Having issues with my Onan QD8000 in my Journey.
Runs fine, shows 66amps on power panel, but blows the circuit breaker on generator if load gets above like 20amp. I can run one AC fine, but when second one kicks in it trips the breaker. I can swap them and get the same result so there doesn’t appear to be an issue with the AC units. Any ideas?
__________________
2014 Journey 36M
Caymanedge is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-06-2023, 08:23 PM   #2
Senior Member
 
2004Horizon's Avatar
 
Join Date: May 2023
Posts: 607
First guess, open your ATS box and torque your lugs. (With power disconnected.)

Second, and follow up recommendation, open your circuit panel and torque your lugs.

Note: There is a torque, but frankly, with a lot of force, you can't over-torque with a 9" screwdriver, unless you possess the strength of a 30 year old (still).

The point is that if you can put 1/8+ turns on the lugs, then you maybe overheating at this connection point.

It worth a shot and it's free. It's also a good think to do as preventative maintenance every 8 years or so.

===

If this is not the problem, my guess, and this is very likely, is it possible you have never Tuned-up your basement AC? ...Have you?

That said, and you have not, then my guess is your AC hard-start-capacitor (and motor starter (aka PTCR)) needs to be replaced.

You should also measure and replace your run capacitors too! Plus these are cheap on Amazon.

What is possible, IMO, is that you are getting a much higher "in-rush" current when you start your AC compressors; and your power panel can't pick it up, because you need a clamp meter designed to measure "in-rush" and I'm sure your power panel will not.

That said, your basement or roof AC is talking you to you you better listen unless you want a compressor in your AC to fail? Fortunately, the cost to DIY a run compactor is cheap and almost anyone can do it if you take pictures and keep track of the wires so you don't mix-up where they go.
__________________
2004 Itasca Horizon 40AD
2004Horizon is offline   Reply With Quote
Old 06-06-2023, 08:28 PM   #3
Senior Member
 
2004Horizon's Avatar
 
Join Date: May 2023
Posts: 607
As for your ATS, if you visibly inspect it and see any thing burnt inside, that's a good signal your lugs are lose and it's a 50/50 chance tightening them will fix your problem for free.

If you need to replace your ATS, make 100A ATS (in today's market) or one you are SURE can handle the 70A neutral your generator demands. Me... I would buy a used Parallax 5070 over any new ATS that uses Chinese contactors, but that's another discussion for another time.

This 70A requirement is because your Onan is rated for 2-35A wires, which to my knowledge is only specified on the QD7500 and QD8000. I.e., you have 2-Neutral-White Wires going to your ATS. So your new ATS need to handle 2-neutral wires. And any RV tech that tells you different is setting up for a fire down the road, potentially!

Just be mindful, an ATS that advertises 50A service may not be what you need. This is why you may need to buy a 100A-ATS box, because they don't make "true 70A-neutral" ATS boxes like they used to.

And I'm going to assume you have a Parallax ATS-5070 like the ones in the diagram below. And if you are really good, you can rebuild or repair your ATS easily, but finding those old 8-Pin Contactors is not easy; and these things are rivetted in place. So you have to deal with that. But if your bridge-rectifier is bad, then you can replace that easily. (Of course, you need to find other posts that talk to this.)

Let's hope you just need to tighten your lugs!

Message to all: If you have never torqued down your ATS and circuit panel lugs, after 15 years, you may be living on borrowed time!
Attached Thumbnails
Click image for larger version

Name:	1 ATS-5070 transfer switch 120V coil relays (KEEP).jpg
Views:	11
Size:	324.4 KB
ID:	394678   Click image for larger version

Name:	1 2004 Horizon Automatic Transfer Switch ATS-5070 #2.jpg
Views:	7
Size:	161.3 KB
ID:	394679  

__________________
2004 Itasca Horizon 40AD
2004Horizon is offline   Reply With Quote
Old 06-06-2023, 08:32 PM   #4
Senior Member
 
Join Date: Jan 2021
Posts: 194
Good deal, thank you!
__________________
2014 Journey 36M
Caymanedge is offline   Reply With Quote
Old 06-07-2023, 06:10 AM   #5
Senior Member
 
Workhorse Chassis Owner
iRV2 No Limits Club
Join Date: Jul 2005
Location: USA
Posts: 5,633
Do you have a red dot temperature gun? Next time you run the genny, try to take aim at the troublesome breaker. I'll bet it's failing or has a loose connection. The breaker should be at the same temp as it's surroundings, until it gets close to max rating.
__________________
TandW
TandW is online now   Reply With Quote
Old 06-07-2023, 07:33 PM   #6
Senior Member
 
Join Date: Jan 2021
Posts: 194
No luck so far. 100amp ATS is fairly new and all the lugs are tight. Power panel lugs are tight as well. All fluids filled up.
Both AC units have soft starts and I am currently running them on a 30amp power feed so it’s not an issue in the rig.
I do not have a temp gauge but I am suspecting it is the breaker. 8 spike t9 Cummins and it’s available for $150. Going to try and get a temp gauge before I spend that money.
Thanks for the help.
__________________
2014 Journey 36M
Caymanedge is offline   Reply With Quote
Old 06-08-2023, 11:15 AM   #7
Senior Member
 
2004Horizon's Avatar
 
Join Date: May 2023
Posts: 607
Sorry. Thought you were were working with a basement AC.

