Old 02-20-2015, 10:46 AM   #71
Member
 
RichK's Avatar
 
Join Date: May 2012
Posts: 55
Question - is it unusual to get a different voltage reading from hot to ground than from hot to neutral? (Inside the RV).

I tested today - 122.4 hot to neutral, and 120.7 hot to ground in an outlet inside the RV. Might that mean a slight issue with a ground connection, or is that normal?

Maybe they use smaller gauge wiring for ground and that explains the difference?
__________________
2012 Winnebago Aspect 30C with Honda Fit TOAD.
More About Me: TrekWithUs.com
RichK is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-20-2015, 02:05 PM   #72
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
Sometimes the ground is a smaller gauge wire than whats used for the load and neutral.

Dr4Film ----- Richard
Dr4Film is offline   Reply With Quote
Old 02-20-2015, 07:17 PM   #73
Senior Member
 
Join Date: Feb 2010
Posts: 4,654
That is indicating out of balance load which may be fine but it could make an EMS nuts.

The neutral carries the difference current between L1 and L2.

If there is more L1 than L2 then current will flow in neutral.

There should never be current flow in safety ground.

If there is a bad neutral connection someplace and the correct loads in the correct place it could make your ems nuts but I do not know if the ems is looking at that unless a 50 amp coach.

And it could be in the campground someplace and just happens when stars line up...

Measure between safety ground and neutral and see how high of a voltage you can measure and follow up with ems manufacturer to see if it reacts as yours does.

It may be you are golden and campgrounds bad.

We had squirrels chew up our neutral in the overhead drop and the large machines (240vac) were fine but light bulbs went real funny as they were 120 vac and created unbalanced loads.

Ours was open connection so lightbulb had effect but a poor connection requires more load.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 02-20-2015, 07:48 PM   #74
Senior Member
 
Old Bounder's Avatar
 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 1,636
Quote:
Originally Posted by TQ60 View Post
That is indicating out of balance load which may be fine but it could make an EMS nuts.
The neutral carries the difference current between L1 and L2.
If there is more L1 than L2 then current will flow in neutral.
There should never be current flow in safety ground.
If there is a bad neutral connection someplace and the correct loads in the correct place it could make your ems nuts but I do not know if the ems is looking at that unless a 50 amp coach.
And it could be in the campground someplace and just happens when stars line up...
Measure between safety ground and neutral and see how high of a voltage you can measure and follow up with ems manufacturer to see if it reacts as yours does.
It may be you are golden and campgrounds bad.
We had squirrels chew up our neutral in the overhead drop and the large machines (240vac) were fine but light bulbs went real funny as they were 120 vac and created unbalanced loads.
Ours was open connection so lightbulb had effect but a poor connection requires more load.
I think this is a 30amp coach we have been discussing. No balancing currents involved.
__________________
'97 Bounder 34V, F53 7.5L-460
Old Bounder is offline   Reply With Quote
Old 02-20-2015, 07:54 PM   #75
Senior Member
 
Old Bounder's Avatar
 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 1,636
Quote:
Originally Posted by RichK View Post
Question - is it unusual to get a different voltage reading from hot to ground than from hot to neutral? (Inside the RV).

I tested today - 122.4 hot to neutral, and 120.7 hot to ground in an outlet inside the RV. Might that mean a slight issue with a ground connection, or is that normal?

Maybe they use smaller gauge wiring for ground and that explains the difference?
Not entirely unusual in a motorhome. The ground and neutral are tied together back in the shore supply somewhere, but your working voltage is between Hot and Neutral. Depending on where you are taking the measurements, there could be many more feet of wire involved in that measurement. It's nothing to be concerned about.
__________________
'97 Bounder 34V, F53 7.5L-460
Old Bounder is offline   Reply With Quote
Old 02-20-2015, 08:14 PM   #76
Senior Member
 
Join Date: Feb 2010
Posts: 4,654
30 amp coach so no balance issue with coach but campground is 240.

So possible...there was another thread regarding this and the voltage between safety ground and neutral was in question but not confirmed the max allowed under NEC.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 02-20-2015, 08:46 PM   #77
Senior Member
 
Old Bounder's Avatar
 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 1,636
Quote:
Originally Posted by TQ60 View Post
30 amp coach so no balance issue with coach but campground is 240.

So possible...there was another thread regarding this and the voltage between safety ground and neutral was in question but not confirmed the max allowed under NEC.
As I read this thread, there have been multiple different campground systems involved where this failure was experienced.

