Why can't 15A + 15A = 30A?

How come there isn't a converter that I could plug two 15A power cords into and get 30A capability out the other side? Seems like with computerization these days, some one would sell a box that I could make 30A for my motorhome at home from two 15A extension cords coming from two different outlets.

Just wondering, I know there is a reason.

F4Gary is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-09-2016, 12:50 PM   #2
Senior Member
 
Lifemember's Avatar
 
Damon Owners Club
Vintage RV Owners Club
Oklahoma Boomers Club
Join Date: Jul 2011
Location: Bartlesville Oklahoma
Posts: 1,300
As long as you divide your 30 amp load into two 15 amp circuits
__________________
1996 Damon DayBreak 454 P37 Chassis
Lifemember is offline   Reply With Quote
Old 02-09-2016, 12:54 PM   #3
Senior Member
 
Winnebago Owners Club
Freightliner Owners Club
Join Date: Feb 2015
Location: BC
Posts: 149
with a meter check the two hot wires from the two outlets. If you have 220v you could combine them into a 220v 30 amp service similar to a 50amp. Not sure if its worth it.
__________________
1999 Winnebago Chieftain
1992 Jeep YJ
1984 Harley Liberty edition
jporietis is offline   Reply With Quote
Old 02-09-2016, 01:11 PM   #4
Senior Member
 
Join Date: Jul 2014
Posts: 24,656
You would need to find 2, 15 amp circuits on different breakers, but on the same leg of your home panel.

If you find two different legs, I would think a shower of sparks would be coming out of the adaptor. At least until one of the breaker poped. You are creating a 240 volt short.

Do it wrong and 240 volts goes to your 30 amp 120 volt MH. That's bad !!!
twinboat is offline   Reply With Quote
Old 02-09-2016, 01:13 PM   #5
Senior Member
 
Join Date: Jul 2014
Posts: 24,656
Quote:
Originally Posted by jporietis View Post
with a meter check the two hot wires from the two outlets. If you have 220v you could combine them into a 220v 30 amp service similar to a 50amp. Not sure if its worth it.
If the OP has 30 amp service it is 120 volt only.

Not the same as 50 amp 120/240 volt service.
twinboat is offline   Reply With Quote
Old 02-09-2016, 01:24 PM   #6
Member
 
Mid Atlantic Campers
Forest River Owners Club
Join Date: Oct 2013
Posts: 84
Quote:
Originally Posted by F4Gary View Post
How come there isn't a converter that I could plug two 15A power cords into and get 30A capability out the other side? Seems like with computerization these days, some one would sell a box that I could make 30A for my motorhome at home from two 15A extension cords coming from two different outlets.

Just wondering, I know there is a reason.

how about thinking of it this way;
2 water hoses, each has 15 psi of pressure.
run both hoses to a bucket, it fills up fast.
now connect the 2 hoses to a y adapter, you still only have 15psi of pressure. you gain nothing.
__________________
2015 FR grey wolf 27RR
2015 chevy 3500HD
kcmusa is offline   Reply With Quote
Old 02-09-2016, 01:28 PM   #7
Registered User
 
Join Date: Feb 2015
Location: Grapevine, Tx
Posts: 2,958
Quote:
Originally Posted by kcmusa View Post
how about thinking of it this way;
2 water hoses, each has 15 psi of pressure.
run both hoses to a bucket, it fills up fast.
now connect the 2 hoses to a y adapter, you still only have 15psi of pressure. you gain nothing.
Now that makes sense.
F4Gary is offline   Reply With Quote
Old 02-09-2016, 01:40 PM   #8
Senior Member
 
Join Date: Jul 2014
Posts: 24,656
Quote:
Originally Posted by kcmusa View Post
how about thinking of it this way;
2 water hoses, each has 15 psi of pressure.
run both hoses to a bucket, it fills up fast.
now connect the 2 hoses to a y adapter, you still only have 15psi of pressure. you gain nothing.
Not completely true. If the Y is near the bucket, you still get 15 psi pressure but the gallons per minute will go up, just like the Amps would in 2 cords.

PSI is like volts.
GPM is like Amps.

Firefighters use parallel fire hoses to get more GPM from the same pressure hydrant. There is some loss in the Y but not near half.
twinboat is offline   Reply With Quote
Old 02-09-2016, 02:01 PM   #9
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,926
Alternating Current, AC, travels in sine waves. If the two outlets are from the same leg of the power panel, they would be in sync. If opposite legs of the panel, you would create a dead short. The 15 amp wiring is not sized to carry 30 amps, its illegal to wire it as proposed. I wouldn't do it.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 02-09-2016, 02:02 PM   #10
Member
 
Mid Atlantic Campers
Forest River Owners Club
Join Date: Oct 2013
Posts: 84
Quote:
Originally Posted by twinboat View Post
Not completely true. If the Y is near the bucket, you still get 15 psi pressure but the gallons per minute will go up, just like the Amps would in 2 cords.

PSI is like volts.
GPM is like Amps.

