Question about building a battery bank and using 24v system

Hello,
had an earlier thread asking about battery bank questions.
I have another question now, I was going to build a 24v system and use a 24v inverter because it's more efficient and the wire will be less expensive.

I bought a used Onan 5500 LP generator and it doesn't have a starting battery.
I am also gong to get en electric tongue jack.
With the 24v system I will need to buy another battery and put it on a charger every night.

Would it be simpler to just buy the 12v inverter (24v is the same price) and spend the extra money for the larger wire and not have to buy another 12v battery to start the generator and power the jack?

I just bought the batteries and I think I got a good deal and bought four 12v 200ah AGM for $1,260 shipped. I cannot used lead acid since the only room for batteries is inside the concession trailer that's being built.
Jasper7821 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-07-2014, 08:53 AM   #2
Senior Member
 
Join Date: Sep 2012
Posts: 4,232
If you do things in series, you can run the wire from the battery that is 12V to the genset.
jesilvas is offline   Reply With Quote
Old 02-07-2014, 08:57 AM   #3
Senior Member
 
jackfish's Avatar
 
Join Date: Jan 2013
Location: Rural Independence, OR
Posts: 951
I believe you could also connect the generator starter and power jack to the 24 volt battery bank with a 24VDC to 12VDC step down transformer supplying sufficient current (150 amps?).
__________________
2013 Leisure Travel Vans Unity U24MB, 635 watts solar, 440 AH batteries, 2000 watt inverter, Koni struts and shocks, Hellwig rear anti-swaybar, SumoSprings front and back, 2012 Hyundai Accent SE, Blue Ox baseplates, Aladdin towbar and Patriot
jackfish is offline   Reply With Quote
Old 02-07-2014, 08:59 AM   #4
Senior Member
 
Join Date: Apr 2010
Location: Western
Posts: 324
A very few folks have converted to 24Vdc house battery banks. As you mention there are a few pluses including the fact that at twice the voltage the current is cut in half so smaller wires can be used, however the downside IMO far out weights the upside. Most all your DC equipment is designed for 12Vdc. You could use DC to DC Boost/Buck conversion which adds complexity and more chances for failure.

For me I stuck with 12Vdc and large wires as needed - welding cables are great.

PS - Those AGM's are indeed Lead Acid batteries just sealed up tight as compared the vented GC Batteries I use
KJINTF is offline   Reply With Quote
Old 02-07-2014, 09:04 AM   #5
Senior Member
 
jackfish's Avatar
 
Join Date: Jan 2013
Location: Rural Independence, OR
Posts: 951
As related in the OP's other thread, it is a concession trailer with a 24 volt system supplying 110V AC through a 24 volt inverter or the generator. No 12 volt draws, except the generator starter and power jack which I would suspect will be used intermittently.
__________________
2013 Leisure Travel Vans Unity U24MB, 635 watts solar, 440 AH batteries, 2000 watt inverter, Koni struts and shocks, Hellwig rear anti-swaybar, SumoSprings front and back, 2012 Hyundai Accent SE, Blue Ox baseplates, Aladdin towbar and Patriot
jackfish is offline   Reply With Quote
Old 02-07-2014, 09:32 AM   #6
Member
 
Join Date: Nov 2013
Posts: 65
Quote:
Originally Posted by jackfish View Post
I believe you could also connect the generator starter and power jack to the 24 volt battery bank with a 24VDC to 12VDC step down transformer supplying sufficient current (150 amps?).
Thanks, that may be a way. Would save me a $75 battery but buying a $100 converter. But at least I wouldn't have to charge a separate battery. Just the shore power plug at night to charge the battery bank.

If I did something like that, I would connect it between the battery bank and inverter right?
Jasper7821 is offline   Reply With Quote
Old 02-07-2014, 09:47 AM   #7
Senior Member
 
Old Bounder's Avatar
 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 1,636
Quote:
Originally Posted by Jasper7821 View Post
Thanks, that may be a way. Would save me a $75 battery but buying a $100 converter. But at least I wouldn't have to charge a separate battery. Just the shore power plug at night to charge the battery bank.

If I did something like that, I would connect it between the battery bank and inverter right?
NO. If you did that, you would step the whole system back down to 12V and lose all the benefit of going to 24V in the first place. You would attach it in parallel with the inverter (just to make a step down to 12V to start your generator)

I'm still of the opinion that a simple connection at the 12V level in your battery bank to obtain 12V to occasionally start your generator is the best way to go. The effect on the battery bank (or any individual battery) will be negligible, in spite of what others claim.
__________________
'97 Bounder 34V, F53 7.5L-460
Old Bounder is offline   Reply With Quote
Old 02-07-2014, 12:29 PM   #8
Member
 
Join Date: Nov 2013
Posts: 65
I talked to the inverter store and they said the 24v is more efficient and their 12v inverter is very power hungry they suggested the 24v.

