I am upsizing the battery bank in my 5er from two to three 100 Ah Battleborn batteries. I also have a Victron Multiplus 3kw hybrid inverter.

I am using 4/0 cable throughout. When I ordered cable, though, I did not account for the ground wire. Should the ground be the same size as the primary wire, or can it be something smaller? My original installation used 2 AWG for the ground, and I have a lot of 1/0 cable available.

Thanks!
__________________
2018 F350 Limited, 2021 Arctic Fox 27-5L
300 Ah Battleborn LiFePo4 batteries
3kw Victron Multiplus hybrid Inverter
JHinman is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-07-2021, 08:51 AM   #2
Senior Member
 
Join Date: Oct 2014
Posts: 3,937
Quote:
Originally Posted by JHinman View Post
Should the ground be the same size as the primary wire, or can it be something smaller?

Thanks!

In a word, YES. Inverter to negative should be the same gauge as positive.


Those little electrons do make a round trip!
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is offline   Reply With Quote
Old 10-07-2021, 09:02 AM   #3
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,698
Quote:
Originally Posted by JHinman View Post
I am upsizing the battery bank in my 5er from two to three 100 Ah Battleborn batteries. I also have a Victron Multiplus 3kw hybrid inverter.

I am using 4/0 cable throughout. When I ordered cable, though, I did not account for the ground wire. Should the ground be the same size as the primary wire, or can it be something smaller? My original installation used 2 AWG for the ground, and I have a lot of 1/0 cable available.

Thanks!
No. I use the solid bare ground wire that you can get at Home Depot in the electrical department, which is especially designed for panel and service entrance grounds. You need a ground for the output on the AC side but there should be little if any current flowing on the ground wire.
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 10-07-2021, 09:05 AM   #4
Senior Member
 
Join Date: Oct 2014
Posts: 3,937
Obviously some confusion.


Are you talking about the 12 VDC wire from negative terminal of battery to inverter?


OR


120 VAC ground wire?
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is offline   Reply With Quote
Old 10-07-2021, 09:10 AM   #5
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,698
S/B interesting. I never refer to the Negative lead as a ground, but then, that's me!
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 10-07-2021, 09:16 AM   #6
Senior Member
 
Jayco Owners Club
Join Date: May 2016
Location: North Texas
Posts: 607
Perhaps a better way to say this, both the positive and negative ~12v wires going to the inverter and used to provide the 12v input power to the inverter need to be the same wire size. ~CA
__________________
2010 Jayco GreyHawk 31SS
craigav is offline   Reply With Quote
Old 10-07-2021, 09:31 AM   #7
Senior Member
 
Jayco Owners Club
Join Date: May 2016
Location: North Texas
Posts: 607
BTW, to add to my thoughts and change my answer slightly, while you should have both the pos and neg cables of the same size, and while not up to code for most electrical work, you could simply add a second 2awg conductor to the negative side along with the existing 2awg cable as 2 x 2awg cables are able to carry as much current as 1 x 4/0 awg cable and that would work for you perhaps easiest. If you don't have any more 2awg laying around and if the inverter connection can support it, you could also run a section of 1/0 cable on the negative, again assuming you keep the 2awg already there. ~CA
__________________
2010 Jayco GreyHawk 31SS
craigav is offline   Reply With Quote
Old 10-07-2021, 09:31 AM   #8
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,698
Frankly, never seen an inverter ground lug that could take a cable anywhere nearly that big anyway. Xantrex specs say a minimum of #8 for the ground.
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 10-07-2021, 09:34 AM   #9
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 10,024
My Xantrex/Trace 2000 WATT inverter uses the same size cable for + - & ground


When in doubt go the safe route, oversize.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is offline   Reply With Quote
Old 10-07-2021, 09:35 AM   #10
Senior Member
 
Join Date: Nov 2018
Location: Beaver Dam, Wisconsin
Posts: 2,723
Best practice is to follow instructions in the installation manual for your inverter make and model.

The ground connection on the metal box of the inverter is typically frame ground for the 120 volt side. It should be the same gauge as the system ground on the 120 volt output. It trips circuit breaker or blows a fuse when certain wiring malfunctions occur.

