Old 05-18-2015, 06:53 PM   #1
Junior Member
 
Fleetwood Owners Club
Join Date: Mar 2015
Posts: 18
Question Surge Protector - Only for Shore Power, or on everything??

We're about to install our Progressive hardwired surge protector.
Are most people just using theirs for Shore Power (easy in-line install on that cable)? Or is it common to have it after a transfer switch (or inverter, etc) so that ANY source of 110 is protected? Not sure a generator or the inverter would have a surge, per se, but if there's no harm in it, I don't mind the extra planning.

Thanks!
travelingbard is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-18-2015, 06:59 PM   #2
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 23,295
I spend 98% of the time on shore power , so I just put it in the power cord.
If I regularly spent time on the generator running , I might have installed it after the transfer switch.
Doesn't the inverter have built in surge protection ?


EDIT; BTW , Welcome to iRV2.
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 05-18-2015, 07:15 PM   #3
Junior Member
 
Fleetwood Owners Club
Join Date: Mar 2015
Posts: 18
I think the better grade inverters do. Looking at a couple of higher end models, possibly having the transfer switch built in. A little worried about having everything in one box, though, as it would be easier to replace/service a single unit instead of having my entire AC trashed if the inverter went down. If the inverter I get does have "good" surge protection, I'll put this unit in front of it...
travelingbard is offline   Reply With Quote
Old 05-18-2015, 07:21 PM   #4
Senior Member
 
Winnebago Owners Club
Freightliner Owners Club
Join Date: Jul 2006
Location: Michigan
Posts: 840
I use a portable Progressive for shore only, so I'm biased... but I'd focus on protecting the shore power side:

If you think of the "surge protection" feature, most likely it will be from the shore line. Not impossible to have a malfunctioning generator, but unlikely. One of the big things a Progressive or similar unit does is check for miswired shore hookups, bad grounds etc. Again not going to have this gen side normally.

However, anything before the Progressive isn't protected. So if you put it after the transfer switch, then it fries before the Progressive sees a problem with the shore power, and maybe a big enough surge takes out more (gen?)

In any case I come down on the side of ensuring the shore power is clean by installing the Progressive on the shore line before it gets to anything else, but JMHO. I know the doc gives you instructions for installing either way (before or after the ATS) so obviously both are 'approved.'

(If you google "progressive surge before after ats" you'll get a lot of hits and discussions both ways, in many forums.)
__________________
Ed & Joie
2004 Vectra 40KD
Freightliner Chassis and Cummins ISC
emiddleb is offline   Reply With Quote
Old 05-18-2015, 10:11 PM   #5
Senior Member
 
dons2346's Avatar
 
Country Coach Owners Club
Join Date: Dec 2010
Posts: 6,372
You can wire it either way.

My coach has the surge protector wired after the transfer switch. This way it protects the coach from crappy power from the shore as well as from the generator
__________________
Don
2002 Country Coach Intrigue
dons2346 is online now   Reply With Quote
Old 05-19-2015, 11:36 AM   #6
Senior Member
 
ShapeShifter's Avatar
 
Monaco Owners Club
Holiday Rambler Owners Club
Join Date: Feb 2010
Location: Buffalo, NY
Posts: 1,632
It seems most people put it before the transfer switch. That's what Progressive recommends. They say it's to protect the transfer switch, and it's not necessary to put it after, because the generator is a cleaner source of power with its own protection.

But I don't buy that logic. A transfer switch is basically a set of relay contacts. There's nothing there that is easily damaged by the kinds of things the EMS protects against: high/low voltage, surges, or wiring problems. The odds of the incoming shore power damaging the transfer switch are VERY low, and if the worst should happen, a transfer switch is one or two hundred dollars, tops.

On the other hand, generators can fail, and when they do they can cause all sorts of nasty problems, including very high voltages if the voltage regulator fails. If that happens, the potential cost to equipment in the coach could be in the thousands.

While I've heard of transfer switch failures caused by loose connections or switching while under heavy load, I've not heard of a single transfer switch failure that was caused by bad shore power. However, I've heard several stories of massive coach equipment damage caused by a failed generator.

