Quote:
Originally Posted by vicm
Got it working. Had just filled propane tank. Air must have been in line.
|
No it wasn't air in line.........LP System is 0.39 psi
When propane is valved out the Main Reg goes into 'lockup'
When you start using propane it can take several attempts to establish flow....especially with fridge, water heater, furnace due to their 'flame proving' circuits
Next time after valving propane in...light off stove top burners on high to place demand on Main reg and establish flow
Still can take couple of tries on fridge....lowest demand appliance