In series keeps the current lower but increases the voltage. This is best for long runs of cablebetwen the solar panels and the SCC since it is high current that causes high voltage drop and associated power loss which is proportional to the square of the current.
In parallel keeps the voltage lower but increases the current.
So your SCC needs to be able to handle both the maximum current and the maximum voltage that it will receive from the solar panels...and the SCC also needs to be located very close to the battery too.
https://www.renogy.com/blog/solar-pa...s-vs-parallel/
And the entire system first needs to be properly designed before buying/selecting any of the RV appliances or your solar panel system elements. The first step is determining your daily AH depletion, which should be made as small as you can reasonably make it by careful/thoughtful selection of your RV appliances. This than determines the battery AH, solar panel power wattage and SCC requirements which should be designed to enable fully replenishing the daily AH depletion in 4 hours or less and preferably using a low cost and robust PWM SCC or if necessary, a more complicated, expensive, and failure prone but about 25% more efficient MPPT SCC. And of course, few people actually do this and you can read about their moronic approaches on RV forums such as this... So yeah, some math, research and soul searching is required...
Gayle & Bob