Xantrex 1800 inverter shutdown

My Xantrex 1800 inverter will shutdown after a variable period of time (hours or minutes). It feeds the residential refrigerator, microwave, TV's and a kithchen outlet. I have checked the battery wiring to the inverter, chassis ground, batteries (new Trojan 105's) and A/C wiring to the circuit breaker panel. I monitor the batteries with a BMI and when the shutdown occurs the voltage is 13.6 or higher. The amperage is around 7. There are no alarms from the remote panel and its display goes blank except for the backlight.

Looking for some feedback from someone who has experienced the same. The inverter has been replaced and both units do the same shutdown.
__________________
2017 Thor Challenger 37YT
Glenn2 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-30-2018, 01:44 PM   #2
Senior Member
 
Monaco Owners Club
Join Date: Sep 2014
Posts: 4,543
So new batteries, and two different inverters shut down intermittently?

Have you monitored the voltage right at the batteries? Is there a remote panel that you could try disconnecting just to try and isolate?
__________________
1996 Tioga Class C
2007 Monaco Diplomat 40 PDQ
TOAD 2012 Cadillac SRX 4
okcnewbie is offline   Reply With Quote
Old 10-30-2018, 01:57 PM   #3
Senior Member
 
Join Date: Jul 2014
Posts: 32,187
Do you have 4 gauge, or larger, cables going to it from the battery, both + and - ?
twinboat is offline   Reply With Quote
Old 10-30-2018, 02:29 PM   #4
Senior Member
 
Join Date: Aug 2017
Location: Syracuse Ut.
Posts: 692
Xantrex 1800 inverter shutdown

Any chance there is an auto reset circuit breaker in the circuit? The lack of fault codes on two units would indicate a possible complete momentary loss of power resetting the inverter to an off condition maybe. Just about any issue I can think of other than complete temporary loss of power to the inverter should result in an alarm or a fault code.

Edit to add, if you have a remote on off switch maybe disconnect the cable at the inverter to rule out a strange fault with the remote switch.
__________________
2016 Bighorn 3270RS, 2015 Ram 3500 CTD/ASIN
Searching_Ut is offline   Reply With Quote
Old 10-30-2018, 05:08 PM   #5
Senior Member
 
Join Date: Feb 2018
Posts: 1,230
Does your inverter have proper air flow for cooling? My 2200 watt inverter has shutdown when I left my pass through storage doors closed while under heavy load running air conditioning. Does fine with door open.
__________________
Jeff--
Arctic Fox 22G w/1440 watts solar/GMC2500HD Double Cab with Leer Cap w/265 watts solar
astrocamper is offline   Reply With Quote
Old 10-30-2018, 05:39 PM   #6
Member
 
Glenn2's Avatar
 
Join Date: Mar 2017
Location: College Station, TX
Posts: 65
To answer all the appreciated input:
The cables to the inverter from the batteries are large gauge, perhaps multi strand welding cable. The voltage drop is .020 volts from batteries to inverter.
The remote controls the power up of the inverter. It has been replaced also. I will move the remote to the inverter, thus removing the phone cable from the equation.
The shutdown problem happens when on the road. Could very well be a heat issue. Does anyone happen to have a 2017 Thor Challenger 37YT that could tell me where their inverter is mounted? Mine is in the upper left hand corner of the storage bay just to the right of the generator bay.

Thanks to all for your help.
__________________
2017 Thor Challenger 37YT
Glenn2 is offline   Reply With Quote
Reply

Tags
inverter, xantrex



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Xantrex XM 1800 Inverter Troubleshoot jshilko RV Systems & Appliances 9 01-17-2019 01:06 PM
Xantrex 1000 upgrade to Xantrex 1800? FloridaNative49 RV Systems & Appliances 4 10-23-2018 08:16 AM
Inverter xm 1800 xantrex pro inverter Teddymoore Class C Motorhome Discussions 2 09-13-2018 09:53 PM
Xantrex 1800 inverter problem PCarillon MH-General Discussions & Problems 13 06-19-2017 09:35 PM