Firefighters use parallel fire hoses to get more GPM from the same pressure hydrant. There is some loss in the Y but not near half.
Firefighters run the hose to a pumper truck that increases the pressure.
__________________
2015 FR grey wolf 27RR
2015 chevy 3500HD
kcmusa is offline   Reply With Quote
Old 02-09-2016, 02:12 PM   #11
Senior Member
 
Old Bounder's Avatar
 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 1,636
Quote:
Originally Posted by twinboat View Post
Not completely true. If the Y is near the bucket, you still get 15 psi pressure but the gallons per minute will go up, just like the Amps would in 2 cords.
There is some loss in the Y but not near half.
This is not a true analogy of what would happen with a "Y", unless the output orifice of the "Y" was twice the size of either input.
__________________
'97 Bounder 34V, F53 7.5L-460
Old Bounder is offline   Reply With Quote
Old 02-09-2016, 02:23 PM   #12
Senior Member
 
docj's Avatar
 
Join Date: May 2011
Posts: 6,946
I guess no one posting on this thread has ever seen a cheater cord before? I have a cheater into which I can plug my 50A cord and then plug the cheater into two 30A receptacles. If the two 30A outlets are separate circuit breakers and are on the same leg of the circuit the net result is to provide ~60A of power capability (that has to be compared to the 100A that is provided by a so-called 50A RV power connection).

There's nothing particularly unusual about being able to do this. Electrically, it's no different than connecting a couple of batteries in parallel. The current is split and half goes into each leg.

Similarly, instead of plugging the two outputs of the cheater into 30A outlets you could use a 30A/15A adapter and plug them into two 15A outlets which would provide you a true 30A of power. Unfortunately, such cheaters won't work with outlets that are protected by GFCI devices and the 115V outlets on all modern RV pedestals have GFCIs. So I don't get much use out of the cheater these days, but it does come in handy every once in a while.

Here's a link to a cheater for sale: http://www.amazon.com/Cordtec-Power-.../dp/B00760FG2E
__________________
Joel Weiss--Campground Reviews administrator
RV Technology Specialist
2000 40' Beaver Patriot Thunder Princeton CAT C-12
docj is offline   Reply With Quote
Old 02-09-2016, 02:45 PM   #13
Senior Member
 
jfran304's Avatar
 
Tiffin Owners Club
Workhorse Chassis Owner
Join Date: Oct 2009
Location: Warner Robins, GA
Posts: 2,613
Quote:
Originally Posted by F4Gary View Post
How come there isn't a converter that I could plug two 15A power cords into and get 30A capability out the other side? Seems like with computerization these days, some one would sell a box that I could make 30A for my motorhome at home from two 15A extension cords coming from two different outlets.

Just wondering, I know there is a reason.

Try one of these. You will have to insure that the electrical outlets that you plug into are on different circuit breakers and you will need 2 of the adaptors from 30 amp to 110. If your coach is 30 amp you will also need an adaptor from 50 amp to 30 amp.

50 Amp 125/250V RV Female - (2) 30 Amp RV Male Plugs Y-Adapter with Powersmart LED's - Furrion F5431RY-SB - Electrical Adapters - Camping World

http://tweetys.com/rv-50-amp-cheater...FQyHaQodWn8HHg

Jon
__________________
Jon & Sue Francis (Retired U.S.A.F.)
Lil Girl-Rescued, Abby Rescued, Peaches Rescued
06 Allegro 35TSA Workhorse Chassis
2013 Chevy Spark Dinghy
jfran304 is offline   Reply With Quote
Old 02-09-2016, 02:50 PM   #14
Senior Member
 
photopilot's Avatar
 
Monaco Owners Club
Join Date: Jan 2016
Location: New Hampshire
Posts: 419
OK, here goes.

I'm not an electrician, but I did play one on a former job, so please correct me if I'm wrong.

50 amp service for an RV is based on the current carrying capacity of each conductor. Each conductor should be rated to carry 50 amps current. I don't have the chart in front of me, but I believe it is 6 gauge. A 50 amp RV plug has 4 wires- two hot, a neutral and a ground. The hot wires carry 120 volts each, 180 degrees out of phase such that if you put a meter across both, you would get 240 volts. However, everything in the RV runs on 120 volts, so they keep the two 120V wires separate, and run each to the neutral.

When you connect a 120V 15/20 or 30 amp adapter to a 50 amp plug, they actually connect the one hot lead to the two hot leads in the RV, so the electrical power is shared between the two legs in the RV. The 50 amp supply provides a LOT more power. 50 amp x 120V x 2 legs = 12,000 watts. Using a 30 amp service, you get 30 amp x 120V = 3,600 watts. (Only one hot lead in a 3-wire 30 A plug). Even less with 15 amps- 1800 watts.

Now, if I understand the OP's question, I suppose you could wire a custom junction box to two different 15 or 20 amp circuits and use a 50 amp receptacle and feed the two hot wires into the RV, giving you twice the power. Not something I would try, but theoretically it might work. It would not work with a 30 amp plug as there is only one hot lead.

I'm not sure how the load manager distributes the power once inside the RV, so I don't know how it would handle the reduced power on each leg. It would be smart to see what devices are on each leg.

If I'm all wet, let me know!

Photopilot
__________________
Walt & Bonnie
2006 Monaco Camelot 40PAQ, Cummins 400 ISL
'16 Ford C-Max, Roadmaster BP, Sterling towbar
photopilot is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30A 220v instead of 50A 220v cb1000rider iRV2.com General Discussion 87 04-07-2016 07:47 AM
Plugging into 15a at home HavingABlast Newmar Owner's Forum 40 01-02-2016 03:28 PM
30A campground service RBowman Travel Supreme Owner's Forum 12 06-18-2014 09:51 PM
30A to 50A Adapter Causes MH Fire Pusherman Class A Motorhome Discussions 173 09-02-2013 05:33 PM
Genset 20a and 30a breakers '04 Southwind Agility57 RV Systems & Appliances 48 07-25-2013 08:27 AM


All times are GMT -6. The time now is 12:16 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2020, vBulletin Solutions, Inc.