Old 03-21-2009, 05:04 AM   #43
Moderator Emeritus
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,060
Quote:
Originally Posted by Roadking View Post
As stated when your RV EMS detects L1 and L2 are in-phase it configures your EMS as either a 30amp source or a 20 amp source (depending on switch settings). A 50amp to 30amp adapter ties L1 and L2 together and hence applies the same phase to each of the legs on the RV, and hence the EMS senses the source as 30 amps, or 20 amps.

Many RVs with 50 amp connections carry a 7.5KW generator. Assuming voltage and current are in phase (which is not true for inductive loads such as AC motors, but lets assume they are) then POWER = Voltage times Current. So a 7.5KW generator operating at 125Volts will provide approximately 60 amps of current. 7500 Watts = 125Volts times 60 amps (again, assuming voltage and current are in phase).

Rarely will the generator actually produce a full 60 amps, and hence, the neutral wire will not be overloaded in generator mode. However, "cheating" the EMS into thinking it is in generator mode, and pulling a full load on a power source that has both L1 and L2 in phase could overload the neutral. As previously stated.. you could potentially pull 100amps on the neutral if both legs L1 and L2 had 50 amps available and you were indeed pulling full capacity. Therefore you should not be creative by "faking " your EMS in generator mode unless you know for certain you are never pulling more than 50 amps Overloading the neutral could cause a fire anywhere along the neutral path all the way back to the main breaker panel where adequate sized neutral wires exist.

On the other hand, if you know the maximum loads your coach pulls on each leg then perchance you may be able to manage the risk. For instance, when I was on my own meter at one particular resort I used a cheater/adapter to get the "out of phase" L1/L2 power. My L1 source had a 30 amp breaker and my L2 source had a 20 amp breaker. The only time I would trip a breaker (the 20 amp) is when the Dryer, Hotwater Heater, and 2nd AC compressor were all running at the same time. So normally, I rarely pulled more than a total 50 amps as I recall only tripping a breaker once.

I also know under normal common sense conditions with my 7.5KW generator running I have never pulled more than 45 amps total. I'm sure I could add an electric heater while running the AC and pull more, but besides me, who would do that?? This means it would be highly unlikely that I would overload a neutral wire as my max draw would typically be only 45 amps. Your coach may be different and if you don't know you should not risk any fires or potential damage.


I totally agree that this is not a good practice and should only be done knowing what you are doing. It is also highly unlikely that you would pull more than 50 amps and if so for a very brief period of time. As with any service the National Electric code allows for de-rating of service conductors for this reason.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-21-2009, 08:19 AM   #44
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 28,679
The Onan 7.5k and 8.0k Quiet Diesel generators produce only 120v, with the two legs in phase. If your motorhome rejects in-phase L1/L2, then you certainly don't want that model of generator, because you could never use the genny!

Total output in these generators is about 63A - 31.5A on each leg in the 7.5 and and more in the 8.0k version. That means the neutral carries up to 63A if the generator is fully loaded. Presumably the neutral feed back to the generator is sized for that.

My cheater box has two 30A connectors with the option of using a 30/20 or 30/15 adapter on each. Therefore the max load I can get is 60A if two 30A sources are available or 50/45A if using a 30A plus a 15 or 20A source.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is now West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 03-21-2009, 08:41 AM   #45
Senior Member
 
Workhorse Chassis Owner
Join Date: Jan 2007
Location: Roving, Datastorm users 3192
Posts: 755
Quote:
Originally Posted by VACMAN View Post
Am I right or wrong in my assumption? If I plug the MH 50 amp plug into a 240 receptacle, that will be bringing 2 legs of 120 volt each to the MH, and the setup on the MH will handle these 2 120 volt lines? Vacman
Well, I think you are both right and wrong... (Your thinking is good your language is a bit off)

Not two legs but one leg divided into two circuits.

This works because there is nothing in the rig that is 240 volt, it's all 120 volt and the appliances do not care if they are plugged into L1 or L2 (the two legs) so they work just as well with one leg.

The issue though is with only 20 amps you can not run much at one time, In fact if my batteries are low 20 amps is JUST the converters, nothing else. in my house, Once the batteries top off I can run other things
__________________
Nothing adds excitement like something that is none of your business.
2005 Damon Intruder 377W Radio Active as WA8YXM
John-D is offline   Reply With Quote
Old 03-24-2009, 04:08 AM   #46
Senior Member
 
randco's Avatar
 
Join Date: Jul 2008
Location: Sarasota, Florida
Posts: 606
Quote:
Originally Posted by David K View Post
The legs for the 120v need to be "out of phase" or from different sides of the breaker box -- not from the same bus bar as the most of the 240v in our houses are done. In the house, phase does not become a consideration as the appliance will use the "in phase" 120v and the neutral wire does not have to worry with the "additive" effect of the 220v -- it don't happen.
If the 240V wiring in your home is wired off of the same buss bar you won't have 240V.
__________________
2004 Damon Escaper 4076
randco is offline   Reply With Quote
Old 03-24-2009, 08:30 AM   #47
Senior Member
 
Workhorse Chassis Owner
Join Date: Jan 2007
Location: Roving, Datastorm users 3192
Posts: 755
My coach is currently plugged into 20 amps. I can run.

Dead batteries (2 banks) the converters. And very little else

Full batteires: The converters, Television or radio and one from the following list

Heater (2,000 watts)
Heaters (1500 + 150 watt) Plus soldering iron
Microwave
Water heater
Air conditoiner

NOTE: Frig at 250 watts is, like the 100 watt soldering iron, a "nothign load" and can be run most any time.

I use the rig most every day, summer and winter, as it's my "Ham Shack" (See sig) and thus I will use either 1AC in the heat of summer or the two small heaters in the winter (I only heat the smallest occupiable room in the rig) I normally run the big electric heater off the generator once a month
__________________
Nothing adds excitement like something that is none of your business.
2005 Damon Intruder 377W Radio Active as WA8YXM
John-D is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wondering if I can use a 50 amp converter cord with my 30 amp service? luke_vardanian Travel Trailer Discussion 12 11-10-2008 03:34 AM
Will a 50 amp surge protector work with a 30 amp system CWIL 5th Wheel Discussion 5 08-21-2008 02:34 PM
30-amp dog-bone with 50-amp shore power jeeprubi RV Systems & Appliances 11 02-14-2008 03:10 AM
Vector 2-10-30 Amp, 80 Amp Start Battery Charger Logthumper Gear and Product Discussions 2 03-23-2007 03:24 AM
Replacing 20 amp electrical land line plug with 30 amp????? Ragman MH-General Discussions & Problems 6 07-21-2006 10:28 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 01:05 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, vBulletin Solutions, Inc.