They also said that tapping into one of the batteries to start the generator and operate the tongue jack would have extremely minimal negative results on the battery bank and it wouldn't cause any harm at all to the battery.
They said if I was running anything for a length of time then use a separate battery but for a few seconds use a few times a day would be perfectly fine.

If I went this route I could connect the wires to a different battery every few weeks or so and hopefully keep each of them exactly the same as the others.
Jasper7821 is offline   Reply With Quote
Old 02-07-2014, 12:52 PM   #9
Senior Member
 
Old Bounder's Avatar
 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 1,636
Quote:
Originally Posted by Jasper7821 View Post
I talked to the inverter store and they said the 24v is more efficient and their 12v inverter is very power hungry they suggested the 24v.

They also said that tapping into one of the batteries to start the generator and operate the tongue jack would have extremely minimal negative results on the battery bank and it wouldn't cause any harm at all to the battery.
They said if I was running anything for a length of time then use a separate battery but for a few seconds use a few times a day would be perfectly fine.

If I went this route I could connect the wires to a different battery every few weeks or so and hopefully keep each of them exactly the same as the others.
It would probably involve repositioning the batteries within the bank, rather than simply attaching across a different battery, as you will need to maintain the same reference to ground between the generator, batteries and inverter.
__________________
'97 Bounder 34V, F53 7.5L-460
Old Bounder is offline   Reply With Quote
Old 02-07-2014, 12:55 PM   #10
Member
 
Join Date: Nov 2013
Posts: 65
Quote:
Originally Posted by loulong View Post
It would probably involve repositioning the batteries within the bank, rather than simply attaching across a different battery, as you will need to maintain the same reference to ground between the generator, batteries and inverter.
Thanks, I was thinking of just having a few feet of wire extra in the battery compartment and just unscrew the connectors and put the leads onto a different battery. But if the system 24v gets disconnected somehow by doing that then I wouldn't want to do it.
When you say maintain the same reference to ground, I don't know what that means.
Jasper7821 is offline   Reply With Quote
Old 02-07-2014, 12:58 PM   #11
Senior Member
 
Join Date: Apr 2010
Location: Western
Posts: 324
So why not go with a 48Vdc inverter and reduce the current even further?
You have 4 batteries put them all in series and you are good to go
48V is far more common than 24V
The vast majority of residential installations use 48V plus 100% of the telecom industry uses 48V

Me I would NOT ever tap off a battery that is in a series string
KJINTF is offline   Reply With Quote
Old 02-07-2014, 02:08 PM   #12
Senior Member
 
Old Bounder's Avatar
 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 1,636
Quote:
Originally Posted by Jasper7821 View Post
Thanks, I was thinking of just having a few feet of wire extra in the battery compartment and just unscrew the connectors and put the leads onto a different battery. But if the system 24v gets disconnected somehow by doing that then I wouldn't want to do it.
When you say maintain the same reference to ground, I don't know what that means.
I was just thinking that if the case of the inverter is grounded to a "common ground" and the generator starter and frame are attached to that "common ground", you need to attach to a battery, within your array, that has 12V on the positive anode with reference to that common ground. Attaching across a battery that is wired into the array with 12V on the negative and 24v on the positive, would cause a spark shower to say the least.

Folks will continue to come out of the woodwork advising against tapping off the necessary 12V from your 24V bank to occasionally start your generator. When they offer to use their money to purchase and install the additional battery, and necessary 12V converter/charger, take them up on the deal.
__________________
'97 Bounder 34V, F53 7.5L-460
Old Bounder is offline   Reply With Quote
Old 02-07-2014, 03:01 PM   #13
Senior Member
 
Join Date: Sep 2012
Posts: 4,232
Quote:
Originally Posted by KJINTF View Post
Me I would NOT ever tap off a battery that is in a series string
Why is that? Just curious, we're all trying to learn.
jesilvas is offline   Reply With Quote
Old 02-07-2014, 04:52 PM   #14
Member
 
Join Date: Nov 2013
Posts: 65
Quote:
Originally Posted by KJINTF View Post
So why not go with a 48Vdc inverter and reduce the current even further?
You have 4 batteries put them all in series and you are good to go
48V is far more common than 24V
The vast majority of residential installations use 48V plus 100% of the telecom industry uses 48V

Me I would NOT ever tap off a battery that is in a series string
The place that I'm buying the inverter doesn't have a 48v inverter. The best price I found for a 24v pure sine 4,000 watt is $1,300.
If I can find a 48v pure sine for that price I would like to look into it.
Jasper7821 is offline   Reply With Quote
Reply

Tags
battery



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 12:28 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.