Running Fridge on Inverter
My fridge is 1.8 amps. 700 watts of solar. 4 six-volt batteries. 40 amp mppt charger. 2000 watt inverter. Im running a swamp cooler constant 3 amps And the fridge starts up good but after about 3 hours when it restarts it kills the inverter. Not sure if its low voltage or too many watts, but I've still got like 12.2 volts. Maybe my batteries are weak. My inverter is next to the batteries with 2 ot cables. I hope this makes sense. Any ideas are appreciated.
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
08-13-2020, 10:56 PM
|
#2
|
Senior Member
Country Coach Owners Club Solo Rvers Club iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
|
12.2 volts is just under 50% charge but still should run your fridge. I have 1220 amp hr of battery but still get near 12.2 by morning with my Jenn Aire residential refer.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
|
|
|
08-14-2020, 12:10 AM
|
#3
|
Senior Member
Join Date: Jul 2014
Posts: 35,413
|
If your starting with 12 .7 volts or more and are down to 12.2 volts, in 3 hours, with the inverter shut down, your batteries are overdue for replacement.
Your draw is 5 amps per hour for 3 hours or 15 AHs.
4, 6 volt batteries should give you 400 AH.
|
|
|
08-14-2020, 08:18 AM
|
#4
|
Senior Member
Entegra Owners Club
Join Date: Jun 2004
Location: Bayfield, Ontario
Posts: 5,465
|
Quote:
Originally Posted by asgweb
My fridge is 1.8 amps. 700 watts of solar. 4 six-volt batteries. 40 amp mppt charger. 2000 watt inverter. Im running a swamp cooler constant 3 amps And the fridge starts up good but after about 3 hours when it restarts it kills the inverter. Not sure if its low voltage or too many watts, but I've still got like 12.2 volts. Maybe my batteries are weak. My inverter is next to the batteries with 2 ot cables. I hope this makes sense. Any ideas are appreciated.
|
What inverter do you have? Does it have a LBCO (low battery cutout) setting? Perhaps it is set too high and is causing your inverter to shut down.
__________________
Don & Gerri
2014 Entegra Anthem 44B
2014 Honda CRV Touring
1300W Solar, 1200AH LiFePO4 FMCA F443497
|
|
|
08-14-2020, 09:03 AM
|
#5
|
Senior Member
Thor Owners Club Ford Super Duty Owner
Join Date: Jul 2011
Posts: 3,793
|
When I first installed a residential fridge my two batteries I had at the time were older and of marginal performance AND the DC power 2 gauge cables between the batteries and inverter were on the small side for what I was demanding of the configuration. At around 12.2 or so volts the start surge of my fridge would drag the battery volts down below inverter minimum and cause a fault. The surge is somewhat quick and the voltage drop is hard to see with a digital meter but you might be able to catch it with an analog meter. I replaced the two tired batteries with four and increased the cables to 4/0 gauge. All has been good ever since.
__________________
2006 Hurricane 31D built on a 2006 Ford F53
|
|
|
08-14-2020, 04:12 PM
|
#6
|
Member
Join Date: Apr 2018
Location: SnapRV.com
Posts: 37
|
it's an Edecoa 2000 watt/4k peak. It's been a good inverter, not sure if it's really 2k watts. I can't set the shut off but it's set at like 11 volts.
|
|
|
08-14-2020, 04:54 PM
|
#7
|
Senior Member
Join Date: Sep 2017
Location: Northern California
Posts: 1,418
|
Quote:
Originally Posted by asgweb
it's an Edecoa 2000 watt/4k peak. It's been a good inverter, not sure if it's really 2k watts. I can't set the shut off but it's set at like 11 volts.
|
Well aged batteries do have more internal resistance and the voltage will drop more than on new ones when a load is thrown on (with a bit of surge). And the batteries being down around 50% state of charge exacerbates this problem with even more internal resistance. The tip-off is the problem occurring some time after drawing energy out of the battery. As other's have said, try to capture the battery voltage during fridge start-up.
|
|
|
08-15-2020, 03:27 PM
|
#8
|
Senior Member
Join Date: Feb 2018
Posts: 1,283
|
I would want to know your cable size and length between batteries and inverter. Voltage drop can be considerable. The cables that come with some inverters are grossly undersized.
Lead Acid batteries are better in your four battery configuration of two 6 volt batteries in series and the pair in parallel. That should work if the batteries a good.
__________________
Jeff--
Arctic Fox 22G w/1440 watts solar/GMC2500HD Double Cab with Leer Cap w/740 watts solar
|
|
|
08-25-2020, 08:15 PM
|
#10
|
Member
Join Date: Apr 2018
Location: SnapRV.com
Posts: 37
|
Quote:
Originally Posted by 757driver
What inverter do you have? Does it have a LBCO (low battery cutout) setting? Perhaps it is set too high and is causing your inverter to shut down.
|
It's an Edecoa. It has a low battery shut off the is not adjustable butI think is set at 10.5 volts.
|
|
|
08-26-2020, 08:59 AM
|
#11
|
Senior Member
Entegra Owners Club
Join Date: Jun 2004
Location: Bayfield, Ontario
Posts: 5,465
|
Quote:
Originally Posted by asgweb
It's an Edecoa. It has a low battery shut off the is not adjustable butI think is set at 10.5 volts.
|
If your LBCO is set to 10.5v that is fine and not your problem.
__________________
Don & Gerri
2014 Entegra Anthem 44B
2014 Honda CRV Touring
1300W Solar, 1200AH LiFePO4 FMCA F443497
|
|
|
08-31-2020, 05:21 PM
|
#12
|
Member
Join Date: Apr 2018
Location: SnapRV.com
Posts: 37
|
Turns out it was the heat sensor breaker. Just kinda cheap. Replaced it with a better one and it works great. probably replace all of them. I also bought a 3K watt inverter but not sure I need it.
|
|
|
08-31-2020, 05:23 PM
|
#13
|
Member
Join Date: Apr 2018
Location: SnapRV.com
Posts: 37
|
Quote:
Originally Posted by Sweetbriar
When I first installed a residential fridge my two batteries I had at the time were older and of marginal performance AND the DC power 2 gauge cables between the batteries and inverter were on the small side for what I was demanding of the configuration. At around 12.2 or so volts the start surge of my fridge would drag the battery volts down below inverter minimum and cause a fault. The surge is somewhat quick and the voltage drop is hard to see with a digital meter but you might be able to catch it with an analog meter. I replaced the two tired batteries with four and increased the cables to 4/0 gauge. All has been good ever since.
|
Just wonder how many amps your fridge is and how many watts your inverter is. Thanks.
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|