So, would you rather risk an inexpensive piece of equipment that is robust and not prone to failure, or would you rather risk many expensive pieces of equipment that are more likely to be damaged? In my mind, the decision is easy: don't worry about the transfer switch, but protect everything else from shore power AND the generator -- I put the EMS after the transfer switch.
__________________
Adam and Sue, and a pack of little furballs
2007 Holiday Rambler Endeavor 40PDQ Limited Edition - Cummins ISL 400
2013 Ford F-150 FX4 toad - USGear Unified Tow Brake, Roadmaster Blackhawk II Tow bar, Blue Ox baseplate
Home base near Buffalo NY, often on the road to a dog show
ShapeShifter is offline   Reply With Quote
Old 05-19-2015, 12:27 PM   #7
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 46,709
As you can see, you'll get opinions both ways. I put mine in the shore power line before the transfer switch.
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is online now   Reply With Quote
Old 05-19-2015, 01:36 PM   #8
Senior Member
 
Sky_Boss's Avatar
 
Newmar Owners Club
Freightliner Owners Club
Spartan Chassis
Join Date: Apr 2012
Location: ON THE ROAD...SOMEWHERE
Posts: 6,958
My first coach SP was after the ATS. My current SP is before the ATS. I wish the current coach was AFTER the ATS.

I've heard both ways on the "protect the ATS" side and the "the generator is well regulated" and found both seem plausible but I would rather ensure power from both sources are regulated.

Also, with the PI remote control I can see L1 & L2 information while on both shore power and generator. With the SP before the ATS you only get L1 & L2 info on shore power.
__________________
Don, Sandee & GSD Zeus. Guardian GSDs Gunny (7/11/15) & Thor (5/5/15)
2006 2015 DSDP 4320 4369, FL Chassis, 2013 CR-V 2020 Jeep Overland, Blue Ox Avail, SMI AF1.
[SIGPIC][/SIGPIC]
Sky_Boss is offline   Reply With Quote
Old 05-19-2015, 01:46 PM   #9
Senior Member
 
ShapeShifter's Avatar
 
Monaco Owners Club
Holiday Rambler Owners Club
Join Date: Feb 2010
Location: Buffalo, NY
Posts: 1,632
Quote:
Originally Posted by emiddleb View Post
However, anything before the Progressive isn't protected. So if you put it after the transfer switch, then it fries before the Progressive sees a problem with the shore power, and maybe a big enough surge takes out more (gen?)
I just don't see this happening. For the power to arc over the transfer switch contacts and back-feed into the generator, it would take a massive surge, like a direct or nearby lightning strike. If that were to happen, that same surge is going to go into the coach and cause all sorts of damage inside the coach as well: when that happens, the transfer switch and the generator are going to be the least of your concerns.

And don't think that the EMS being before the transfer switch is going to protect you from a direct or nearby lightning strike, it can't. The Progressive EMS is a very capable unit and can absorb a few thousand Joules of energy during a surge. That's an impressive amount. However, a lightning strike has millions to billions of Joules of energy, and nothing in your rig stands a chance against that, including the Progressive EMS.
__________________
Adam and Sue, and a pack of little furballs
2007 Holiday Rambler Endeavor 40PDQ Limited Edition - Cummins ISL 400
2013 Ford F-150 FX4 toad - USGear Unified Tow Brake, Roadmaster Blackhawk II Tow bar, Blue Ox baseplate
Home base near Buffalo NY, often on the road to a dog show
ShapeShifter is offline   Reply With Quote
Old 05-19-2015, 02:21 PM   #10
Senior Member
 
flaggship1's Avatar


 
Fleetwood Owners Club
iRV2 No Limits Club
Join Date: Sep 2012
Location: Rainbow Riding
Posts: 18,574
Quote:
Originally Posted by ShapeShifter View Post
It seems most people put it before the transfer switch. That's what Progressive recommends. They say it's to protect the transfer switch, and it's not necessary to put it after, because the generator is a cleaner source of power with its own protection.

But I don't buy that logic. A transfer switch is basically a set of relay contacts. There's nothing there that is easily damaged by the kinds of things the EMS protects against: high/low voltage, surges, or wiring problems. The odds of the incoming shore power damaging the transfer switch are VERY low, and if the worst should happen, a transfer switch is one or two hundred dollars, tops.

On the other hand, generators can fail, and when they do they can cause all sorts of nasty problems, including very high voltages if the voltage regulator fails. If that happens, the potential cost to equipment in the coach could be in the thousands.

