Onan Emerald Plus 5000 Watt Generator
How do I remove and replace the starter solenoid and/or the starter?
__________________
2000 R-Vision Condor 1310, 34ft.,Chevy 454 Fuel Injection Auto O/D
2014 Honda CR-V, Blue OX Aventa Tow,SMI Brake
USAF(Ret) 1958-1978 Vietnam Veteran
|
|
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
05-15-2022, 04:31 PM
|
#2
|
Senior Member
Join Date: Aug 2020
Location: Ohio
Posts: 1,398
|
Unplug all batteries and shore cord.. remove front panel on gen.. very carefully full panel out.. should be there right hand side.. 2 LG wires connected and may one small..
It can be tested in place..
Now for starter.. you are going to have small hands or many different hand tools..
It looks like can be done.. but if you need more room.. you are going to.. have to.. drop it down a few inches.. you can rent a motorcycle jack.. or use a floor jack and cribbing..
Use all safety precautions..
Use your cellphone with camera and flash and record all wires 1st..
You can use your cell phone with camera and flash and record up under inside back of gen.. and see.. the starter is only held on by 2 each 1/2 in looking bolts..
The starters are generally bullet proof..
What problems are you having ?
Good luck and keep us posted
__________________
2000 southwind storm, workhorse custom chassis with 7.4l vortec
|
|
|
05-16-2022, 04:36 AM
|
#3
|
Senior Member
Join Date: Jul 2008
Location: Winter Garden, FL
Posts: 169
|
Thank you for the quick response.
I did some troubleshooting prior to this post. My generator was starting and running fine then one day it would not even make a sound when trying to start. I checked my house batteries and discovered they were weak so I removed and replaced the house batteries with new ones. After the installation I tried to start my generator and all I got was a clicking sound when I engaged the starter switch both the remote switch and the switch on the generator panel. I then removed the electric panel from the front of the generator to check wiring which was all good. Fuses were also checked and found to be good. Next, I checked the voltage from the outlet side of the control board to the solenoid and it showed 12.5 volts. I then jumped a wire directly from positive battery post to the coil terminal on the starter solenoid and I received the same result of the clicking sound. That leads me to believe that I have a bad starter solenoid and/or a bad starter. Any additional suggestions would be greatly appreciated.
__________________
2000 R-Vision Condor 1310, 34ft.,Chevy 454 Fuel Injection Auto O/D
2014 Honda CR-V, Blue OX Aventa Tow,SMI Brake
USAF(Ret) 1958-1978 Vietnam Veteran
|
|
|
05-17-2022, 09:49 AM
|
#4
|
Senior Member
Join Date: Aug 2020
Location: Ohio
Posts: 1,398
|
One other idea.. check your ground.. use jumper cable and clamp down on beefy part of gen motor.. then run other side to beefy part of frame.. then give it a try.. free and 5mins to check for good ground..
Next if not the problem..go back ove battery connections.. clean them up real good and lugs.. sometimes gen gets starting power from chassis battery.. so
I would do next.. use all safety precautions... and jump directly from car to gen selenoid.. clamp on grounds first .. then clamp pos from car to starter side of gen selenoid. See what I get.. takes 10mins and free..
Then if still not starting.. I would think about pulling starter.. many a/p stores test starter for free..
Good luck and keep us posted
__________________
2000 southwind storm, workhorse custom chassis with 7.4l vortec
|
|
|
05-17-2022, 06:00 PM
|
#5
|
Senior Member
Join Date: Dec 2021
Posts: 124
|
You could try bypassing the solenoid by jumpering across its "hot" contacts with a screwdriver, to see if the starter spins.
If it still doesn't spin, try tapping the case of the starter with a hammer while attempting to crank the engine. Often, when a starter goes bad, it can be jarred into occasionally still working.
__________________
2021 Casita Spirit Dlx - San Antonio, TX
|
|
|
05-30-2022, 10:48 AM
|
#6
|
Senior Member
Join Date: Jul 2008
Location: Winter Garden, FL
Posts: 169
|
Update:
After additional troubleshooting my Aux Gen start issue, I isolated the problem to the starter relay solenoid. I removed and replaced the solenoid with a new one. (Part # 307-2570). The generator started without further issues. Thank you to all for your suggestions.
__________________
2000 R-Vision Condor 1310, 34ft.,Chevy 454 Fuel Injection Auto O/D
2014 Honda CR-V, Blue OX Aventa Tow,SMI Brake
USAF(Ret) 1958-1978 Vietnam Veteran
|
|
|
 |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|