150-foot 50 amp extension cable

Hi. "Long-time lurker, first time poster"

I had a pad made for my Forza and an electrician and plumber installed a proper 50 amp hookup like the ones you find at campsites.

However, from time to time I want the coach in my driveway close to my house, which is ~175 ft from the hookup.

I wonder if I could make a cable using 4awg conductors and plugs.

A few questions for input:
1. Is this possible and safe?

2. Would the following aluminum wire work (this application is a simple extension cord, would not be buried):
https://www.wireandcableyourway.com/...ion-cable.html

I could use some 4/4 SOOW which is copper but it is 4x the price and I think unnecessary for the length we're talking about (e.g. https://www.wireandcableyourway.com/...0aAgSfEALw_wcB)

3. Seems that the standard Camco plugs can take up to 4ga wire so would those work ok? Would they be compatible with aluminum wire which is typically less flexible? I have no experience with those terminations so not sure how the bindings work on the inside. https://www.amazon.com/Camco-PowerGr...000PGVZ30?th=1

Thanks in advance for any thoughts or input.

Matt
__________________

MattyA is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-15-2020, 08:45 PM   #2
Senior Member
 
dkoldman's Avatar
 
Winnebago Owners Club
Ford Super Duty Owner
Join Date: Oct 2019
Location: Dallas, Texas
Posts: 361
Quote:
Originally Posted by MattyA View Post
Hi. "Long-time lurker, first time poster"

I had a pad made for my Forza and an electrician and plumber installed a proper 50 amp hookup like the ones you find at campsites.

However, from time to time I want the coach in my driveway close to my house, which is ~175 ft from the hookup.

I wonder if I could make a cable using 4awg conductors and plugs.

A few questions for input:
1. Is this possible and safe?

2. Would the following aluminum wire work (this application is a simple extension cord, would not be buried):
https://www.wireandcableyourway.com/...ion-cable.html

I could use some 4/4 SOOW which is copper but it is 4x the price and I think unnecessary for the length we're talking about (e.g. https://www.wireandcableyourway.com/...0aAgSfEALw_wcB)

3. Seems that the standard Camco plugs can take up to 4ga wire so would those work ok? Would they be compatible with aluminum wire which is typically less flexible? I have no experience with those terminations so not sure how the bindings work on the inside. https://www.amazon.com/Camco-PowerGr...000PGVZ30?th=1

Thanks in advance for any thoughts or input.

Matt
If I follow correctly, this should be easy. Have your electrician come back out and simply add a 50 amp service at your house. You don't need a plumber. The money you will save on the wiring will pay for the electrician. You can even get a simple 50 amp box, but I would get a subpanel that serves 50/30/20. It is only about $130.

That cord otherwise would be awfully heavy to run that long. Sounds like you got the real deal set up, make it even nicer, we will all be jealous
__________________

__________________
2019 Sunstar 29VE
Safe T Plus; EC-30 AGS Nighthawk X4 AC2200 WiFi EX7300; H/W Heater & Chassis Disconnect Switches; Surge Guard 44270
dkoldman is offline   Reply With Quote
Old 07-15-2020, 08:59 PM   #3
Junior Member
 
Join Date: Jul 2020
Posts: 4
Yes, thatís an option. But itís a bit more complicated...the property has 300 amp service and the RV pad is being run from the panel at the house where the service comes in. The driveway is in front of the garage which is actually also a guest house with 100 amp service and a very full panel. It is possible but complicated. For the amount of time Iím going to have the RV in the driveway Iím basically trying to figure out if a really simple solution could work that doesnít involve a permanent install.

Btw the pad has 20/30/50 on the h frame and a panel that can be added-to so there is flexibility if we want to put anything else there in the future. It is indeed a sweet setup!
MattyA is offline   Reply With Quote
Old 07-15-2020, 09:14 PM   #4
Senior Member


 
Join Date: Jun 2017
Posts: 2,654
When you move the RV by the house for this "temporary" time will you really need 50 amp service? Or do you simply need power for the fridge and maybe just 1 A/C? Would a 20 or 30 amp extension cord do the trick for this case?
tfryman is offline   Reply With Quote
Old 07-15-2020, 09:18 PM   #5
Senior Member
 
Join Date: Jun 2016
Location: Omaha, Ne
Posts: 283
I would not use aluminum wire for that distance, the conductivity is only like 3/5th's (60%) of copper wire, you will drop more voltage then you would with copper and it could potentially run hotter.
__________________
Curt
2015 Wildcat 295RSX
2014 Ram 3500 CC 6.7 cummins
wildcatter is offline   Reply With Quote
Old 07-15-2020, 09:26 PM   #6
Senior Member
 
JJH3rd's Avatar
 
National RV Owners Club
Workhorse Chassis Owner
Join Date: Feb 2011
Location: Covington, GA
Posts: 657
Send a message via Skype™ to JJH3rd
This might help:
(https://www.thespruce.com/extension-...hart-1152866);

(https://www.calculator.net/voltage-d...culator.html);

(https://www.southwire.com/calculator-vdrop)
__________________
J.J. Hayden (KN4SH)
Covington, GA
2005 National Dolphin 5342
JJH3rd is offline   Reply With Quote
Old 07-15-2020, 09:44 PM   #7
Senior Member
 
dkoldman's Avatar
 
Winnebago Owners Club
Ford Super Duty Owner
Join Date: Oct 2019
Location: Dallas, Texas
Posts: 361
If you not going to use that much, the extension cord off 20/30 suggested is simply enough.

In my view getting a 175 ft 50 amp extension cord is a non starter Way to heavy to move around.

