,
I would suggest strongly that you hire an electrician to put in the correct outside outlet that you need. Sorry but with electricity, if you have to ask you shouldn't do it. Stay safe and hire a pro.
Glad you were there to catch your fire.
__________________
Jeff and Annette Smith. Sparky, lemon Beagle.
2022 Chevy Equinox RS.
2007 Dutch Star
Xmcdog is offline   Reply With Quote
Old 01-16-2022, 04:54 PM   #12
Senior Member
 
Winemaker2's Avatar
 
Join Date: Nov 2006
Location: Western NY
Posts: 6,149
Quote:
Originally Posted by Xmcdog View Post
Joe,

I would suggest strongly that you hire an electrician to put in the correct outside outlet that you need. Sorry but with electricity, if you have to ask you shouldn't do it. Stay safe and hire a pro.

Glad you were there to catch your fire.
Agree
Above proves you can start a fire with less than 30A and without tripping breakers.
Lots of house fires get started from 15A circuits and lamp cords.
The benefit of dog bones is that are out in open air... make connections in a wall or elect box and if not done correctly you have moved the source closer to combustibles.
__________________
Don & Marge
'13 Newmar Ventana 3433 - '14 CR-V TOAD
'03 Winnebago Adventurer 31Y - SOLD
Winemaker2 is offline   Reply With Quote
Old 01-16-2022, 04:55 PM   #13
Senior Member
 
Join Date: May 2018
Posts: 3,204
Quote:
Originally Posted by MSHappyCampers View Post
Only one space heater.
That's 1,500 watts and plenty enough to expose a weak connection, For that kind of draw everything must be in good condition, all strands of wire intact and connected at terminals, terminals tight and blades clean and fitting tightly into sockets. An extension cord can exacerbate the situation.
Some, if not all dogbones and many cords are put together with solder or tinned leads at the terminations and once they are overheated enough the solder can melt and create a loose connection. A fire can easily start with current well under the circuit breaker rating.

You might also consider cutting out a square of siding and replacing with stainless steel around the outlet.
__________________
Brian, 2011 Winnebago Via Class A on Sprinter Chassis
2000 Jeep TJ toad
Tucson, AZ
bigb56 is online now   Reply With Quote
Old 01-16-2022, 05:00 PM   #14
Senior Member
 
dizcom's Avatar
 
Freightliner Owners Club
Holiday Rambler Owners Club
Join Date: Jun 2021
Posts: 1,629
Quote:
Originally Posted by Tedo View Post
Clearly not an electrician, but I would make sure your wiring gauge for the outlet is sufficient to support 50 amp. Suspect you may also need to upgrade your circuit breaker. Glad you caught the issue in time.

Yep, and that your run isn't too long to drop the voltage too far. This also takes the problem you encountered and moves it inside your home. You're better off running a whole new 50 amp run, with circuits, rather than trying to jury rig something. It's what we did. It's not as hard as it might seem.
__________________
2021 Holiday Rambler Armada 44LE
2021 Jeep Wrangler High Altitude toad w/Ready Brute Elite II
dizcom is offline   Reply With Quote
Reply

Tags
dog



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Outlets have shorted out Kcontres Class A Motorhome Discussions 6 10-07-2016 05:34 PM
Shorted out Diesel Batteries pawolverine Class A Motorhome Discussions 1 06-22-2013 08:07 PM
Shorted out the TriMark power lock system Johnontheroad Monaco Owner's Forum 8 02-14-2010 04:15 PM
Batteries shorted out -- all 8 of them granny MH-General Discussions & Problems 21 10-16-2006 07:39 AM
Heater shorted out 2BlueHeelers Toy Haulers Discussion 5 09-22-2006 06:50 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:09 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.