50 amp extended run with UF electrical cable

Hi, need some help...
Moving my Dutch Star to my daughter's 5 acres...
Need to bury around 200 feet of UF cable for service...
DS draws a max of 50 amps (25amps at 120 volts)...
Looking at 6/3 UF cable but confused if 6 ga is big enough...
Charts say no more than a 3% drop in voltage....
Any help is appreciated...
Bob
South Carolina
__________________
2001 Dutch Star 3666 (Workhorse gas)
Lugoff, SC

KE5FTF...Bob & Kathy
Bmaintz8 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-22-2017, 12:55 PM   #2
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
There are many calculators for wire gauge on the internet. Be sure to measure from the power panel, not just the outside run. Also, be sure that the professional electrician that does the wiring knows RV 50 amp service is two 50 amp hot lines of 120v, not 240v. The two hot lines also need to be 180º out of phase from each other.

Furthermore, TEST the new outlet with a meter before plugging in the RV.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 11-22-2017, 01:06 PM   #3
Senior Member
 
Isaac-1's Avatar
 
Join Date: Jun 2016
Location: SW Louisiana
Posts: 8,953
I would also suggest measuring the voltage at the panel you are connecting to, I did something similar to install an outlet in the shed on the family farm where I store my coach, though my run was less than 100 ft using 6/3 UF with ground from the sub panel. With mine due to the already low voltage at the panel I get drop outs caused by low voltage detection by my Surge Guard EMS in my coach when I run higher amp appliances while also running my air conditioner, etc. For example last summer I tried running a 12 amp carpet cleaner and my roof mounted air conditioner at the same time which caused enough voltage drop for my EMS to disconnect the line power.
__________________
2002 Safari Trek 2830 on P32 Chassis with 8.1L w/ 400 watts solar 420Ah LiFePo4
2017 Jeep Cherokee Overland & 2007 Toyota Yaris TOADs with Even Brake,
Demco Commander tow bar and Blue Ox / Roadmaster base plates
Isaac-1 is offline   Reply With Quote
Old 11-22-2017, 01:32 PM   #4
Senior Member
 
powercat_ras's Avatar
 
Winnebago Owners Club
Solo Rvers Club
Join Date: May 2015
Posts: 1,834
I would feed a RV pedestal box, such as the Siemens TL137US Talon Temporary Power Outlet Panel with a 20, 30, and 50-Amp Receptacle Installed, with a 50 Amp 240 Volt breaker using 4/3 UF with Ground Cable at a minimum, given that you don't expect to use more than 25 amps out of each leg normally. For a 200 foot run, 3 volts AC less at the 120 volt load than at the source - worst case with 25 amp load on one leg and zero amp load on other leg of the 50 amp RV outlet.

If you can afford it go ahead and use 2/3 UF the 4/3 UF will have too much voltage drop if the amps is over 25 out of each leg, due to the long 200 feet run. Some future RV using it might use more as the feed will be capable of 50 out of each leg.
__________________
Randy - Manhattan, Kansas
2015 Vista 27N
2020 Ford Escape Hybrid
[SIGPIC][/SIGPIC]
powercat_ras is offline   Reply With Quote
Old 11-22-2017, 02:50 PM   #5
Senior Member
 
Join Date: Oct 2017
Posts: 326
Quote:
Originally Posted by BFlinn181 View Post
There are many calculators for wire gauge on the internet. Be sure to measure from the power panel, not just the outside run. Also, be sure that the professional electrician that does the wiring knows RV 50 amp service is two 50 amp hot lines of 120v, not 240v. The two hot lines also need to be 180º out of phase from each other.

Furthermore, TEST the new outlet with a meter before plugging in the RV.


50 amp “RV” service is nothing unique. It is regular 240/120 volt 50 amp. Same deal as in your home. The 50 amp connector (plug/receptacle) is nothing unique. The same as in homes used by ranges/cooktops.

Two 120v hot lines IS 240v. That is how it works.
325BH is offline   Reply With Quote
Old 11-22-2017, 03:16 PM   #6
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
Quote:
Originally Posted by 325BH View Post
50 amp “RV” service is nothing unique. It is regular 240/120 volt 50 amp. Same deal as in your home. The 50 amp connector (plug/receptacle) is nothing unique. The same as in homes used by ranges/cooktops.

Two 120v hot lines IS 240v. That is how it works.
You are correct when it's wired properly. On a 50 amp outlet, a DIY could also hook up the two hot leads from the same side of the breaker panel, thus not providing correct power. The neutral can be the same gauge as two hot leads because the AC power is 180º out of phase.

The bigger problem comes when folks plug into a 30 amp dryer outlet. An RV 30 amp outlet is 30amp 120v, a dryer (or welder) is 30 amp 240v. Folks without an EMS have fried their RV appliances plugging into an outlet that 'looks' like RV 30 amp plug.

I'd still suggest using a professional, licensed electrician to do the wiring. Most places require an inspection also.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 11-22-2017, 03:17 PM   #7
Senior Member
 
Join Date: Oct 2017
Posts: 326
Quote:
Originally Posted by Bmaintz8 View Post
Hi, need some help...
Moving my Dutch Star to my daughter's 5 acres...
Need to bury around 200 feet of UF cable for service...
DS draws a max of 50 amps (25amps at 120 volts)...
Looking at 6/3 UF cable but confused if 6 ga is big enough...
Charts say no more than a 3% drop in voltage....
Any help is appreciated...
Bob
South Carolina


If your Dutch Star is 50 amp service, it is two 120 volt hots, 50 amps each. This is standard 240/120 volt service like in your home. Nothing unique.

200 feet is a concern.

