Will Temporary Hi Amp Loads Damage Batteries?

We are getting ready to head south soon and have been putting our new solar/battery/inverter setup through its paces. We have 740 amp/hrs of Trojan L16 AGM batteries and a 2800 watt Magnum Inverter. Wire runs between Batteries and Inverter are short, less than 3 feet and we have a small 4 cup 600 watt coffee pot. Noticed that during the brew process of about 5 minutes the voltage dropped to 12.25 and then immediately bounced back up to 12.87 as soon as the brewing stopped. Voltage was below 12.3 for about three minutes. State of charge stayed around 99%. This is the highest draw item we have (normally boil water for our drip when boondocking). Will this kind of temporary high load damage our batteries?
__________________
Tom, Tish and Ripley (the American Bulldog)
wingtip is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-05-2018, 01:21 PM   #2
Senior Member
 
Join Date: Jan 2008
Location: Los Angeles, CA
Posts: 242
Not at all.
__________________
2017 Coachmen 233RBS
2018 Ford F-150 Super Crew 3.5ECO 3.55
babock is offline   Reply With Quote
Old 12-05-2018, 01:26 PM   #3
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
Did you try looking up the specifications for your batteries?

For 600 watts you would draw ~5 Amps at 120 VAC. That roughly translates to 50 Amps @ 12VDC with efficiency losses. Divide that by the number of 12 V battery strings and see what Trojan says about current draw.
nothermark is offline   Reply With Quote
Old 12-05-2018, 01:35 PM   #4
Senior Member
 
RoadDogYVR's Avatar
 
Outdoors RV Owners Club
Join Date: Nov 2018
Location: Aldergrove, British Columbia Canada
Posts: 205
Trojan's website gives a 75 amp draw capacity minute figure of 215 minutes for that battery so a 50 amp draw is safe.
__________________
TT: 2018 Outdoors RV Blackrock 20RD "Rolly House"
TV: 2016 Ford F150 XLT FX4 2.7EB EAT6
Aldergrove, British Columbia
RoadDogYVR is offline   Reply With Quote
Old 12-05-2018, 06:14 PM   #5
Senior Member
 
Join Date: Nov 2015
Posts: 773
We regularly use our inverter to power the microwave. According to my meter, it draws between 150-175 DC amps for up to 5 minutes. Batteries are still going strong after 3 years of use.
__________________
2012 Dodge C3500 DRW 4x4 Long Box, WeatherGuard 90 Gal transfer tank, B&W Companion Hitch
2012 Keystone Montana 3100RL, 520W Solar, 460AH batteries, Morningstar MPPT 45 CC, Bogart 2030RV monitor.
drdarrin is offline   Reply With Quote
Old 12-05-2018, 08:13 PM   #6
Senior Member
 
Join Date: Jul 2014
Posts: 35,441
Your not hurting the batteries with that draw.

If your reading the volts at the inverter, I'm wondering what size cables you have between the inverter and batteries.

Take a reading right at the batteries to see how much voltage drop your getting thru the cables.
twinboat is offline   Reply With Quote
Old 12-05-2018, 08:24 PM   #7
Senior Member
 
rarebear.nm's Avatar
 
Excel Owners Club
Winnebago Owners Club
Ford Super Duty Owner
Join Date: Aug 2014
Location: Santa Fe, NM
Posts: 6,814
As others have said- no that draw is safe. It is normal to see a voltage drop that bounces back.

Do you have a battery monitor, like a Trimetric 2030 by Bogart? That will read voltage at the batteries if installed correctly.
__________________
Fred & Denise (RVM157) New Mexico
2007 Excel Classic 30RSO & Coach House 272XL E450
2007 RAM 3500, Diesel, 6Spd Auto, SWD, 4x4, CC & LB
[SIGPIC][/SIGPIC]
rarebear.nm is offline   Reply With Quote
Old 12-05-2018, 11:14 PM   #8
Junior Member
 
Join Date: Dec 2014
Location: British Columbia
Posts: 24
Thank you everyone for your input.

We have a Victron battery monitor. I've forgotten the actual cable size (1/0?) but it's big, maybe the diameter of my thumb. We know not to draw our batteries down below 50% and normally keep the limit much higher than that.

What spooked us was the low voltage alarm (on the Victron). We had it set at 12.3 volts and it activated part way through the brewing experiment at about the 2 minute mark, although the little coffee pot didn't skip a beat. All this got us thinking about high amp draws and the effect on our batteries.

We didn't set our system up to brew coffee or to cook in the microwave specifically but to provide us with sufficient power to live (frugally) and run essential systems while boondocking. We have a whole-house setup and other than the coffee pot and micro I can't think of anything else that would draw this much (A/C is wired for gen or shore only) just want to make sure we don't subject our investment to abuse.
__________________
Tom, Tish and Ripley (the American Bulldog)
wingtip is offline   Reply With Quote
Old 12-05-2018, 11:23 PM   #9
Senior Member
 
bluepill's Avatar
 
Join Date: Jan 2011
Location: Pensacola, FL
Posts: 2,457
FWIW, I set my low voltage alarm for 11.8 volts. That means it will trip under a 50 amp DC load when the batteries are actually at about 12.3 volts under no load. That's about 60% state of charge. Eliminates false alarms.
__________________
2008 Itasca 37H
2011 & 2012 Len & Pat's "One lap of America"
27K miles & 41 states in 13 months
Yellowstone Lake 6-1-2012
bluepill is offline   Reply With Quote
Old 12-05-2018, 11:34 PM   #10
Senior Member
 