Good idea to rule out a weak breaker. Is the breaker one of the 2-35A breakers on the generator?

If so, let us know if you can switch the neutral wires to see if your "good" breaker trips after you do this. If not, then it's not a bad breaker.
__________________
2004 Itasca Horizon 40AD
2004Horizon is offline   Reply With Quote
Old 06-08-2023, 11:20 AM   #8
Senior Member
 
Join Date: Apr 2018
Posts: 3,441
Quote:
Originally Posted by Caymanedge View Post
Having issues with my Onan QD8000 in my Journey.
Runs fine, shows 66amps on power panel, but blows the circuit breaker on generator if load gets above like 20amp. I can run one AC fine, but when second one kicks in it trips the breaker. I can swap them and get the same result so there doesn’t appear to be an issue with the AC units. Any ideas?
Breakers are a bimetal spring. They go bad all the time. Next time you run the gen check the breaker that blows for heating up. Your finger on the face of it will suffice. The two breakers can be tied together with a bar so both will trip. But if so one should be hotter than the other
__________________
2004 Dynasty 4
shootist is offline   Reply With Quote
Old 06-08-2023, 11:47 AM   #9
Senior Member
 
Join Date: Jan 2021
Posts: 194
Grabbed an IR. Thermometer this morning. Will try and check it later today. Cummins gave me the new breaker number, 2P 35 $143…320-1875-01
__________________
2014 Journey 36M
Caymanedge is offline   Reply With Quote
Old 06-08-2023, 11:50 AM   #10
Senior Member
 
Join Date: Jan 2021
Posts: 194
Forgot to mention. When I checked the oil the yellow end to the dipstick came off….so I picked up some hi-temp JB Weld….
__________________
2014 Journey 36M
Caymanedge is offline   Reply With Quote
Old 06-08-2023, 11:56 AM   #11
Senior Member
 
Join Date: Apr 2018
Posts: 3,441
Quote:
Originally Posted by Caymanedge View Post
Grabbed an IR. Thermometer this morning. Will try and check it later today. Cummins gave me the new breaker number, 2P 35 $143…320-1875-01
Does blue seas make a breaker that will fit. That is out of this world pricing

https://www.bluesea.com/products/cat...rcuit_Breakers

Blueseas makes top quality stuff, onan/ cummins is chinese for the most part.
__________________
2004 Dynasty 4
shootist is offline   Reply With Quote
Old 06-10-2023, 05:33 AM   #12
Senior Member
 
Join Date: Jan 2021
Posts: 194
So I finally got a chance to do some testing. Circuit breaker sat at an ambient 75d, fired up the generator and after a few minutes running only moved up a degree or two. Then I engaged one AC and the breaker temp rose to 78d. After 10min I engaged the second AC and after 5min it only rose to 80d. It ran longer than previously when the breaker would trip with no signs of overheating issues and it never tripped.

When it failed previously the ambient temp was much higher, like 87. Might have played a factor but hard to imagine it would move it that much. Research shows the breaker could function normally up to 130d.

I will test it again tomorrow when at a location to better run these tests.

Thanks for the input.
__________________
2014 Journey 36M
Caymanedge is offline   Reply With Quote
Old 06-10-2023, 10:39 AM   #13
Senior Member
 
Join Date: Apr 2018
Posts: 3,441
Quote:
Originally Posted by Caymanedge View Post
So I finally got a chance to do some testing. Circuit breaker sat at an ambient 75d, fired up the generator and after a few minutes running only moved up a degree or two. Then I engaged one AC and the breaker temp rose to 78d. After 10min I engaged the second AC and after 5min it only rose to 80d. It ran longer than previously when the breaker would trip with no signs of overheating issues and it never tripped.

When it failed previously the ambient temp was much higher, like 87. Might have played a factor but hard to imagine it would move it that much. Research shows the breaker could function normally up to 130d.

I will test it again tomorrow when at a location to better run these tests.

Thanks for the input.
You are not measuring the actual bimetallic spring.
__________________
2004 Dynasty 4
shootist is offline   Reply With Quote
Old 06-10-2023, 10:47 AM   #14
Senior Member
 
Join Date: Jul 2014
Posts: 34,354
First, where are you reading 66 amps from your generator ?
Amps are a measurement of current being drawn not available.

Then you say the amps are reading 20 for 1 A/C. Even that's a bit high, unless you have other things going.
twinboat is offline   Reply With Quote
Reply

Tags
onan, troubleshooting



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan QD8000 overheat issue that may not be overheating treypal RV Systems & Appliances 19 06-12-2018 02:59 PM
QD8000 Onan Generator Won’t Start RustyTools Monaco Owner's Forum 10 08-14-2017 03:18 PM
Onan HDKAK QD8000 H-Spec Gremlin f15epilot Travel Supreme Owner's Forum 3 03-04-2017 04:26 PM
Onan QD8000 HDKAK Overheat code 33 al.m RV Systems & Appliances 2 05-30-2011 12:04 PM
Onan QD8000 Quits. Belt? ronboc RV Systems & Appliances 12 08-27-2007 09:34 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 08:34 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2023, vBulletin Solutions, Inc.