Onan Gen Power missing at one leg

I am trying to troubleshoot my gen and looking for some knowledge. Any ideas would be appreciated.

Generator has 2 breakers on the control panel. There are 2 black wires coming from deeper inside the generator into the control panel each feeding their respective breaker. Measuring directly on the wire terminal at the breaker, one wire has 120 VAC and the other has 0. I am trying to find the cause of the dead leg and how to fix this.

I took a few measurements based off other suggestions, not sure what they mean. supposedly all within spec.

1. Pins 1 and 10 (Rotor, sliprings, brushes), 88 ohms cold after 2 months, ~33 ohms AVG after cranking and taking multiple measurements

2. Pins 3 and 9 (aux stator windings), 2.7 ohms

3. Pins 4 and 5 (windings) , 0.4 ohms

Onan 5500 Marquis Gold out of a 2004 5th Wheel
Model #: 5.5HGJAB-1038C
S/N: K030564396
PrestonH22 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-10-2025, 04:38 PM   #2
Senior Member


 
Join Date: Mar 2024
Location: Bohemia NY
Posts: 1,601
You need to determine how your generator was wired at installation. There is usually a choice for split leg 240-120 volts with neutral or for both to be 120V and the Neutral. Basically, the windings are in series with a center, or they are paralleled. For the later both breakers will be 120 to the neutral or ground and 0 to each other. There should be a connection box or terminals to set that up. Either a wire is open there or the generator lost a winding on the stator.
__________________
Dennis
Bohemia NY
2008 Nimbus 342 SE Carlyle
d23haynes57 is offline   Reply With Quote
Old 01-10-2025, 04:41 PM   #3
Senior Member
 
DarkSideJeep's Avatar
 
Entegra Owners Club
Spartan Chassis
Join Date: May 2023
Location: Cedar Rapids, IA
Posts: 1,593
Quote:
Originally Posted by PrestonH22 View Post
I am trying to troubleshoot my gen and looking for some knowledge. Any ideas would be appreciated.

Generator has 2 breakers on the control panel. There are 2 black wires coming from deeper inside the generator into the control panel each feeding their respective breaker. Measuring directly on the wire terminal at the breaker, one wire has 120 VAC and the other has 0. I am trying to find the cause of the dead leg and how to fix this.

I took a few measurements based off other suggestions, not sure what they mean. supposedly all within spec.

1. Pins 1 and 10 (Rotor, sliprings, brushes), 88 ohms cold after 2 months, ~33 ohms AVG after cranking and taking multiple measurements

2. Pins 3 and 9 (aux stator windings), 2.7 ohms

3. Pins 4 and 5 (windings) , 0.4 ohms

Onan 5500 Marquis Gold out of a 2004 5th Wheel
Model #: 5.5HGJAB-1038C
S/N: K030564396
The generator has two brakers as well. Have you checked the generator breakers? I have been there myself.
__________________
Dan, 2018 Thor ACE 30.3, 1996 Tiffin Allegro
2022 Entegra Aspire 44W, -- Spartan k2 chassis, -- 450 L9 Cummins
2020 Jeep Gladiator Rubicon
DarkSideJeep is offline   Reply With Quote
Reply

Tags
onan, power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Omg leg rest extenders.. monaco windsor leg rest stuck Jbrougham Monaco Owner's Forum 7 11-11-2023 09:29 AM
One leg missing Capt. Steve Entegra Owner's Forum 15 07-08-2019 07:48 PM
One leg missing on generator FixerCQI RV Systems & Appliances 12 10-17-2018 04:04 PM
Power Line One Panel Limits One Leg 50 Amp circuit to 30 Amps SteveG Winnebago Industries Owner's Forum 17 03-05-2008 05:43 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:07 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, vBulletin Solutions, Inc.