However, some inverters are designed to also frame ground the 12 volt side and larger gauge is required.
__________________
Paul Bristol
Kodiak Cub 176RD
Nissan Pathfinder 2015
Persistent is offline   Reply With Quote
Old 10-07-2021, 09:47 AM   #11
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,698
Too bad I didn't invest in copper futures. This is a calculation for a 3000 watt inverter, running at 12.8 volts (fully charged bank.) Roughly 250 amps draw, inverter located 5 feet from the battery bank (5+5 = 10 foot run). as you can see, 4/0 to 2/0 buys .07 volts at peak draw, or .5%. Hardly worth it.
Attached Files
File Type: pdf 3000 Watt Inverter Cabling.pdf (17.0 KB, 6 views)
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 10-07-2021, 10:07 AM   #12
Senior Member
 
Jayco Owners Club
Join Date: May 2016
Location: North Texas
Posts: 607
Quote:
Originally Posted by Sbrownstein View Post
Too bad I didn't invest in copper futures. This is a calculation for a 3000 watt inverter, running at 12.8 volts (fully charged bank.) Roughly 250 amps draw, inverter located 5 feet from the battery bank (5+5 = 10 foot run). as you can see, 4/0 to 2/0 buys .07 volts at peak draw, or .5%. Hardly worth it.

Line loss is only one consideration, keep in mind that if you have 250a sustained current that a 2/0 cable is going to run much hotter and in fact hotter than what most 2/0 cables are rated for. I don't have the specifications in front of me, but the 2/0 cable would likely run 225+ degrees or more (very hot) at a sustained 250a where the 4/0 cable would run much cooler (perhaps 75f degrees cooler, although I don't have the specs to check this right now to tell exactly how much cooler, but for sure a lot cooler with the larger conductor). ~CA
__________________
2010 Jayco GreyHawk 31SS
craigav is offline   Reply With Quote
Old 10-07-2021, 10:51 AM   #13
Senior Member
 
Join Date: Sep 2020
Location: Boise, ID
Posts: 553
The ground I refer to connects the aluminum enclosure to the trailer chassis.

The AC lines all have 3-wire connectors.

The Victron manual does not discuss the ground.
Attached Thumbnails
Click image for larger version

Name:	442394BE-8BDC-4B14-BB34-C78C53F4348A.jpg
Views:	8
Size:	117.5 KB
ID:	345356   Click image for larger version

Name:	AF2571C4-6318-4B5D-A008-478EF9125CC2.jpg
Views:	11
Size:	367.9 KB
ID:	345357  

Click image for larger version

Name:	2E94FC19-DBB4-4A51-B33C-E553B6F49EB1.jpg
Views:	11
Size:	147.0 KB
ID:	345358  
__________________
2018 F350 Limited, 2021 Arctic Fox 27-5L
300 Ah Battleborn LiFePo4 batteries
3kw Victron Multiplus hybrid Inverter
JHinman is offline   Reply With Quote
Old 10-07-2021, 10:57 AM   #14
Senior Member
 
powercat_ras's Avatar
 
Winnebago Owners Club
Solo Rvers Club
Join Date: May 2015
Posts: 1,621
I suggest a 6 AWG solid copper grounding conductor, as short as possible. Chances are the grounding connection on the inverter would have to be modified to take anything larger than that.

Equipment grounding conductor table
__________________
Randy - Manhattan, Kansas
2015 Vista 27N
2020 Ford Escape Hybrid
powercat_ras is offline   Reply With Quote
Reply

Tags
inverter



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onboard ground fault conflicts with campground ground fault skatebus80 Country Coach Owners Forum 3 07-15-2017 01:42 PM
Ground clearance with jacks up down to the ground Rvlegaleagle Class C Motorhome Discussions 8 09-01-2016 07:54 AM
Positive ground or negative ground? 1010 iRV2.com General Discussion 43 07-14-2015 12:29 PM
New Ground Connection needed deandec Class A Motorhome Discussions 2 06-15-2014 12:47 PM
no ground ok-ground trips gfi FLYING BUTCH iRV2.com General Discussion 14 06-01-2011 07:52 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 09:31 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.