Something in the path, from external power cord plug to transfer switch contacts, is not playing nice in this RV.
__________________
'97 Bounder 34V, F53 7.5L-460
Old Bounder is offline   Reply With Quote
Old 02-21-2015, 07:12 AM   #78
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
Where are ground and neutral tied together? I would assume it would be the outlet box just from seeing grounding rods at the installations I remember. That would also require one of the common blocks at the distribution panel in the MH be floating. I wonder if there is a problem there.
nothermark is offline   Reply With Quote
Old 02-21-2015, 09:06 AM   #79
Senior Member
 
Old Bounder's Avatar
 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 1,636
Quote:
Originally Posted by nothermark View Post
Where are ground and neutral tied together? I would assume it would be the outlet box just from seeing grounding rods at the installations I remember. That would also require one of the common blocks at the distribution panel in the MH be floating. I wonder if there is a problem there.
There is nothing in that scenario that would cause the recorded symptoms.

Bonding the neutral and ground in the RV Distribution Panel usually does not cause an operational problem, but does present a potential safety concern. By code, the RV panel should be wired just as a sub panel in a S/B.
__________________
'97 Bounder 34V, F53 7.5L-460
Old Bounder is offline   Reply With Quote
Old 02-21-2015, 10:22 AM   #80
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
Correct!

RV Pedestals should have the ground and neutral separated and not bonded.

The bonding should only be done at the main supply panel and not at any sub-panels.

Dr4Film ----- Richard
Dr4Film is offline   Reply With Quote
Old 02-21-2015, 10:26 AM   #81
Member
 
RichK's Avatar
 
Join Date: May 2012
Posts: 55
I think I've found the problem! I did as suggested, and ran the Generator, ran things on the generator, etc.. Put it back to park power, tried running the Microwave and BAM power went out.

My EMS NEVER lost power - the readout showed 123V the entire time.

So I have a bad transfer switch, right? I have a Parallax Power Supply ATS 301 FYI.

Yes, I had the cover off the transfer switch - power was coming in 122.4V, and no power was coming out for a couple minutes.

Should I try cleaning all the contacts and wires? Or is the Transfer switch bad?

Thanks again for everyone's help!
__________________
2012 Winnebago Aspect 30C with Honda Fit TOAD.
More About Me: TrekWithUs.com
RichK is offline   Reply With Quote
Old 02-21-2015, 11:11 AM   #82
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
OK....Take a look at the ESCO ATS LPTBRD.

I prefer this model over others. Mine has been working FULL-TIME since 2001 without a glitch.

Dr4Film ----- Richard
Dr4Film is offline   Reply With Quote
Old 02-21-2015, 11:49 AM   #83
Senior Member
 
Old Bounder's Avatar
 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 1,636
Quote:
Originally Posted by RichK View Post
Should I try cleaning all the contacts and wires? Or is the Transfer switch bad?

Thanks again for everyone's help!
Absolutely you can try cleaning the contacts. Unplug from shore power and clean the Normally Closed contacts on the power contactor.

A few swipes through the contacts with very fine emery cloth should do it.

AS Richard suggested, a new ATS may be in your future. IOTA also makes a very reliable (and much less expensive) ATS.
__________________
'97 Bounder 34V, F53 7.5L-460
Old Bounder is offline   Reply With Quote
Old 02-21-2015, 11:53 AM   #84
Member
 
RichK's Avatar
 
Join Date: May 2012
Posts: 55
Quote:
Originally Posted by Old Bounder View Post
Absolutely you can try cleaning the contacts. Unplug from shore power and clean the Normally Closed contacts on the power contactor.

A few swipes through the contacts with very fine emery cloth should do it.

AS Richard suggested, a new ATS may be in your future. IOTA also makes a very reliable (and much less expensive) ATS.
Will do (try cleaning). It looks like IOTA no longer makes transfer switches? I looked online and can't find any for sale.
__________________
2012 Winnebago Aspect 30C with Honda Fit TOAD.
More About Me: TrekWithUs.com
RichK is offline   Reply With Quote
Reply

Tags
power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
No Battery Power to Coach LairdT Toy Haulers Discussion 10 01-09-2015 06:47 AM
2002 Holiday Rambler Ambassador No Shore Power !! vrodcp Monaco Owner's Forum 2 11-10-2014 04:54 AM
Switching Power Sources on an 85 Mallard wolf_7669 Vintage RV's 4 10-28-2014 02:16 PM
Suddenly, no DC power Campnfools RV Systems & Appliances 1 08-31-2014 08:57 PM
Uugghhh... No power but shore power TPLI Class C Motorhome Discussions 22 05-08-2014 08:41 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:00 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.