The quick answer would be between 1AWG and 4AWG... depending on how balanced the load is. In reality, 4AWG would probably be OK.
325BH is offline   Reply With Quote
Old 11-22-2017, 03:28 PM   #8
Senior Member
 
Join Date: Jul 2014
Posts: 35,438
Why are we even talking about 30 amp service ?

The OP asked about a 50 amp extension. Do we need to muddy the waters with 30 amp 120 volt service and old outdated dryer outlets ?

Also, to pick up 2 hots on the same leg, in a service panel, you would need 2 independent 50 amp breakers, or bust one apart, and place then apart from each other. Again, the OP has enough sense to question the wire gauge. Do you think he would split up a double pole breaker ?

Its a standard 240 volt service. There Is no RV 50 amp service.
You can NOT make a " two the same phase " 50 amp service and get 240 volts from it.
twinboat is offline   Reply With Quote
Old 11-22-2017, 03:56 PM   #9
Senior Member
 
saddlesore's Avatar


 
Foretravel Owners Club
Join Date: Apr 2016
Location: Home is Where WE PARK IT...
Posts: 6,054
Quote:
Originally Posted by twinboat View Post
Why are we even talking about 30 amp service ?

.
Because there are Forum members that may only have a 30a or 20a RV, and may be following this thread, also it is not uncommon for a RV'r to put in a 50/30/20 wired pedestal.
Not everyone has the deep pockets to have a 50a RV....
__________________
Retired truckdriver,
'02 Foretravel... "This Shack will do"
being pushed by an '06 Scion xB
SKP's of Box Elder, South Dakota
saddlesore is offline   Reply With Quote
Old 11-22-2017, 04:32 PM   #10
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
Quote:
Originally Posted by twinboat View Post
Why are we even talking about 30 amp service ?
I brought it up because wiring can be done in a variety of ways and it is more problematic in 30 amp RVs than 50 amp ones, but it does happen. Google 30 amp outlet and you'll find a variety of 30 amp styles, some of which look like your RV plug but will fry it. Same for 50 amp outlets, there are a variety of styles. That's why I said it's best to tell an electrician exactly what style of 50 amp service you want to be installed. I've had my 50 amp EMS fail to connect at campground pedestals that aren't wired properly.

Quote:
Originally Posted by saddlesore View Post
Because there are Forum members that may only have a 30a or 20a RV, and may be following this thread, also it is not uncommon for a RV'r to put in a 50/30/20 wired pedestal.
Not everyone has the deep pockets to have a 50a RV....
I don't necessarily believe it takes 'deep pockets' to have a 50a RV, my '98 is 50a and I don't have a high-end RV or deep pockets. The rest of the above is quite true, a search of the forum will yield horror stories of plugging into outlets that aren't configured for RV service.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 11-22-2017, 04:47 PM   #11
Senior Member
 
Bmaintz8's Avatar
 
Newmar Owners Club
Join Date: Feb 2012
Location: Elgin, SC
Posts: 291
Wow.... Thanks for all of your help...
We are a few months before we move the DS to my daughter's place...
Will need to measure the distance & see if we will have to go to the 4 ga...
I have looked at the Calculators & loss factors...
In regards to the UF cable do we need the bare ground wire which makes it 4 wires all together...
My neighbor next to me is a certified RV mechanic & does some work in the park, I'll ask him to wire it all up for me...
__________________
2001 Dutch Star 3666 (Workhorse gas)
Lugoff, SC

KE5FTF...Bob & Kathy
Bmaintz8 is offline   Reply With Quote
Old 11-22-2017, 04:59 PM   #12
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,697
There are two considerations for selecting wire size: ampacity (amp load) and voltage drop. 6 gauge UF will handle 55A/wire and the voltage drop calculator I used shows about 6 drop, depending on the assumptions used. It looks like 4 gauge or even 2 gauge would be a better choice for that distance. Chances are that RV won't actually put two 50A loads on the two hot wires, so you could probably use 35-40A in your load calculations, even though there may be peak periods where it gets a bit higher. As a practical matter, wires are often sized based for 80% of peak load.


There are various tables and calculators available online to show how much voltage drop can be expected over a given length. 3%-5% is generally considered to be the max acceptable drop, assuming you start out with adequate voltage (120/240 in this case).
Here is one such:
http://www.nooutage.com/vdrop.htm
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 11-22-2017, 05:19 PM   #13
Senior Member
 
Join Date: Jul 2014
Posts: 35,438
For that long a run, conduit and 4 single wires may be cheaper. I believe you can use a lighter gauge in conduit then UF cable.
twinboat is offline   Reply With Quote
Old 11-22-2017, 05:42 PM   #14
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
I would consider to run #4 THHN in conduit. In most places you can bury conduit 18", whereas direct burial is 24". That 6" at the bottom can be hard digging. UF is expensive. Include a couple pull wires for future additions. Either way it will likely be considered as a detached subpanel and require a ground rod at the pedistal/destination.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Reply

Tags
electric, electrical



Currently Active Users Viewing This Thread: 2 (0 members and 2 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
House Batteries Removed & Shore Power & Battery Disconnect switches on Run? CoachStreamr Gulf Stream Owner's Forum 7 10-16-2017 11:26 PM
can 50 amp coach run a/c on 30 amp service eddiel Winnebago Industries Owner's Forum 8 09-04-2016 05:09 AM
50 amp MH on 30 amp shorepower - run W/D? larrymo Class A Motorhome Discussions 16 07-05-2016 01:08 PM
To run or not to run..that is the question Jimbo8264 iRV2.com General Discussion 7 11-18-2006 04:30 PM
front brakes run hot on the first run of the day--why? DougJ Ford Motorhome Chassis Forum 7 09-16-2006 11:51 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 01:05 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.