50 amp power

I have a 40 amp breaker on a 50 amp outlet for my RV. What is the average draw for a RV? Do most Rv need 50 amp?
4each is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-27-2016, 12:10 PM   #2
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
You have a 40 amp on one leg and a 50 on the other?
Or two 40 amps, one on each leg?
Or what?

A 50 amp RV plug in has two 50 amp breakers, one on each leg for a total of 12,000 watts (50 x 2 x 120)

If you have a 40 on one leg and a 50 on the other then you have 50 + 40 x 120 = 10,800 watts

If you have two 40 amp breakers than you have 40 x 2 x 120 or 9,600 watts.

To know if it's enough you need to figure out what you'll run all at once and total it up.

Our's is one that could use all 12,000 watts. Just the AquaHot on electric would take 4,000 watts, the electric floor heat is about 3,000 watts, then there's the three heat pumps and the 240 volt dryer, the Jenn air refer/freezer, lights, TV's etc.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Old 05-27-2016, 12:12 PM   #3
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,777
Quote:
Originally Posted by 4each View Post
I have a 40 amp breaker on a 50 amp outlet for my RV. What is the average draw for a RV? Do most Rv need 50 amp?
4each
A "dual 40A breaker" on a 50A outlet will allow you to use up to a total of 80A of 120V power in your RV at one time...(rather than the 100A total a "so called" 50A RV outlet will provide).


DUAL 40A BREAKER

Mel
'96 Safari
mel s is offline   Reply With Quote
Old 05-27-2016, 12:40 PM   #4
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
You will likely never exceed the 40a breaker, if actually setup properly. Its probably a 40a breaker to match the wire size, which is a good thing.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 05-28-2016, 12:30 PM   #5
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 28,297
I wouldn't say "never", but odds are that 2x40A is going to be more than sufficient. I've hit 40-42 amps once in awhile, when an a/c, the water heater, and the washer dryer all happen to cycle on at the same time (they all share Leg #2). Even then, it usually steadies out about 26-32 on one leg and 20-28 on another. We sometimes run off twin 30A circuits and that works nearly as well, but we use the dryer cautiously ( I usually flip the water heater off, just to be sure) I don't trip a breaker.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is now West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 05-28-2016, 03:08 PM   #6
Senior Member
 
Join Date: Sep 2009
Location: Central Indiana
Posts: 1,422
I have a double 30 amp breaker wired to a 50 amp outlet. The wire size is #10-4 conductor, and the run is less than 40 feet. With both air conditioners, water heater, and initial charge for batteries plus miscellaneous lighting etc , I have never tripped the breaker. Large rallies count on 24 amps per leg or a total of 48 amps.
mrboyer is offline   Reply With Quote
Old 06-10-2016, 11:49 AM   #7
Member
 
Join Date: Apr 2014
Posts: 46
Forgot to ask, but how do you tell how many amps are being pulled on l-1 and l-2?
Oldone1 is offline   Reply With Quote
Old 06-10-2016, 12:32 PM   #8
Senior Member
 
Steve Ownby's Avatar
 
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,587
Quote:
Originally Posted by Oldone1 View Post
Forgot to ask, but how do you tell how many amps are being pulled on l-1 and l-2?

If you have a EMS like the Progressive, then that is one of the items it scrolls through.
__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
Steve Ownby is offline   Reply With Quote
Old 06-10-2016, 07:10 PM   #9
Senior Member
 
seasonedsole's Avatar
 
Mid Atlantic Campers
Ford Super Duty Owner
Join Date: Sep 2010
Location: NE PA
Posts: 154
The tricky part is dividing usage between both line 1 and line 2. Usually, from the factory line 1 has much more on it, line 2 often is 2nd Air Conditioner.
__________________
Doug and Lisa, FMCA 436113
2006 Fleetwood Providence 39L
350 HP Cat, Spartan, 24' ATC enclosed
Subaru Outback, Cricket SW3
seasonedsole is offline   Reply With Quote
Old 06-10-2016, 09:33 PM   #10
Senior Member
 
rgvtexan's Avatar
 
Winnebago Owners Club
Freightliner Owners Club
Join Date: Oct 2009
Location: E WA or S TX
Posts: 4,083
Quote:
Originally Posted by 4each View Post
I have a 40 amp breaker on a 50 amp outlet for my RV. What is the average draw for a RV? Do most Rv need 50 amp?
A little info on your RV will help. I would guess that most RVs don't even have 50 amp service. I know there are many RV sites that don't have it.

