Quote:
Originally Posted by tina2
Hi everybody,
Need your help again!
I finished my solar panels project, here is my final configuration.
I use "Renogy 3000W inverter" & 3 x Ampere Time 12V 100Ah Lithium batteries. But when I tried to run the air conditioner, it drew about 1.7kw (reading from the battery monitor). It lasted about 1 minute then the inverter beeped and reset automatically. Same thing happened when I use the Microwave (about 1.4kw). At first, I used 6AWG to parallel connect the batteries (by the battery manual), I thought maybe the cable couldn't afford the load, but today I switch to #2/0 to parallel connect the batteries, but still not working.
Can anyone give me some advice?
Thanks!!!
|
Sorry about the delay replying. Anything new to report?
My thoughts based on the above.
Nothing else is running when you fire up the microwave or A/C, right? I.e., the water heater is turned off at the water heater or its breaker is open (if it's on its own breaker). Etc.
With three batteries, you should be good for 300 amps. The Renogy 3 kW inverter can draw up to about 280 amps, but only if it has 3 kW of load on it. You have the batteries connected for proper current balance, so the 200 amps or so from a microwave or A/C should not cause a battery BMS to "open." If one were to open, the others would overload and also open quickly. A "weak" BMS might open prematurely triggering the others to also open. Seems unlikely but can't be ruled out from what we know so far.
There's nothing but #2/0 from the batteries to the inverter on both negative and positive routes, right?
Do you feel any heat in the #2/0 connections after the trip?
Can you watch the DC voltage with the monitor when you switch on the microwave or A/C (I'd use just the microwave for testing for now).
What is the monitor showing in the way of load/current on the batteries just before you switch on the microwave?
If you want, you can call me. I'll post my number in a pm. Best to call since I don't get on-line every day and am preparing for an excursion.