My "dogbone" shorted out!
Our house has a 30A receptacle outside. I have a 30a extension cord plugged into it, then a 30A-50A dogbone adapter to the 50A shorepower cable from the MH.
We were sitting the the den when we saw a HUGE amount of white smoke blowing across the patio from the direction of the MH! I was sure that the MH was on fire! I rushed outside and the dogbone connection to the 30A extension cord was blazing and throwing sparks everywhere! It was laying against the vinyl siding on the house, which was also on fire!
I quickly unplugged the 30A cord from the wall receptacle and used a water hose to extinguish the fire!
I want to install a 50A receptacle on the wall to eliminate the extension and dogbone. Since this is a 120VAC circuit, can I just wire the two "hot" legs on the wall outlet together? I'm assuming that's what the dogbone does but want to be sure. Below is the outlet I plan to order.
https://www.amazon.com/gp/product/B0...KIKX0DER&psc=1
The scary thing about this is that had we not been home we would probably lost the house and the MH! The weird thing about this is that the house circuit breaker did not trip!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
01-16-2022, 02:53 PM
|
#2
|
Senior Member
Join Date: Nov 2015
Posts: 26,820
|
30A only has ONE Hot, ONE Neutral, ONE Ground
*50A has 2 HOTS
The Dogbone takes the ONE HOT and jumpers it to both Hots on the 50A
*RV is only getting 30A total
50A Receptacle requires TWO hots --each fed from Separate 50A Circuit Breaker
**Need to pull an extra wire (#6 ga) and install double 50A CB in Main AC Panel of house
Should check that 30A CB in house ---sparking/smoking dogbone should have tripped
ON EDIT:
Reading your post again.......you want to use the same 30A CB/circuit currently at receptacle and replace the 30A with a 50A receptacle jumpering the ONE 30A hot to both 50A terminals on receptacle
Correct?
YES that can be done.......not up to code
you can have a 50A Outlet fed by 2 separate 30A CBs
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
|
|
|
01-16-2022, 02:56 PM
|
#3
|
Senior Member
Join Date: Jul 2020
Posts: 820
|
Clearly not an electrician, but I would make sure your wiring gauge for the outlet is sufficient to support 50 amp. Suspect you may also need to upgrade your circuit breaker. Glad you caught the issue in time.
__________________
2018 Phaeton 44OH
2023 Chevy Traverse Toad
Florida
|
|
|
01-16-2022, 02:57 PM
|
#4
|
Senior Member
Join Date: Mar 2019
Posts: 471
|
The dogbone does indeed connect the single hot lead from the 30A 120V outlet to both hots on the 50A cord.
In theory, your plan is better than a dogbone of unknown quality.
Before you proceed, I’d want to see that you do have a 30A breaker protecting your outlet. The likely failure was a poor quality connection overheating, but best to be sure.
|
|
|
01-16-2022, 03:07 PM
|
#5
|
Senior Member/RVM #90
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,771
|
This is what it looks like! Not sure why it's sideways!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
|
|
|
01-16-2022, 03:11 PM
|
#6
|
Senior Member/RVM #90
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,771
|
Quote:
Originally Posted by Old-Biscuit
30A only has ONE Hot, ONE Neutral, ONE Ground
*50A has 2 HOTS
The Dogbone takes the ONE HOT and jumpers it to both Hots on the 50A
*RV is only getting 30A total
50A Receptacle requires TWO hots --each fed from Separate 50A Circuit Breaker
**Need to pull an extra wire (#6 ga) and install double 50A CB in Main AC Panel of house
Should check that 30A CB in house ---sparking/smoking dogbone should have tripped
ON EDIT:
Reading your post again....... you want to use the same 30A CB/circuit currently at receptacle and replace the 30A with a 50A receptacle jumpering the ONE 30A hot to both 50A terminals on receptacle
Correct?
YES that can be done.......not up to code
you can have a 50A Outlet fed by 2 separate 30A CBs
|
Yes, that's the plan. Wouldn't that be the same thing that the dogbone is doing? I don't have any way to run two 120VAC circuits to the outlet.
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
|
|
|
01-16-2022, 03:12 PM
|
#7
|
Senior Member/RVM #90
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,771
|
Quote:
Originally Posted by Jkwilson1989
The dogbone does indeed connect the single hot lead from the 30A 120V outlet to both hots on the 50A cord.
In theory, your plan is better than a dogbone of unknown quality.
Before you proceed, I’d want to see that you do have a 30A breaker protecting your outlet. The likely failure was a poor quality connection overheating, but best to be sure.
|
I plan to replace that 30A breaker for sure!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
|
|
|
01-16-2022, 03:15 PM
|
#8
|
Senior Member
Join Date: May 2018
Posts: 3,204
|
The connection most likely overheated either at the plug blades or the dogbone had some broken strands at the blade connection from repeated use/bending or from poor construction and the load was sufficient to cause it to get hot enough over time to start a fire. The breaker didn't trip because there was no overload. This happens with engine block heaters when the cords get old, strands break inside the cord and the connection eventually becomes what is known as a "glowing connection". Over several hours a glowing connection gradually starts burning the plastics around it with a very hot fire which, if undetected, can burn the entire vehicle down. The breaker doesn't trip until enough plastic burns to expose bare conductors which then make contact and trip it, but by then the fire is well under way. Were you running heat pumps or space heaters?
