Parallel or Serial configuration for Go-Power Panels

My new 5th wheel came with one 190W Go-Power panel installed.
I replaced already the simple PWM controller with a 40 amp Renogy Rover MPPT controller. Now I want to install a second solar panel. I opted for another identical Go-Power to avoid potential balance issues.

Normally I would configure them in series go get better output in low light conditions and reduce voltage drop in the cable. But the Go-Power manual specifically warns to install multiple panels in parallel (quote "Failure to follow this connection procedure will cause the system to produce large currents which the protection device, DC fuse is not designed the handle" end quote).

Now I thought that all modern solar panels have proper parallel and serial diodes to prevent damage to the panel but then, maybe this one not? Does not make sense because the panel is already more expensive than the typical panels on Amazon.

Any opinion? Maybe not take a risk and just do what the doctor said?

Thanks, JB
__________________
2021 F350 Lariat SRW Diesel, 2021 Alliance Paradigm 310RL 5th Wheel, Superglide Hitch, 380W Solar, Onan 5500 Propane Genset
Jerry Burks is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 04-25-2021, 08:51 PM   #2
Senior Member
 
Join Date: Jan 2018
Location: UT
Posts: 1,256
i'm not sure I understand your post clearly or the instructions you quoted. Wiring the panels in parallel will double the current and keep the voltage the same so if there is a worry about overcurrent, parallel should be avoided.

As you apparently know, there are valid reasons to avoid series wiring because shading one panel will bring down the entire series string to a lower output. Parallel helps reduce this problem a bit but will double the current so you need to have the charge controller and wire gauge to handle the extra current.
__________________
Ed
2023 Geneva 28VA
2018 Thor Palazzo 33.3
iluvuk is offline   Reply With Quote
Old 04-26-2021, 12:21 PM   #3
Senior Member
 
Join Date: Apr 2019
Location: Fort Collins, CO
Posts: 309
Quote:
Originally Posted by iluvuk View Post
i'm not sure I understand your post clearly....
Well, that is the point. I quoted the warning in the Go-Power manual and I don't understand it, either.

I have the additional panel installed now and to be sure connected both in parallel. I estimate about 0.9 V voltage drop at 18 amps in 50 feet total of 10 gage wire. That would be 5% loss of the panel voltage vs. 2.5% when in series. Part of that difference should be compensated for by about 1% better efficiency of the Renogy Rover MPPT controller running at 20V compared to 40V.

So I guess I can live with that...
__________________
2021 F350 Lariat SRW Diesel, 2021 Alliance Paradigm 310RL 5th Wheel, Superglide Hitch, 380W Solar, Onan 5500 Propane Genset
Jerry Burks is offline   Reply With Quote
Old 04-26-2021, 09:24 PM   #4
Senior Member
 
Join Date: Apr 2019
Location: Fort Collins, CO
Posts: 309
Oh well. After I did the install I got feedback from Go-Power tech support:

"Thank you for your inquiry.

We usually use pwm controllers with our 190 watt panels. so this is why we suggest wiring in parallel. (the limitation on the controller) With a MPPT controller it should be able to handle a higher voltage and be able to be wired in series . I would check the max voltage and current input on the controller to verify this."

So the warning was not about the panels but rather the PWM controller....

Anyway, I will just leave it wired parallel for now. Small difference.
__________________
2021 F350 Lariat SRW Diesel, 2021 Alliance Paradigm 310RL 5th Wheel, Superglide Hitch, 380W Solar, Onan 5500 Propane Genset
Jerry Burks is offline   Reply With Quote
Old 04-26-2021, 09:32 PM   #5
Senior Member
 
Join Date: Apr 2005
Posts: 4,458
Quote:
Originally Posted by Jerry Burks View Post
Oh well. After I did the install I got feedback from Go-Power tech support:

"Thank you for your inquiry.

We usually use pwm controllers with our 190 watt panels. so this is why we suggest wiring in parallel. (the limitation on the controller) With a MPPT controller it should be able to handle a higher voltage and be able to be wired in series . I would check the max voltage and current input on the controller to verify this."

So the warning was not about the panels but rather the PWM controller....

Anyway, I will just leave it wired parallel for now. Small difference.
Actually I think you know this stuff better than many of us. Sounds like it turned out well.
radar is offline   Reply With Quote
Old 04-29-2021, 03:27 PM   #6
Senior Member
 
Join Date: Sep 2017
Posts: 1,052
Quote:
Originally Posted by Jerry Burks View Post
Well, that is the point. I quoted the warning in the Go-Power manual and I don't understand it, either.

I have the additional panel installed now and to be sure connected both in parallel. I estimate about 0.9 V voltage drop at 18 amps in 50 feet total of 10 gage wire. That would be 5% loss of the panel voltage vs. 2.5% when in series. Part of that difference should be compensated for by about 1% better efficiency of the Renogy Rover MPPT controller running at 20V compared to 40V.

So I guess I can live with that...

Extra 2.5% (PEAK) drop on your 380w system translates to just 9.5w loss. Drink a beer and enjoy your solar!
SJ-Chris is offline   Reply With Quote
Old 04-30-2021, 09:23 AM   #7
Member
 
Join Date: Sep 2020
Posts: 76
It's a little moot at this point, but you need a certain amount of voltage to charge the batteries and wiring in series gives the MPPT controller more to work with in marginal conditions, like first and last light or cloudy conditions. I noticed the difference when I rewired my four panels from parallel to series/parallel, doubling the voltage.
treeoflib is offline   Reply With Quote
Old 04-30-2021, 10:22 AM   #8
Senior Member
 
Join Date: Jan 2018
Location: UT
Posts: 1,256
Quote:
Originally Posted by treeoflib View Post
It's a little moot at this point, but you need a certain amount of voltage to charge the batteries and wiring in series gives the MPPT controller more to work with in marginal conditions, like first and last light or cloudy conditions. I noticed the difference when I rewired my four panels from parallel to series/parallel, doubling the voltage.
Excellent point!
__________________
Ed
2023 Geneva 28VA
2018 Thor Palazzo 33.3
iluvuk is offline   Reply With Quote
Old 04-30-2021, 10:47 AM   #9
Senior Member
 
Join Date: Jul 2014
Posts: 35,403
More amps cause more voltage drop in same size wire.
2 panels and a MPPT controller, run them in series.
twinboat is online now   Reply With Quote
Old 04-30-2021, 12:47 PM   #10
Senior Member
 
Join Date: Jan 2018
Location: UT
Posts: 1,256
Twinboat is correct. I have noted however that if you have panels in series, even with mppt, and one portion of one panel is shaded, it takes down the output of the entire series string of panels. Tests on youtube seem to confirm this. Have you found a way around this with new technology or other suggestions? Only thing I have found is avoid shade on all panels which is not practical, wire in parallel with bigger wire, or put each panel on its own charge controller. Interested in the experience of others.
__________________
Ed
2023 Geneva 28VA
2018 Thor Palazzo 33.3
iluvuk is offline   Reply With Quote
Reply

Tags
panel, power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Damage from connecting solar panels in parallel? bbon Going Green 2 08-15-2019 11:40 AM
Solar panels in 3 series sets to parallel. dckromm Going Green 20 08-03-2019 07:33 AM
Solar in series and parallel with 3 panels? Vintage465 Outdoors RV Owner's Forum 25 02-21-2019 11:59 AM
suggestions on connecting 3 160 watt panels in parallel. dssl Going Green 5 06-04-2018 04:50 PM