While I've heard of transfer switch failures caused by loose connections or switching while under heavy load, I've not heard of a single transfer switch failure that was caused by bad shore power. However, I've heard several stories of massive coach equipment damage caused by a failed generator.

So, would you rather risk an inexpensive piece of equipment that is robust and not prone to failure, or would you rather risk many expensive pieces of equipment that are more likely to be damaged? In my mind, the decision is easy: don't worry about the transfer switch, but protect everything else from shore power AND the generator -- I put the EMS after the transfer switch.
Transfer swith on our coach went when a park transformer blew. I had a Power Master VC 50 voltage controller inline, followed by the PI PT50 C. 120 contacts fried. Voltage controller and Surge protector were fine. Have no idea how that occurred but it did.

New transfer switch was a little more that one or two hundred dollars.

http://www.dyersonline.com/trc-40250...FQcQaQodTFsApg

Still have the same set up and the 40250 that does all the PI SP does.

Note. Also required an upgraded display and pigtail. About $800.
Attached Thumbnails
Click image for larger version

Name:	1432066887588.jpg
Views:	79
Size:	55.4 KB
ID:	94682  
__________________
Steve & Annie (RVM2)
2008 Fleetwood Bounder 38F ~ 325 ISB Turbo ~ Freightliner XC 2014 CR-V ~ Invisibrake / Sterling All Terrain
Sioux Falls, SD (FullTime Since Nov 5th 2014)
flaggship1 is offline   Reply With Quote
Old 05-19-2015, 03:29 PM   #11
Senior Member
 
ShapeShifter's Avatar
 
Monaco Owners Club
Holiday Rambler Owners Club
Join Date: Feb 2010
Location: Buffalo, NY
Posts: 1,632
Quote:
Originally Posted by flaggship1 View Post
Transfer swith on our coach went when a park transformer blew. I had a Power Master VC 50 voltage controller inline, followed by the PI PT50 C. 120 contacts fried. Voltage controller and Surge protector were fine. Have no idea how that occurred but it did.
Fried contacts on a transfer switch are usually due to arcing caused when switching power sources while under load. Are your sure the contacts weren't already burned before the park transformer blew, perhaps pushing the compromised transfer switch over the edge? It's mighty curious that the more sensitive components before the transfer switch were fine while the more robust contacts were burned.

But even if the failure is directly attributable to the blown transformer, that's one ATS failure. I've read about many more generator failures taking out lots of equipment in a coach.

Quote:
New transfer switch was a little more that one or two hundred dollars.
That's not a typical transfer switch. That's a TRC SurgeGuard (roughly equivalent to a PI EMS) built into a transfer switch. Most of that cost is for the EMS protection.

Of course, if you look hard enough, you can find an exception to just about any statement. It's more telling to back up a level, and look at the other transfer switches they offer: they range from $38 to $200 (not counting the 100 A transfer switches, or those with built in EMS or surge protection.)

This just doesn't make sense. If that's the transfer switch you had, why did you waste money on the redundant PI PT50 C? Or, look at it the other way around, if you had the PI PT50 C, why not put in a more reasonably priced transfer switch? And if you already had that transfer switch (with built in surge protection) AND the PI PT50C, and it STILL blew up from the transformer failure, that seems to indicate it was a rather drastic event that took out your transfer switch contacts.
__________________
Adam and Sue, and a pack of little furballs
2007 Holiday Rambler Endeavor 40PDQ Limited Edition - Cummins ISL 400
2013 Ford F-150 FX4 toad - USGear Unified Tow Brake, Roadmaster Blackhawk II Tow bar, Blue Ox baseplate
Home base near Buffalo NY, often on the road to a dog show
ShapeShifter is offline   Reply With Quote
Old 05-19-2015, 08:17 PM   #12
Senior Member
 
flaggship1's Avatar


 
Fleetwood Owners Club
iRV2 No Limits Club
Join Date: Sep 2012
Location: Rainbow Riding
Posts: 18,574
Quote:
Originally Posted by ShapeShifter View Post
Fried contacts on a transfer switch are usually due to arcing caused when switching power sources while under load. Are your sure the contacts weren't already burned before the park transformer blew, perhaps pushing the compromised transfer switch over the edge? It's mighty curious that the more sensitive components before the transfer switch were fine while the more robust contacts were burned.