__________________
Brian, 2011 Winnebago Via Class A on Sprinter Chassis
2000 Jeep TJ toad
Tucson, AZ
|
|
|
01-16-2022, 03:20 PM
|
#9
|
Senior Member/RVM #90
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,771
|
Quote:
Originally Posted by bigb56
The connection most likely overheated either at the plug blades or the dogbone had some broken strands at the blade connection from repeated use/bending or from poor construction and the load was sufficient to cause it to get hot enough over time to start a fire. The breaker didn't trip because there was no overload. This happens with engine block heaters when the cords get old, strands break inside the cord and the connection eventually becomes what is known as a "glowing connection". Over several hours a glowing connection gradually starts burning the plastics around it with a very hot fire which, if undetected, can burn the entire vehicle down. The breaker doesn't trip until enough plastic burns to expose bare conductors which then make contact and trip it, but by then the fire is well under way. Were you running heat pumps or space heaters?
|
Only one space heater.
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
|
|
|
01-16-2022, 04:14 PM
|
#10
|
Senior Member
Monaco Owners Club Freightliner Owners Club Holiday Rambler Owners Club
Join Date: Sep 2019
Location: Thornville, Ohio
Posts: 3,687
|
I have seen through the years the different dogbone's melt including one I had. Most of them just are not made well.
What happens is inside they develop a poor connection with a micro gap. The connection continues to work through micro arching which is where the heat comes from. The circuit is not overloading so no breaker is tried.
I still use dogbone's. But now I come back and fell the dogbone for heat. Any heat, even warm I trash the dogbone.
You could do what you were thinking of on your 30 outlet. Its not to code and would be very confusing. I would label the outlet with a sticker as to what it is. I have a 50 amp out that has two phase 30 amp wire and breaker. It was an old welder circuit and I never replaces the 10 guage wire with #6.
__________________
Art & Joyce
Thornville, OH
Kia Soul pushing a 36' DP Endeavor
|
|
|
01-16-2022, 04:24 PM
|
#11
|
Senior Member
Join Date: Dec 2019
Location: Alberta
Posts: 1,976
|
Joe,
I would suggest strongly that you hire an electrician to put in the correct outside outlet that you need. Sorry but with electricity, if you have to ask you shouldn't do it. Stay safe and hire a pro.
Glad you were there to catch your fire.
__________________
Jeff and Annette Smith. Sparky, lemon Beagle.
2022 Chevy Equinox RS.
2007 Dutch Star
|
|
|
01-16-2022, 04:54 PM
|
#12
|
Senior Member
Join Date: Nov 2006
Location: Western NY
Posts: 6,149
|
Quote:
Originally Posted by Xmcdog
Joe,
I would suggest strongly that you hire an electrician to put in the correct outside outlet that you need. Sorry but with electricity, if you have to ask you shouldn't do it. Stay safe and hire a pro.
Glad you were there to catch your fire.
|
Agree
Above proves you can start a fire with less than 30A and without tripping breakers.
Lots of house fires get started from 15A circuits and lamp cords.
The benefit of dog bones is that are out in open air... make connections in a wall or elect box and if not done correctly you have moved the source closer to combustibles.
__________________
Don & Marge
'13 Newmar Ventana 3433 - '14 CR-V TOAD
'03 Winnebago Adventurer 31Y - SOLD
|
|
|
01-16-2022, 04:55 PM
|
#13
|
Senior Member
Join Date: May 2018
Posts: 3,204
|
Quote:
Originally Posted by MSHappyCampers
Only one space heater.
|
That's 1,500 watts and plenty enough to expose a weak connection, For that kind of draw everything must be in good condition, all strands of wire intact and connected at terminals, terminals tight and blades clean and fitting tightly into sockets. An extension cord can exacerbate the situation.
Some, if not all dogbones and many cords are put together with solder or tinned leads at the terminations and once they are overheated enough the solder can melt and create a loose connection. A fire can easily start with current well under the circuit breaker rating.
You might also consider cutting out a square of siding and replacing with stainless steel around the outlet.
__________________
Brian, 2011 Winnebago Via Class A on Sprinter Chassis
2000 Jeep TJ toad
Tucson, AZ
|
|
|
01-16-2022, 05:00 PM
|
#14
|
Senior Member
Freightliner Owners Club Holiday Rambler Owners Club
Join Date: Jun 2021
Posts: 1,629
|
Quote:
Originally Posted by Tedo
Clearly not an electrician, but I would make sure your wiring gauge for the outlet is sufficient to support 50 amp. Suspect you may also need to upgrade your circuit breaker. Glad you caught the issue in time.
|
Yep, and that your run isn't too long to drop the voltage too far. This also takes the problem you encountered and moves it inside your home. You're better off running a whole new 50 amp run, with circuits, rather than trying to jury rig something. It's what we did. It's not as hard as it might seem.
__________________
2021 Holiday Rambler Armada 44LE
2021 Jeep Wrangler High Altitude toad w/Ready Brute Elite II
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|