Loren Rice's Avatar
 
Join Date: Nov 2012
Location: Ridgefield, Wa.
Posts: 274
battery draw

I believe occasional hard draws are actually good for a lead acid battery. Your coffee pot time and rate is fine and occasional micro wave use, maybe limited to a few minutes. Don't think id do a 2hr run (no turkey baking) What's bad is to draw a battery bank down to 10.5 which is considered dead. Don't want to do that. Drawing a battery bank down to no lower than 80% is a good way to keep your batteries around for a long time.
Next thing is to have a good three stage charger. a charger that when your batteries are charged will go into a maintenance level of 13v. at that voltage you don't boil the water out but still maintain the charge perfectly. These often now days are in better inverters/ chargers. But sometimes in older less expensive rigs you'll find a converter/charger that are pretty brutal on batteries. I've heard people exclaim my batteries were good when I got here two months ago and now their dead. That's because their charge portion of the inverter maintained the batteries at too high a voltage. Again when on standby 13v. is the sweet spot.

Hope this helps, There's a lot more to be said but I tried to hit the hi spots .
__________________
94 Monaco Sig m11 elect fuel inj
95 Jeep toad
Loren Rice is offline   Reply With Quote
Old 12-05-2018, 11:50 PM   #11
Senior Member
 
rarebear.nm's Avatar
 
Excel Owners Club
Winnebago Owners Club
Ford Super Duty Owner
Join Date: Aug 2014
Location: Santa Fe, NM
Posts: 6,814
Our low voltage alarm is set for 12.0 volts. I wired a bypass switch in so if the alarm has disengaged the power I can bypass it for some vital function, but knowing what I'm doing at the same time.

Our solar system has provided 100% of the 12 volt recharge for almost a year now. The breaker switch to the converters has been off all that time. Even under heavy furnace use I don't see battery charge dropping under about 92% in the morning. We have 460AHs of battery capacity.
__________________
Fred & Denise (RVM157) New Mexico
2007 Excel Classic 30RSO & Coach House 272XL E450
2007 RAM 3500, Diesel, 6Spd Auto, SWD, 4x4, CC & LB
[SIGPIC][/SIGPIC]
rarebear.nm is offline   Reply With Quote
Old 12-06-2018, 06:58 AM   #12
Community Moderator
 
Spdracr39's Avatar


 
Monaco Owners Club
Join Date: Jul 2016
Location: Central, Arkansas
Posts: 11,291
If you are concerned get a battery temp sensor. Its the heat that damages them not the current draw. ( disclaimer this does not include extreme circumstances or running the voltages down under 12 v when not under load).
__________________
2004 Beaver Monterey Laguna IV
Cummins ISC 350HP Allison 3000 6 speed
2020 Chevy Equinox Premier 2.0t 9 speed AWD
Spdracr39 is online now   Reply With Quote
Old 12-06-2018, 07:57 AM   #13
Senior Member
 
Join Date: Jul 2014
Posts: 35,441
The 20 hour discharge rate is 5 amps per 100 AH capacity.

With 740 AH that's a bit over 35 amps. Do that for 10 hours straight and you will use 50% of your capacity.

At the 10 hour rate, you can draw 74 amps for a bit less then 5 hours, before you've used 50 % of the AH in the battery bank.

If you look at the Trojan Specs, you will see a 5 and 1 hour discharge rate. The fact that they list them, strongly suggest that you can discharge them at that rate.

Even the RC lists 75 amps as a discharge rate for RC minutes.
twinboat is offline   Reply With Quote
Old 12-07-2018, 10:24 AM   #14
Junior Member
 
Join Date: Dec 2014
Location: British Columbia
Posts: 24
Both our Magnum inverter/charger and Morningstar solar controller are fully programmable for our AGM batteries and are temperature compensated so we're getting a pretty good picture of what's going on.

It's cold here (-6ºC) and we accidently overloaded our system yesterday morning (three aux heaters, furnace, coffee pot and microwave ... oops).
Circuit protection on the Magnum shut it down while the batteries gave us time to turn stuff off. Voltage dipped to 11.9 briefly and came right back up while SOC stayed above 95%. Had to reset the Magnum and clear an error on the Morningstar but otherwise all was good.

Still trying to get a working handle on battery temp as it relates to charging voltage. I'm guessing the sensors will make adjustments to charge voltage automatically ... I'm back into the books on that subject this morning.

We're also adjusting alarm settings on the Victron and we'll see how that goes towards reducing false alarms.

Slowly getting educated on this new system and we're pretty happy with it so far! Looking forward to Quartzsite in January and seeing how it performs in a warmer climate. Appreciate all the tips and advice!
__________________
Tom, Tish and Ripley (the American Bulldog)
wingtip is offline   Reply With Quote
Reply

Tags
batteries



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Temporary Internet & Wifi in S&B B52Rnav Technology: Internet, TV, Satellite, Cell Phones, etc. 0 11-03-2018 12:10 PM
Parasitic/unknown loads on house batteries? smlranger Country Coach Owners Forum 31 11-24-2015 08:26 AM
L1 & L2 loads on 50 amp NRF RV Systems & Appliances 7 01-06-2015 06:28 PM
Parasitic Loads on House Batteries CaptPat Monaco Owner's Forum 3 07-11-2010 10:41 AM
Disconnecting batteries for temporary storage TheJazzMan Newmar Owner's Forum 2 05-26-2009 05:19 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 12:33 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.