But even if the failure is directly attributable to the blown transformer, that's one ATS failure. I've read about many more generator failures taking out lots of equipment in a coach.


That's not a typical transfer switch. That's a TRC SurgeGuard (roughly equivalent to a PI EMS) built into a transfer switch. Most of that cost is for the EMS protection.

Of course, if you look hard enough, you can find an exception to just about any statement. It's more telling to back up a level, and look at the other transfer switches they offer: they range from $38 to $200 (not counting the 100 A transfer switches, or those with built in EMS or surge protection.)

This just doesn't make sense. If that's the transfer switch you had, why did you waste money on the redundant PI PT50 C? Or, look at it the other way around, if you had the PI PT50 C, why not put in a more reasonably priced transfer switch? And if you already had that transfer switch (with built in surge protection) AND the PI PT50C, and it STILL blew up from the transformer failure, that seems to indicate it was a rather drastic event that took out your transfer switch contacts.
The transfer switch I had was the 2008 factory $200 TRC switch that is now redundant - discontinued - no longer available. I could have bought any switch I wanted. I chose the new upgraded model. Which was also the one Fleetwood said was the replacement model. Of course any number of them could have worked.

The quick fix on the old switch was to move the lines from 120 pedestal switch side to the generator side while I waited for the new one to come in. Worked fine for several days like that.

I can't tell you what state the switch was in other than fried and can't say why other than the blown transformer. We had been full time in the coach for about a month when it went out. 12:30 am. - Boom wakes us up. Fridge starts beeping. Go outside and park host is out telling everyone the transformer blew.

But the new display and the new switch were worth the money to me. Since my power line was modified - cut and plugs added so the VC5O and PI could be mounted in electric bay, I left it that way.

The new display actually does something - and so does the switch. And it's now six months full time and working fine.

BTW - our transfer swith is under the bed. I could have moved things around but am not a big generator user per se. It gets used on the road sometimes. And exercised with load when sitting.
Attached Thumbnails
Click image for larger version

Name:	1432087144661.jpg
Views:	49
Size:	31.9 KB
ID:	94707  
__________________
Steve & Annie (RVM2)
2008 Fleetwood Bounder 38F ~ 325 ISB Turbo ~ Freightliner XC 2014 CR-V ~ Invisibrake / Sterling All Terrain
Sioux Falls, SD (FullTime Since Nov 5th 2014)
flaggship1 is offline   Reply With Quote
Old 05-19-2015, 08:55 PM   #13
Senior Member
 
Join Date: Feb 2010
Posts: 4,603
You can get industral grade surge protection that installs into the ac load center.

They are about 3 inches cubed and can pull a 30 to 50 amp breaker.

Larger ones more.

Having one connected yo the ac load center mains can trip the breakers of any source if it gets that far.
Attached Thumbnails
Click image for larger version

Name:	ForumRunner_20150519_195531.png
Views:	48
Size:	487.3 KB
ID:	94712  
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 05-19-2015, 09:04 PM   #14
Senior Member
 
flaggship1's Avatar


 
Fleetwood Owners Club
iRV2 No Limits Club
Join Date: Sep 2012
Location: Rainbow Riding
Posts: 18,574
Quote:
Originally Posted by TQ60 View Post
You can get industral grade surge protection that installs into the ac load center.

They are about 3 inches cubed and can pull a 30 to 50 amp breaker.

Larger ones more.

Having one connected yo the ac load center mains can trip the breakers of any source if it gets that far.
Now there's something to look into.
__________________
Steve & Annie (RVM2)
2008 Fleetwood Bounder 38F ~ 325 ISB Turbo ~ Freightliner XC 2014 CR-V ~ Invisibrake / Sterling All Terrain
Sioux Falls, SD (FullTime Since Nov 5th 2014)
flaggship1 is offline   Reply With Quote
Reply

Tags
power, shore power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
No power to chassis dgrover Ford Motorhome Chassis Forum 3 04-20-2015 04:31 PM
Partial power loss on Power Distribution panel MikeandBecky Class A Motorhome Discussions 16 02-17-2015 06:01 PM
My Progressive Surge Protector/Hughes Autoformer Installation jigsup Newmar Owner's Forum 17 09-27-2014 08:44 PM
Power Issue Turbofans Newmar Owner's Forum 3 08-29-2014 02:32 PM


All times are GMT -6. The time now is 12:33 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.