Since we brainstorming, here is another option. Not sure how / where run from house to your pad is, but have the electrician find a sweet spot closest to driveway between run from house to new RV pad. Have him mount an external switch on the line of the existing breaker ( I am guessing it it is 50 or 60 amps) from the 300 amp service. You could then run a 2nd line to driveway location using same 50 or 60 amp breaker. With the Switch, you should be able to send power to RV Pad, or Driveway or Off. Given what you already have, this is what I would do, you would have two cakes and eat them both too
__________________
2019 Sunstar 29VE
Safe T Plus; EC-30 AGS Nighthawk X4 AC2200 WiFi EX7300; H/W Heater & Chassis Disconnect Switches; Surge Guard 44270
dkoldman is offline   Reply With Quote
Old 07-16-2020, 03:02 AM   #8
Senior Member
 
Join Date: Jul 2018
Posts: 2,633
Quote:
Originally Posted by dkoldman View Post
If you not going to use that much, the extension cord off 20/30 suggested is simply enough.

In my view getting a 175 ft 50 amp extension cord is a non starter Way to heavy to move around.

Since we brainstorming, here is another option. Not sure how / where run from house to your pad is, but have the electrician find a sweet spot closest to driveway between run from house to new RV pad. Have him mount an external switch on the line of the existing breaker ( I am guessing it it is 50 or 60 amps) from the 300 amp service. You could then run a 2nd line to driveway location using same 50 or 60 amp breaker. With the Switch, you should be able to send power to RV Pad, or Driveway or Off. Given what you already have, this is what I would do, you would have two cakes and eat them both too
^^^ This ^^^

A switch is probably the easiest way to use a single service. I drag some 4/4 SO around and 100 ft is no fun at all. A 175' run would require wheels and maybe an assistant.
__________________
2005 Four Winds Majestic 23A
ďTo the world you may be one person; but to one person you may be the world.Ē - Dr Suess
Solo_RV_Guy is offline   Reply With Quote
Old 07-16-2020, 03:32 AM   #9
Senior Member
 
USMCRET's Avatar
 
Newmar Owners Club
Join Date: Jul 2011
Posts: 2,036
I have 100’ of 50 amp cord I bought ill-advisedly. I used it one time. It’s far too heavy to work with, or at least I am not of a mind to mess with it. 30 amp on the other hand, is much more user friendly.
__________________
2005 Newmar KSDP 3910
ISC on a Spartan
USMCRET is offline   Reply With Quote
Old 07-16-2020, 04:59 AM   #10
Senior Member
 
xrated's Avatar
 
Join Date: Jan 2017
Location: "Murvil", TN
Posts: 1,155
Buy a portable generator that is large enough for what you need....unless you are going to have it parked there for days on end.
__________________
2016 F350 Crew Cab Dually Diesel King Ranch 4x4
2018 Grand Design Momentum 394M Toy Hauler
Excessive Payload Capacity is a Wonderful Thing!
xrated is online now   Reply With Quote
Old 07-16-2020, 05:51 AM   #11
Junior Member
 
Join Date: Jul 2020
Posts: 4
Super helpful everyone. Many thanks.

I agree that running another line from the main service with a switch is the best solution, but probably major overkill.

Right now I am plugged into an exterior 20a wall outlet using an adapter and the energy management system in the coach is working to try and keep it cool. But the power is insufficient and the breaker trips all the time because the same circuit runs a very important family fridge and chest freezer in the garage as well as a large garage dehumidifier. Plus I had to disconnect the aerator in the pond which yields an unhappy wife (a 100-ft 10 awg extension to run that from an outlet off another circuit is arriving tomorrow!).

I get all the points about weight...I had sort of discounted them as "annoying details" but they are of course good points. Also there is the issue of "yet another thing to store in the garage"...that cord would be bulky indeed!!!
MattyA is offline   Reply With Quote
Old 07-16-2020, 05:55 AM   #12
Junior Member
 
Join Date: Jul 2020
Posts: 4
Btw the voltage drop calculator is a great resource. The diff btw Al and Cu is not as big as I expected.
MattyA is offline   Reply With Quote
Old 07-16-2020, 06:44 AM   #13
Senior Member
 
Join Date: Dec 2019
Location: NC
Posts: 184
I was going to say just run the onboard gen. A portable would have much more flexibility in the long run.
Good call Xrated.
__________________
17 year member on that other RV forum.
2005 Cummins 3500 dually 2014 Blue Ridge 3025RL
Toby Dog is online now   Reply With Quote
Old 07-16-2020, 06:44 AM   #14
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 6,988
The aluminum wire you linked to is not flexible at all and would be a pain to use. Also, this type of wire has no protective covering and is designed to be in conduit unless you get a direct bury type cable which adds even more rigidity to the cable.



You say that you have a guest house with a 100 amp service. I would take a look at it and see if you could make some changes to add a double pole breaker for a 50 amp plug. You possible could add a small subpanel and move some wires around, depending on access.

I dis this on one of the two 200 amp panels I have in order to add a 50 amp plug for my RV parking.
__________________

__________________
Jim J
2002 Monaco Windsor 38 PKD
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is online now   Reply With Quote
Reply

Tags
cable



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sanicon 10 foot extension tom chelbana Newmar Owner's Forum 4 09-14-2019 09:45 PM
Can you guys help me get a foot up? Or in this case two foot! WyoFree Class A Motorhome Discussions 11 02-20-2017 03:11 PM
Diesels in 24-25 foot and 28-30 foot rj flyer Class C Motorhome Discussions 5 02-15-2017 10:34 PM
42 foot or 37 foot 5th Wheel lungguy 5th Wheel Discussion 13 12-30-2016 01:53 PM
50 amp coach to 30 amp extension to 50 amp house? abarkl RV Systems & Appliances 10 01-02-2015 08:55 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 07:01 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
×