You can put your make. year, and model in the signature block.

Help us help you. Welcome to the best place for help.
__________________
04 Horizon QD, 12 Ford Flex, Excalibar, Brakemaster, Winter Texan, RVin! since 1974
Norm, Donna & Tinker Kat(RIP) 01 Z3
Life is a Timed Event, you only get One Go Around!
rgvtexan is offline   Reply With Quote
Old 06-10-2016, 09:51 PM   #11
Senior Member
 
Steve Ownby's Avatar
 
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,587
Quote:
Originally Posted by 4each View Post
I have a 40 amp breaker on a 50 amp outlet for my RV. What is the average draw for a RV? Do most Rv need 50 amp?

Should be find most of the time. Any particular reason you're using a double pole 40 amp instead of a double pole 50 amp.
__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
Steve Ownby is offline   Reply With Quote
Old 06-10-2016, 10:17 PM   #12
Senior Member
 
MtnTrek's Avatar
 
Join Date: Jul 2015
Location: Currently; SW Cali. Sunny & warm!
Posts: 1,323
Quote:
Originally Posted by Steve Ownby View Post
Should be find most of the time. Any particular reason you're using a double pole 40 amp instead of a double pole 50 amp.
OP'r could specify, but the breaker was more than likely installed to be in compliance with the specific wire gauge installed in that circuit, ( dryer, stove, etc.)
Breakers are to protect the branch circuit wiring from overload. Unless the OP'r knows for sure it wouldn't be advised to modify said circuit.

Happy trail.
__________________
J & J, DRV Suites ES-38RSSA #9679
GM Denali, 3500HD-Max, 4x CC, 8' DRW,
EZGo-TXT, Clubcar Precedent
MtnTrek is offline   Reply With Quote
Old 06-11-2016, 05:14 AM   #13
Senior Member
 
H. Miller's Avatar
 
Monaco Owners Club
Texas Boomers Club
Join Date: Jan 2009
Posts: 2,529
Quote:
Originally Posted by 4each View Post
I have a 40 amp breaker on a 50 amp outlet for my RV. What is the average draw for a RV? Do most Rv need 50 amp?
AMAZING! Above question asked 2 weeks ago with all sorts of "WAG's" given in the mean time. Correct answer depends on additional info from OP who has not been heard from again.. Guess an adequate answer was found elsewhere
__________________
Hal & Ginny Miller '04 Beaver Santiam PRT40
'04 Saturn Vue - US Gear Brake - Blue Ox tow
3"girls" (2 Irish Setters - 1 Retriever) - RIP Annie & Emily (12/26/2017)
H. Miller is offline   Reply With Quote
Old 06-14-2016, 08:27 AM   #14
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 28,297
Yeah, he didn't even visit again to read answers, let alone contribute further. So we are all pretty much talking to each other and not helping 4each. C'est la vie!
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is now West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Reply

Tags
power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
"NORCOLD & DOMETIC RECALLS" & Service Manuals Norcold & Dometic "007" RV Systems & Appliances 89 07-18-2019 04:41 PM
Generator Maintenance & MANUALS Onan & Generac & PARTS "007" RV Systems & Appliances 34 07-06-2019 02:09 AM
2011 RV chassis Mods & parts & Tech info new & old chassis "007" Ford Motorhome Chassis Forum 4 09-27-2011 07:26 AM
50 amp to 30 amp to 20 amp?? fansill MH-General Discussions & Problems 5 05-15-2011 01:36 AM
50 amp power down to 15 amp power TEDDE Monaco Owner's Forum 29 05-04-2011 10:08 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:00 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.